Question about Mitsubishi MSZ-A24NA Split System Air Conditioner
There is no cooling. After running a short time, the indoor unit only, the left LED blinks. The right LED turns off. I can't find anything about this. Could I be low on gas? Regards, Charles
  • 139 Answers
Look around them lights.., on the circuit boards.. or on the diagram.. them blinks are codes. so find the codes that are their .they will tell you the problem... p/s like 3 short flashes may mean fuse s are out at the dissconnect .you have to look and you will find it good luck
Posted on Aug 23, 2010
How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR
14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• Compressor
Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
Oct 13, 2017 | Panasonic Heating & Cooling
Luxpro psd111 thermostat shows snowflake (sometimes blinks), outdoor fan works, but no cool air comes out inside- no air flow at all. Is it the thermostat or an a/c unit malfunction?
If the outdoor unit is running the indoor fan should definitely be running. Turn power off to indoor unit. Put red green and yellow wires together behind the tstat with a wire nut. That is power (red), indoor fan (green), and compressor (yellow.) Turn power back on. This is bypassing the tstat and you should have indoor fan and outside running as well. If yes the problem is in the tstat, if no indoor fan the problem is in the unit. Good Luck!! Let me know!!
Apr 28, 2017 | Heating & Cooling
Luxpro PSD111 thermostat reading 78 when set to cool at 72. Snowflake blinking and not cooling. Please advise. Thank you.
Usually blinking means you are in a time delay. Obviously not for three hours but... Turn fan to on position and verify your indoor fan is working. If so check outdoor unit and see if it's running. If no indoor fan turn breaker off, and inside the tstat put the red and green wires together and turn breaker back on. If indoor fan runs you have a bad tstat. Good luck!!
Mar 22, 2017 | Heating & Cooling
Mitsubishi timer light 6 times blinking
Indoor unit indicator
RUN lamp = 6 time flash
TIMER lamp = Comes on
Outdoor unit indicator (LED5) = Stays off
Description of trouble = Indoor fan motor error (2)
Cause = Defective fan motor, Connector poor connection
Conditions of flashing = When air conditioner is operating and indoor fan motor is turned ON, indoor fan motor speed of 400 rpm or under continued for more than 30 seconds. (Air conditioner stops.)
May 29, 2016 | Mitsubishi Heating & Cooling
Front grill
Check the air filter and if it is dirty, replace..
Turn equipment off and let the ice melt.
After ice melts, place a/c in cooling mode and set the thermostat to 3 degrees below room temp display.
The indoor unit fan should start blowing cold air immediately and then turn off once the room temp drops one degree below the cooling temp setting.
If the indoor unit does cycle off, check the outdoor unit and make sure it turns off at the same time.
If the outdoor unit continues to run and the indoor fan is not running, the indoor unit will ice up.
A defective compressor relay that is stuck in a closed position will cause icing of the indoor unit because it keeps the compressor running when it should turn off with the indoor fan.
Do you have an error code being displayed on the controller?
Is there an led light that is flashing on the indoor unit?
Another possibility causing the indoor unit to ice up is if the freon in the system starts to get low.
Make sure the ice has all melted for this next check.
Pretty easy to check without special tools.
If the air filter is clean and there is no dust/ dirt blocking the fins on the indoor unit, turn a/c back on to cool and check that the indoor unit fan comes on and is blowing air good.
Once everything seems to running good go to the outdoor unit.
There will be two lines with black rubber insulation covering them.
Peel back the insulation three inches on each line and observe the copper lines.
If either line starts to frost up the a/c system is most likely low on refrigerant.
Another cause of indoor unit icing could be that the aluminum fins behind the air filter are clogged with dust or other foreign material.
This would block the air that must be pulled in causing the indoor unit coil to become too cold due to lack of air flow and it will ice up.
Operating the cooling system when the outdoor temperature is below 60 degrees can cause the indoor unit to ice up also.
I'm Robert.
Florida certified a/c contractor. 30 years experience.
Hope this helps.
Mar 18, 2014 | Fujitsu Heating & Cooling
Its a trane unit model# TUE060A936K3 in cooling mode condensor comes on the indoor fan does not in heating mode every thing comes on but the blower fan does not there is not a led light blinking code...
Either the vent is blocked or the pressure switch that tells it that the purge blower is running is not working right...for some reason that switch is not making contact and so it will not let it light..
heatman101
Aug 11, 2010 | Heating & Cooling
AIR CONDITIONER LG S18AN
The operating LED will be blinking 5 times, means that there is a
comunication error (serial comunication) between the outdoor and the indoor unit.
Dec 28, 2008 | LG LS-K1830CL Cool Mini Split Air...
Lg split indoor fan runs non stop
Hello Hamid,
The unit is designed to run the indoor fanmotors continuously when in cooling mode on both indoor units (evaporators). The reason is that this circulates the air and the temperature thermistor or sensor is able to sense return air temperature and in turn start or stop the outdoor unit and compressor as required according to the setpoint temperature. The reason for either unit not reaching setpoint temperature can be a couple of reasons. A) Incorrect design - the unit may be too small for the application. You can calculate this roughly at 650BTU per square meter of room in a relatively warm ambient climate. Or secondly B) The outdoor unit has leaked and is short of refrigerant. You can check this when the outdoor unit is running by feeling the thicker copper tube on the right hand side of the unit. This should be cool to cold. If no temperature difference is felt, it is short of refrigerant. Hope this helps you. Goodbye
Aug 11, 2008 | LG LS-L1210CL Mini Split Air Conditioner
No cooling after power out, indicator lights pattern not in manual
The Mitsubishi units have to be reset by turning off the indoor units by switching the remote or thermostat to off. Then turn off the breaker to the outside unit(s). After 30 seconds,turn on the breaker and then you can turn on the remote for cool. If no lights come on on the inside units, most likely you have blown a fuse soldered on the main PC board. At this point, call your technician. A goos tech will be able to wire in an in-line fuse holder so if it should happen again, you can easily replace the fuse. If you do see a light or two come on at the indoor unit but the outdoor unit does not start after 3 or 4 minutes, sounds like you will need to call a technician. Most likely you have a blown fuse on the main PC board of the outside unit. It is not an easy one to replace. Good Luck!
Aug 31, 2007 | Mitsubishi MSH09TW Air Conditioner
Mitsubishi MSZ-A24NA Split System Air Conditioner Logo
492 people viewed this question
Top Mitsubishi Heating & Cooling Experts
D. E. Hev
MightyMikeJr
Are you a Mitsubishi Heating and Cooling Expert? Answer questions, earn points and help others