Where do the wires from the thermostat attach to an outdoor Payne AC condencer unit ??
  • 2 more comments
  • bsassanel790 Aug 24, 2010
    I guess that I need a location on the condencer (sp) . My wife was weeding around the back of the unit and by mistake yanked the wire out and I cant find a place to re-attach it.. can you help ???
    All that is well and good BUT it is not the thermostat that is in question. I need to know where the two leads of the thermostat wire should be connected to the condensor unit. As I explained before, this wire was pulled from the unit while weeding around it.
  • bsassanel790 Aug 25, 2010
    Thanks for your efforts but my problem is still that I have no idea where inside of the condensor unit that I should attach this wire (two leads) that were pulled out by mistake. The unit (condensor) is a Payne. I am not sure of the model but it is not a very large one. Is it dangerous to let the System run without the control wire attached as the fan in the outdoor unit isn't running while the unit in the furnace is???
  • bsassanel790 Aug 26, 2010
    Yes and thank you
  • 407 Answers
Your thermostat wires will go directly to your furnace, then from your furnace they will go to the outside condenser. Without knowing what model and year furnace you have, or if it's a heat pump system or not, I can't tell you exactly hoe they hook up. For most units now, they have a electrical board inside the furnace that all the thermostat wires hook to. The terminals will be marked for each wire. The condenser wires will usually be connected to the Y(Cooling) and C/B (Common) terminals. Now if you have a heat pump system, it can be a little more tricky. Your standard split system will have 2 wires (usually Red and White) going to the condenser, while your Heat Pump will have up to 7 wires and will sometimes connect to a box before going into the furnace. Like I said, it's difficult to tell without knowing what furnace and system you have, but hopefully I have already answered your question. Hope this helps and good luck!
Posted on Aug 25, 2010
  • Brandon Berry
    Brandon Berry Aug 26, 2010
    I'm sorry it took this long to respond, the business is still really busy right now. The wires you are referring to connect to two wires inside the electrical panel on the unit. They will usually be in a separate compartment (small metal piece separating them), but not always. You should see either two bare wires close together or possibly two wires with wire nuts on the end if they did not come off. It doesn't matter how the wires hook up as they will work both ways. But no, there are no terminals they connect to, just two wires that hook up to the two going to the unit. Sorry for the misunderstanding and the time again. If you have any other questions, I will try to respond as fast as possible.
    Top Expert:
  • Heating & Co... Master
  • 75,744 Answers
That varies from model to model, contact Payne customer support for instructions for your paticuliar AC unit
    Genius:
  • 1,478 Answers
The wires going to the condensing unit are shown as red and white however these colors can be different. The important part of these two wires going to the air conditioner condensing unit is that the one wire orginates from the thermostat Y terminal and terminates at the condenser and the other wire originates from the common side of the transformer which is most commonly installed in the air handler. On rare occassions the transformer can be found in the condensing unit not because the manufacturer installed the transformer in the condenser but because the transformer was blown and replaced in the condenser instead of the air handler. Additionally, the colors here are typical but can be different depending on who wired the unit and their color coding system. 99% of the HVAC technicians will use this color code but there is an occassional oddball who knows better than everyone else or the wiring color combination was not available for the wire used to wire the equipment.
Take care.
Posted on Aug 24, 2010
  • Jimoh Adeleke Muyideen Aug 24, 2010
    • Red to the thermostat RH or thermostat RC terminal with a jumper
      wire between thermostat RH and thermostat RC. Or Red to the
      thermostat R terminal which is shared with both the heating
      and cooling. It has an internal jumper built in to the
      sub-base. The red wire is the source hot wire from the
      transformer. All other wires, except the common wire, controls
      a specific relay or contactor that energizes the fan, heating, or
      cooling depending on the selection. The following is the
      common wiring colors but your system may not be common and
      different colors could have been used.
    • Green to the thermostat G terminal. This is the color that controls the fan or the relay that control of the blower.
    • Yellow to the thermostat Y terminal. This is for control of the air conditioning.
    • White to the thermostat W terminal. This is for control of the heating.
How to troubleshoot thermostat wiring?
I'm not sure if the thermostat is wired correctly. First, the thermostat is wired directly to the outdoor unit (compressor/condenser unit). It is NOT directly connected to the indoor unit. It connects to a low voltage control panel in the outdoor unit that sends a signal to your indoor fan/evaporator. This wire is called the fan relay switch and physically runs between the low voltage controls of the indoor and outdoor units. If the fan relay is bad it's possible that the unit runs continuously. To prevent destroying your outdoor unit there is a safety feature that prevents the indoor fan from shutting down while the outdoor unit is running. If the indoor fan did shut down while the outdoor unit was running than you would slug your compressor. That is, your compressor normally sees refrigerant gas but is instead seeing refrigerant liquid. That would not be good since this scenario would destroy your compressor. It sounds like a faulty fan relay. The actual contactor portion of the relay is in the outdoor unit.
Aug 22, 2014 | Honeywell Electronic Programmable...
Heat pump wont come on
Make sure you have power to the outdoor unit. The outdoor unit on a minisplit powers the indoor unit.
Dec 13, 2013 | Carrier Heating & Cooling
New Payne Furnace PG95SAS How to hook up wires for powering
MOST UNITS HAVE KNOCK OUT WHERE THE POWER GETS HOOKED UP, HANDY BOX WITH A SWITCH NEED TO BE ATTACHED, MAKE SURE YOU ARE USING A GOOD GROUND, AND HARD WIRED NOT AN EXTENSION RUNNING TO AN OUTLET.
Dec 08, 2013 | GE 1/3 Hp Furnace Blower Motor...
All of the sudden tonight it was getting hot went to adjust thermostat and it was blank. No air and no fan. Bought new thermostat (above). checked circuit breakers. thermostat shows it is on but wont kick...
At the thermostat you have several colored wires. Touch the green and red wire together and see if the indoor fan comes on. If you know what wire goes to the coil on your AC contactor touch the red wire to that wire. If it starts the outdoor fan and your compressor the thermostat is not wired correctly. All you are doing by my suggestion is bypassing the thermostat to eliminate it as the possible problem.
The outdoor AC contactor coil wire is usually yellow or blue, but you must make sure not to short the red wire to the other side of your transformer as that will cause you to have to buy a new transformer. Your unit wire diagram should show the wire to the AC contactor coil. You need to determine which wire feeds the AC coil which closes the contactor to the compressor and outdoor fan motor.
If this helps please rate me at fixya.com
Aug 03, 2011 | Heating & Cooling
WIRING THE THERMOSTAT TO AC UNIT THEN FROM THE UNIT TO HANDLER
Generally, you would go from the thermostat to the air handler, and then, from the air handler to the outdoor unit. I don't know if you have a heat pump or not, so I will give you a simple diagram and you can contact me if you need more.
Thermostat : Y G R W and sometimes C
Air handler: Y G R W and C
Outdoor unit: two wires connecting to the contactor ( not heat pump)
Thermostat; Y--------------Y(air handler cooling)------------------one side of contactor, outdoor unit
G-------------G (air handler, fan)
R--------------R (air handler ,hot)
W-------------W (air handler, heat)
C--------------C (air handler, common)------------other side of contactor, outdoor unit
This is a typical wiring diagram. Just contact me if you have something different. Hope this helps. Stay cool. mark
Jul 10, 2011 | Heating & Cooling
Payne AC not working. 1. Thermostat set 68 to AC w/fan on. 2. Breakers and switch near heater are on. 3. Outside unit has 220v but is not running. 4. Fan in heater/Ac unit is not running 5. ...
Dan is this a new system, or has some work on the system (to include the thermostat) been done recently?
Sounds like the thermostat may be wired wrong. From what you describe, the igniter element is coming on, as though you are calling for heating. Do you allow the ignitor to keep going and see if the gas fires off, or are you seeing this and shutting down the system immediately?
If you had the t-stat changed recently, or this is a new system, contact the installing contractor. It may be under warranty.
Sep 03, 2010 | Carrier Heating & Cooling
The unit is not communicating between the Furance and the AC
Then it is not communicating with the thermostat. When you turn it to cooling and the fan comes on, then the thermostat is communicating
with the furnace.
If you have 24volts between Y and C then it is communicating with the AC Unit. If you go outside and remove the electrical panel(shut off power
to outdoor unit) you can still hear the contactor being pulled in.
If you cannot hear that you need a new two wire from furnace to outdoor unit
Jul 16, 2010 | Ruud UAMB024 Air Conditioner
AC unit not kicking on...
You need a "Y" terminal. "Y" is pretty standard on every heat pump. It is the wire that will energize the compressor contactor at the outdoor unit, allowing the compressor and condensor fan to run.
Apr 03, 2010 | Heating & Cooling
No cool air. Thermostat AUX light turned on
I suggest you call a qualified service repair man. There are as many ways to connect a heat pump as there are people doing them. Nothing is standard industry wide that has anything to do directly with color codes, so it would be meaningless to go into them here. The terminals may be adapted to standard but but the thermostat manufacturer may not follow any terminal designations.
However you may just have an extra wire touching one of the terminals inside the thermostat. You can check this by removing the cover. Look where the wires attach to the terminal screws on the thermostat. Sometimes a new service person cuts the insulation back too far here or in the outdoor or indoor units and a "whisker" from one wire can touch the other terminals. A whisker is not the normal case try and move it away from another terminal if its is touching there. However, you may have jumpers in place especially if you have W, W1, W2... at any of the 3 sections, meaning the outdoor, indoor and thermostat.
If you can tell me the terminal designations R,Y, W1, W2, E, G, O, (B)... at the thermostat and the color thereon each, then at the indoor unit terminals or wire designations and the color there, then at the outdoor unit and the color thereon each terminal or wire designation there. I might be able to help if the above whisker check you don't find anything.:
Mar 25, 2009 | Heating & Cooling
Have a Payne A3PZ airconditioner and a Roberts Aire thermostate need help with wireing it up. The was I understand is that you need a Payne therostate to use with Payne AC unit. But surely there is a...
No, Payne is a cheap Carrier unit. Keep track of your wires and what terminals they are attached to. Usually, units are either a 4 wire or 5 wire setup. In either of these the R terminal is your 24v power, G term is your fan, W is your heat, and Y is your cool. Some times there is a 5 wire which is your common. You use a common if your thermostat isn't powered by a battery. On the R terminal, they are usually marked RC/RH and have a jumper between them. The only time you should remove the jumper is in a 5 wire set up. RC refers to the common and RH refers to Hot or power. Make sure that when you are installing the new tstat there is usually a very small switch that you change for either an electric unit or a gas unit. Change according to what you have. As long as you keep track of your colors and terminals on your old tstat, you won't have to open up your unit to see where the wires are terminating. Good luck to you!
Mar 22, 2009 | Heating & Cooling
Heating & Cooling Logo
182 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen