No y connection on furnace module to connect a.c. This is on a goodman model gmp075-3 furnace. I bought the b18099-13 replacement module and still no y terminal. I dont know were to land the t-stat wiring. please help
  • 828 Answers
"Y" terminal at the stat feeds condensing unit outside, common from the condensing unit to common on the furnace transformer.
"G" terminal on the stat brings the fan on for air circulation. In cooling mode "Y" terminal also brings the fan on. If this furnace was not A/C ready check the VA capacity of the transformer. Should be about 40VA. Make sure there is a fan relay to bring the fan on in the cooling mode.
Posted on May 01, 2008
Replacing Goodman Furnace B18099-26 with ICM286 fails
decouple the output of the pcb ,put a 10-100nf between the two connectors
Nov 06, 2013 | ICM286 Furnace Control Board
How to install a spark ignitor in a gas furnace?
How to install a spark ignitor in a gas furnace? - Fixya
www.fixya.com/support/t15727344-install_spark_ignitor_in_gas_furnace
Jan 8, 2013 - How do I connect the high voltage wire to the Model 990-516 spark - Air ... SOURCE: Goodman furnace wont light, ignitor suspected. Notice.
carrier igniter
Jan 08, 2013 | Heating & Cooling
The blower fan on my furnace runs all day ,,, and on the trouble its said if light stay on that its incorrect twinning / polarity what do I do...and i bought a new board for if and still the same thing
You may have a bad ground or neutral wire in the circuit breaker panel for your house. Chack all wire connections and make sure that the black wire from your breaker panel connects to the black wire of the furnace. Check all ground wires in the furnace.
Jan 27, 2011 | Goodman GDS80904BNA Open Flame Heater
Goodman furnace model # GMNT100-4B On vacation neighbor checked house house filled with gas. He shut off main and furnace. Came home turned on gas to everything except furnace. All good. Furnace will not...
from my experience with goodman units ,it could have been a gas supply problem there are so many protective sensors that i dont think it is the unit by the way is it electronic ignitor or pilot
May 14, 2010 | Goodman GMS90703BXA Heater
Hi Proper way on wiring furnace.
I can give you a start, For heat only, R terminal on furnace to Red wire to R or RH terminal on thermostat. W terminal to White wire to W terminal on thermostat. G terminal to Green wire to G terminal on thermostat. This will get you heat but not air conditioning.
Jan 06, 2010 | Goodman Heating & Cooling
Goodman GPM075-3 air conditioning connections
your thermostat powers 'Y' for cooling. That in your case blue wire connects to 'Y' on the control board in the furnace. Then a pair of low-voltage wires connects 'Y' and 'C' on the furnace to the two wires to the coil of the contactor in the a/c condensing unit. So to follow the path, the signal wire from the thermostat sends 24v down the Y wire to the furnace board Y terminal which also connects to one side of the contactor coil in the air conditioner. To complete the control circuit to the air conditioner there has to be a common wire. This is connecting the C wire from the furnace board to the other side of the contactor in the air conditioner. Hope this helps.
Dec 11, 2009 | Goodman Heating & Cooling
Goodman furnace
double check your wiring. R terminal on the furnace will provide 24 volts to the t-stat. W terminal in the t-stat will send 24 volts back to the furnace W terminal to turn on the heat. G terminal in the t-stat will send power to the G terminal in the furnace when the t-stat is switched to fan on. Y terminal in the t-stat will send power to the Y terminal in the furnace which in turn will send 24 volts to the A/C outside. The C terminal in the furnace should be connected to the c terminal in the A/C outside as well as to the T-stat. Check the fuse again
Jun 02, 2009 | Goodman GMS90703BXA Heater
Furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
induced draft blower
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.
Nov 23, 2008 | Goodman GMS90703BXA Heater
Goodman GMP100-5 Rev Furnace Manual
I don't know where you are located, but there is a Goodman distributor in Sacramento, CA. Also in Ontario CA. They are a distributor so they may be able to help you or tell where to find someone who will help. Goodman is also known as GMC or Janitrol.
Jan 07, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
168 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen