Question about Emerson Computers & Internet
Recently we had the UPS input feeder breaker trip due to a the wrong voltage supplied to a switch. the switch was rated for 120v and the electrical contractor connected 208v to the phone switch. The UPS sensed the problem and according to the alarm history transferred to bypass - inverter leg overcurrent - output undervoltage - bypass frequency out of tolerance - critical power supply failure. Why did the input breaker trip\r\n Thanks
  • 6966 Answers
SOURCE: UPS problem
Based on your post/description, two (2) possibilities:
1. electronic fault - main power/AC mains sensor which could be really just a relay; or
2. corroded fuse terminals or fuse holder.
The first is a bit of a challenge since different brands/models have different sensing circuitry design. Some can be as earlier stated, a simple AC relay while others could be a TRIAC switch with a DIAC trigger. Still, some could be an elaborate AD converter and a myriad of logic circuitry. Often, a service manual or at least a schematic diagram would be needed, however these are not that readily available and most often the tech or DIYer must resort to winging it. This of course would require familiarity with electronic circuitry and components, use of a DVM and a soldering iron. Extreme caution must be exercised since even with 12VDC supply most of the electronics are at least at 60VAC+ level.
The 2nd possibility would be of course be the easiest to determine and repair. Replace/clean.
Should the downtime & repair cost makes the project no longer economically reasonable, perhaps your best bet would be to simply replace the UPS since their prices are relatively low.
Hope this be of initial help/idea. Pls post back how things turned up or should you need additional information.
Good luck and kind regards.
Thank you for using FixYa.
Posted on Apr 16, 2008
  • 348 Answers
SOURCE: emerge UPS 500va special power supply not working..
there is a fuse behind the ups which can be removed by opening the socket replace it if faulty
and you can operate the ups
Posted on Nov 27, 2008
  • 748 Answers
SOURCE: mge galaxy 20kva ups input breaker trip
Does it trip immediately or after a time? If it's immediate then there's a dead short on the line (or possibly inside the UPS). If it takes time to trip then there's a slow build up of too much current use. This is usually caused by defective capacitors in a power supply.
Posted on Apr 06, 2009
  • 2777 Answers
SOURCE: I recently purchased a used Belkin F6C800-UNV UPS,
This is normal in some lower end UPS's, the voltage can swing quite a bit, a drop of 40 seems like quite a bit but it's out of the question. It will also adapt to what is plugged in yes. Ultimately to test you would want to try it with something like an actual PC plugged in and make sure it stays running. I'd say otherwise it sounds normal to me.
Posted on Jul 10, 2009
  • 2567 Answers
SOURCE: bypass LED on the ups is on
This an excerpt from the UPS's manual:
The Bypass LED illuminates indicating that the UPS is in bypass mode. Utility power is sent directly to connected equipment during bypass mode operation. Bypass mode operation is the result of an internal UPS fault, an overload condition, or a user initiated command through an accessory. Battery operation is not available when the UPS is in bypass mode.
Posted on Jul 19, 2009
Wiring diagram for a 1988 sunline travel trailer.some of the light switches and outlets have no power going to them.what could be the problem?
Your trailer has two electrical systems, 12v and 120v. The 12v system has a battery and perhaps a converter/charger to power it. The 120v system must he hooked up to 'shore power.' Both systems have their own protection. The 12v system has a fuse panel, check for power at each fuse. 12v wall switches are often smaller and don't look like typical 120v switches like in a house.
The 120v system has a breaker box and circuit breakers. Reset each breaker by turning off then on again. In addition, the 120v outlets might have a GCFI outlet near a sink. It often is wired first in a breaker circuit, thus giving GCFI protection to other outlets in the circuit. Test the GCFI and make sure it clicks off and can be reset.
May 01, 2017 | RVs
Hobart P660 keeps shutting off and tripping the breaker
Sounds like the cable is too small. If you're hooking it up to 15 amp breaker you need the correct diameter size extension cord, and the equipment cannot be rated more than 15 amp or you'll have a problem. I perceive this may be the solution based on the fact that you said that the motor was not coming up to speed.
Jan 07, 2014 | Hobart P660 Stand Mixer
I have a 300GAL Spa that was installed on a 120v 20amp two pole. I had a 240v 50amp breaker that I replced with two 120v 20amp breakers, we wired the tub and the pump works but when the heater is turned...
What is the amp rating for the tub? What voltage are you actually running the tub on, 120 or 240? Is the 120v 10amp two-pole then the switch rating since you mention a switch? If there is no amp rating on the control what is the wattage of the heater element and how much horsepower is the pump rated for?
In the end it seems likely you do not have high enough breaker ratings to carry the pump(s) and the heater at the same time. Depending on the electrical circuit wire size and the breakers and switches you may need to make some adjustments or replace some of the components but I'll/we'll need more details on your existing setup and the tubs electrical demand to help you further.
Mar 28, 2011 | Apollo Pool & Spa
Ups starts beeping
Is there any indicator lights ON showing the fault condition?
This could indicate that the battery has a low charge. Even if you switch off the mains supply and it switches over to the battery, the UPS may shut down after a short time as the battery power (charge) runs out.
If the battery is more than 3 years old then it may be due for replacement.
May 10, 2010 | Powercom BNT-1000AP (dspcmbnt1000ap) UPS...
UPS SU700J use in united states: OK? Rated for 100V Japan power, 120V US: OK? Or bad?
ok no problem from 85v min to 140vac max input voltage is between accceptable range of window
Mar 05, 2010 | APC (SU700J) UPS System
What is the maximum amount of electrical energy that can be delivered durning a short circuit for low voltage 230v/400v
Tom, Not sure if what you're asking relates to the Maximum electrical energy (Voltage and Amps) that can occur during a short circuit through a properly protected electrical circuit (protected by a circuit breaker, etc.) or if the question is for the maximum amount you could potentially get from a short circuit on a 230V or 400V electrical line to ground OR another electrical line/supply.
IF the circuit is a 230V-AC circuit protected by a double circuit breaker, you could see the entire Voltage (230V-AC) and up to the full Ampere rating of the circuit breaker, (20, 30, 40, 50, etc Amps) during a short circuit condition to Ground.
IF the circuit is a 400V-AC circuit protected by a double circuit breaker, you, again, could get the entire Voltage (400V-AC) and up to the full Ampere rating of the circuit breaker protecting the circuit, when shorted to Ground.
Now, IF the short condition involves one of the above line voltages AND you are having it shorted against another Voltage/Amp circuit, the total potential Voltage and Amps you could experience, would basically be the sum of the two Voltages (and Amps) of the two (2) circuits being put into a short condition. So you would/could see a potential short circuit of whatever voltage is available, depending on what and where the short circuit is occurring.
By way of example, I've seen a 240V-AC 60 Amp circuit shorted to another 240V-AC 60 Amp circuit and the resultant "short condition caused enough damage, due to the voltage and Amps provided, to melt and weld the machinery's electrical connections, rendering the unit a total loss, not to mention that the person that caused the short to occur, received a face-full of melted copper metal bits all over their face and body. Thankfully they were wearing safety glasses, and their eyesight was saved, albeit, with some temporary blindness caused by the extremely bright flash and explosion.
The examples provided assume a properly working/functioning circuit breaker protection. However, if the circuit breakers are faulty, it is possible to recieve much higher vlotages and Amps, since there would be no protective circuit breaker that could trip the power off. In that case, the Main circuit breaker becomes the fail-safe protective device and that could have a much higher Amp rating, thus the maximum Voltage/Amps would be limited by the Main electrical ciruit breaker and electrical supply available at the location where the short circuit occurs.
This could be MUCH higher Voltage and extremely high Amps, depending on the situation and equipment involved.
If you have more information about the particular situation, please post a follow-up comment and I'll provide you with some more info.
I hope you find this Very Helpful and best regards!
Nov 17, 2009 | Square D Qob120 1pole 20amp 120v Circuit...
Hi, I bought a 1500va APC UPS. Its not charging when connected to the mains power supply. It still beeps and stays on battery. I have set up the transfer voltage and sensitivity adjustment to no avail....
Hi, I am a licensed Master Electrician with 27 years exp.
Need more info. Did it work before? Are you positive your incoming voltage is correct? I will assume all of them things as yes and see what I can think of to fix ya up.
I would connect it to a load and let the batteries totally deplete, like a small drill or something that pulls close to the 12.5vac (1500va). Disconnect the load and unplug it for a minute, then plug it back in and then see if it charges. If it does, leave it alone til it completes charging then put a load on it. It shouldnt charge with a load on it if the battery is already fully charged. Then unplug it from the wall receptacle (main power) and see if it transfers and the batteries take over. If it does it should not charge again. A UPC should only charge when your load is being supplied by the main power, i.e., the UPS is plugged in and not transferred to the battery state.
I hope I have helped with what info I had, if not then get back with me, their are other issues, like internal fusing on the main power supply coming in as well as battery charger internal fusing. NOTE: If you ever replace an internal fuse on a UPS be absolutely sure, without a doubt that it is of the same type as in voltage, ac or dc, and most importantly the amp rating. BTW in case you didn't know, to get the amp rating of something rated in VA, as in 1500va, you divide 1500 (the va) by 120v. (supply voltage) that is assuming it is 120v. if any other voltage just adjust your divisor to match the voltage. 1500va/120v = 12.5 amps. Good luck!
Nov 06, 2009 | APC Back-UPSĀ® ES UPS System
My ups battery brekar trips freqvently
UPS battery backups sometimes come with two ratings, one is continuous use, and the other is Peak use. In other words if you stay at the continuous load and it isn't in a hot area, or in a place where heat can build up (excessive heat lowers the UPS rating alot) you should be fine, but if you are over that rating and into the Peak rating for more than 10 seconds or so (varies) it will trip to protect itself. Or it could simply be a faulty breaker. Look at how much load you have
Just in case you dont already know, the way to tell how many amps any UPS can handle is to divide the va by the supply other words a 1200va UPS plugged into a 120v. outlet will handle 10 amps, but if you want a UPS that you are going to use at 10 amps you would want one that was rated for 1200va continuous, or better yet, go up to a 1500va and it will never let you down. Good luck.
Nov 06, 2009 | Emerson PowerSure Personal 500VA...
"On Battery" Alarm Sounds when Power Available.
if this comes sometimes and goes, this means that the power to ups is sometimes deviating from the specific ups input range, hence the ups is rejecting it. mesure the input voltagesand frequency with a multimeter and check whether they match the specified ones in the ups manual. aslo with some ups there are switches that you use to set the input voltages or number of phases in the ups input. check the manual to see whetther your ups has such.
Oct 24, 2009 | APC BX800 Back-UPS XS 800 (APNBX800) UPS...
Mge galaxy 20kva ups input breaker trip
Apr 06, 2009 | MGE UPS Galaxy 3000 UPS System
Computers & Internet Logo
Top Emerson Computers & Internet Experts
Stan Skaggs
Stan Skaggs
ray gallant
Are you an Emerson Computer and Internet Expert? Answer questions, earn points and help others