I have a fulton boiler that keeps misfiring due to a low flame signal error. had electrode and flamerod replaced. i am afraid the tech guy did not place the flame rod correctly. my boiler is still mis firing. dont know what it should look like... please help..... small business suffering, west virginia
  • 149 Answers
Easy fix take a piece of steel wool clean flame sensor lightlly also check your ground very important. but most times
cleaning rod will solve good luck ps turn off power peforming any maintenance
Posted on Aug 21, 2010
Burnham water boiler V8 series Lockout code sensor err. whats the simple fix. reset it & it stayed on for hours but locked out again
this seems a common error to get , theres a few thing to check , but first you need to decide if you wish to take it apart or youll hire someone ,
the error means that the flame sensor isn't seeing the flame in a constant mode , but intermittently this usually happens due to electrodes needing replacement or adjustments but can also be a dirty nozzle as well
but a service tech usually cks some other less common faults these have as well
oil burners should have yearly prevent service done to keep from having these types of problems
Jan 18, 2017 | Heating & Cooling
I am getting 7 red light blinking on my goodman furnace. how to fix Flame Sense Microamp Signal Low ?
If its the flame sensor check connections to and from sensor.
Try cleaning sensor or replace sensor .
Nov 06, 2016 | Heating & Cooling
Noritz Boiler NH-1501-DV-NG Shuts off at radom times with blinking error code 123
error code 123 is a flame rod sensor problem. Chances are the flame rod is sending a weak signal to the control unit. Check for a loose flame rod electrical connector. Peek in the flame inspection windows to ensure there is a proper flame on that side of the burner. If non of the above then try removing the flame rod and cleaning with 400 grit sandpaper or replace it with part order # SKC7448 (called an Ignition plug ELV & Packing EHK SETV)
Dec 16, 2012 | Noritz NH150-DV-NG Indoor Direct Vent...
MY IDEAL LOGIC 30 HAS FAULT CODE L2 ALMOST EVERY DAY SINCE INSTALATION DEC 2010
is boiler still under warranty?
normal warranty lasts at least 2 years
if so get ideal to send one of their engineers out
L2 relates to flame failure
either boiler has failed to ignite
or
boiler has not detected flame once lit
several causes
failure to ignite
ignition electrode/spark generator
failure to detect lit flame
detection electrode/detection lead
blocked condensate pipe
or defective condensate syphonic trap
you really need an engineer to check these components
Mar 16, 2011 | Heating & Cooling
Electric and battery working fine but gas will not come on. It keeps clicking and then the red light comes on
Assuming this is on a travel trailer / RV, correct?
The red "check" light indicates that the fridge was not able to detect the presence of a flame from the burner area. This could be due to low LP gas pressure (causes different flame size), no LP gas (tanks are exhausted / turned off), damaged wiring going to the igniter / sense electrodes, defective gas valve, or damaged igniter / control board.
Aug 18, 2010 | Refrigerators
F4 fault with Vizo Plus 24. Not condensation tube as this was changed to new tube with sensors on ''blue plug'' by engineer last year when I called them out for re-curring F4 fault - new sensors are bone...
Hi, if the ignition module fires or tries to fire 4 times, this indicates the module is faulty and locks out for safety reasons because of an internal fault.The f-4 code sounds like the pressure switch was open due to condensation not letting it fire up, so the switch was ok, so they changed out the tubing. When you re-set the boiler control module, it locks out due to a internal fault. Change it out and you will be back up and running. The electrodes from the module will cause this as they come from the module. Make sure the condensate trap has no blockage at all as this can cause this problem. I am not guessing, I would replace the boiler module control that you have been re-setting. Keep me posted,
Sincerely,
Shastalaker7
Mar 18, 2010 | Heating & Cooling
My boiler(baxi luna HT330) keeps going into E1 fault mode.
After you pressure system do you bleed the rads then top up again .