Just wondering on a 1500 or 2000 240 volts how any on theses can i connect to one circuit, and whats the standard wire ty you
  • jim wells Sep 12, 2008
    i have the same problem, i have a 240 v fahrenheat f2544 electric convector baseboard heater, i would like a diagram or help with the wiring, i havefour wires from box.red/hot black/hot...white groung and bare ground
  • promed Dec 04, 2008
     i have a base board heater blower and the power is there but it did not turn on please advise wiring
    Scholar:
  • 68 Answers
Convert the watts to amps or get the amp rating off the device, this will tell you the minimal wire size, and then you will need to measure the distance from the breaker to the device, that will determine if the wire size needs to be increased for a long distance.
Example the 1500 uses 20 amps and 20 amps requires #12. 20 amps on a #12 is good for 100 feet anything further and you have to go up a wire size.
Take the amp rating and distance to the hardware store and they will have the chart and the correct wire for you to use. In the US 220 or 240 used to be three wire, 2 hots and a neutral through a double pole breaker, now the new NEC rules demand 4 wires for 220 volt devices, so you will need to check with whatever local code authority as to what they want on new installs versus replacement, if you are grandfathered in some way.
As to the four wires above, from the box, is that the heater box or circuit breaker box? In either case, the two hots go through their own breaker, called a double pole breaker, at the correct amperage rating. the white which is neutral and yes ground, is tied to the neutral bar in the breaker box, the bare or green, goes from the frame of the heater or the chassis, some common metal part, probably a green screw in the heater, and then in the breaker box, it will wire in with the rest of the bare grounds, this is a four wire 220 connection where they have quit using the white neutral as the only ground, and have insisted on adding this fourth bare chassis ground.
Once you have the correct wire size for the amperage, and the correct breaker size, and the wire size does not exceed the max limits for the size, you should be good to go.
However if you are concerned you can pull this off, pay a pro to do it, it is not worth a fire on a heater wiring job, for a few bucks on the install, it happens to often and not worth it, I have written on hear now several times, and have no responses, I have over thirty years in electrical devices including NEXRAD RADAR, motors above 5000 HP and understand all this, and the dangers.
Again wbwill@sbcglobal.net, or allexperts.com
I am not sure about fees, if there are any they go through this system in all fairness.
Will
Posted on Nov 15, 2008
Why do the house lights flicker and dim when I turn on my HP Laserjet printer? Once it shows it's ready, the lights return to normal.
1) The printer is on a circuit that is close to overloaded.
The printer power needed, is just enough to push the load, to the edge of too much.
I do not know what country you are in, but let me use the USA as an example.
The USA uses 120 Volts (AC)
In the Service Panel, (Circuit breaker panel), there are circuit breakers used for receptacles, and lighting. The standard size of circuit breaker to use for these types of circuits, is a 20 Amp breaker.
( 20 Amperes)
120 Volts times 20 Amps = 2400 Watts
(120 Volts X 20 Amps = 2400 Watts)
This is THE maximum load this circuit will take.
Come close to this maximum load (2400 Watts), and the lights may flicker.
Solution is to use a different receptacle, that is not as loaded with appliances, etc.
(The receptacle will be on a different circuit)
[ I would also remove some of the load off of that circuit. With 2400 Watts available, one should only use a load that is close to using 2100 or 2200 Watts.
This leaves a cushion of 200 to 300 Watts if needed.
If there is an appliance that has an electric motor in it, (Refrigerator for one example), you need a 'buffer zone' of at least 200 to 300 Watts.
Someone needs to go through, and see what all is connected to this one circuit. (One circuit breaker) Then that person needs to go through, and see that the circuit will not be overloaded, by varying what can be plugged into this circuit, or used on this circuit, at one time ]
There is another thing however that I would like you to have checked by a professional.
I need to explain how power comes into a Service Panel in your home, first.
There are 3 main large cables coming into the Service Panel, at the top.
(From the Service Meter can outside)
Two Conductor wires that carry the power, and 1 Neutral wire. (There is also a bare copper Ground wire. More on that in a moment)
http://www.make-my-own-house.com/diagram-electrical-home-wiring.html
Again, using the USA as an example, there is 240 Volts (AC) coming in to the Service Panel.
There are 3 thick wires covered in insulation. (Black)
One thick wire is 120 Volts. It connects to a power lug at the top of the Service Panel, inside the Service Panel, and connects to the Left side.
(Only seen if the cover of the Service Panel is removed.
You? NO. Professional? YES)
Another thick wire also carries 120 Volts, and connects to a separate lug at the top of the Service Panel, on the inside of the Service Panel.
This lug is on the Right side.
The last thick wire is a Neutral wire.
It connects to a lug in the Middle.
[ LUG = Square/rectangular piece of metal Base, with square piece of metal Top.
There is a screw going though the top, and into the base.
Tightening the screw squeezes the Top and Base together ]
Electricity coming into your home, or business is AC.
Alternating Current.
AC vibrates. It vibrates the wires.
After time the vibration can loosen the connection, of the wire to the Lug. (Screw vibrates loose)
This can also cause the lights to flicker.
With the wire connection being loose, Resistance is created.
Resistance creates Heat.
Heat creates FIRE.
Please have these connections checked in your Service Panel by a professional. I want you to be safe.
For additional questions, or to have me explain anything I have stated in more detail, please post back in a Comment.
Regards,
joecoolvette
Jan 21, 2012 | HP LaserJet 4 Printer
Trying to change plug from a 3pronge hookup to a 4.The dryer only has 3 wires to hook up extenstion plug has white,red,black,green ...what do i do
It is your responsibility
 To contact a qualified electrical installer.
 To be sure that the electrical connection is adequate and in
conformance with the National Electrical Code, ANSI/NFPA
70-latest edition and all local codes and ordinances.
The National Electric Code requires a 4-wire supply
connection for homes built after 1996, dryer circuits involved
in remodeling after 1996, and all mobile home installations.
A copy of the above code standards can be obtained from:
National Fire Protection Association, One Batterymarch Park,
Quincy, MA 02269.
 To supply the required 3 or 4 wire, single phase, 120/240 volt,
60 Hz., AC only electrical supply (or 3 or 4 wire, 120/208 volt
electrical supply, if specified on the serial/rating plate) on a
separate 30-amp circuit, fused on both sides of the line. A
time-delay fuse or circuit breaker is recommended. Connect
to an individual branch circuit. Do not have a fuse in the
neutral or grounding circuit.
 Do not use an extension cord.
 If codes permit and a separate ground wire is used, it is
recommended that a qualified electrician determine that the
ground path is adequate.
Electrical Connection
To properly install your dryer, you must determine the type of
electrical connection you will be using and follow the instructions
provided for it here.
 If local codes do not permit the connection of a neutral ground
wire to the neutral wire, see "Optional 3-wire connection"
section.
 This dryer is manufactured ready to install with a 3-wire
electrical supply connection. The neutral ground wire is
permanently connected to the neutral conductor (white wire)
within the dryer. If the dryer is installed with a 4-wire electrical
supply connection, the neutral ground wire must be removed
from the external ground conductor screw (green screw), and
secured under the neutral terminal (center or white wire) of the
terminal block. When the neutral ground wire is secured under
the neutral terminal (center or white wire) of the terminal block,
the dryer cabinet is isolated from the neutral conductor.
 A 4-wire power supply connection must be used when the
appliance is installed in a location where grounding through
the neutral conductor is prohibited. Grounding through the
neutral is prohibited for (1) new branch-circuit installations,
(2) mobile homes, (3) recreational vehicles, and (4) areas
where local codes prohibit grounding through the neutral
conductors.
Sep 23, 2011 | Estate EED4100SQ Electric Dryer
I have a Motor Guide Brute 767, 67 lb thrust 24 volt trolling motor. It will only run at about half speed even with new batteries.
I believe you may have a bad low voltage circuit board problem. I do not think they make the board any longer but you may be able to convert it to work by bypassing the circuit board. I am working on one now.
Mar 22, 2011 | MotorGuide STANDARD MOTOR REPLACEMENT...
I have a new ingersol rand 80 gal 7.5hp air compressor 230volt single phase and was wondering what size breaker it needs to be put on
Your owners manual spec sheet should give you that answer. However since that unit at max loads should pull 32 to 35 amps I recommend 1.5 times max amps. So approximately a 50 amp breaker. This all based on standard wire size and length of wire run. Also when checking your voltage at load you should be showing 235 to 240 volts.
Jan 09, 2011 | Ingersoll Rand - Rand Type - 30...
Electrical Short in Printed Circuit Board.
Hi, do you know what these wires were for? You can bypass the board, but if the wires are for lets say the blower motor and you bypass and put them to direct hot legs, you will run all the time, or what ever shorted the block in the first place must have a short. Its probably in the wires at this block and if you apply it to 120 volts it may fry again. I would follow these wires back to see what they run first. Yes, it can be done.
Shastalaker7
Jun 08, 2010 | Amcor PLM-14000E Portable Air Conditioner
I have a problem with a heater. It does not turn on and the circuit board was already changed, but the problem still continues. When the ignator was disconnected the black wire had power and if its...
not enough info on type of heater you have.
if it is a standard furnace with induced draft motor. the pressure switch must be satisfied before the igniter will get voltage to burn bright and light the gas in the burner.
Nov 24, 2009 | Coffee Makers & Espresso Machines
Re: 1/2 hp liftmaster Just installed new circuit board Neither sensor light works and the power sources at the board are not hot If I put the meter on the # 1 terminal and either #1 or #2 I get 34...
Are you sure you connected the wiring to the new board correctly? Terminal #1 should have a white wire with red tracer. Terminal #2 should have 3 solid white wires and terminal #3 should have 2 white wires with black tracer.
Does the opener do anything at all?
Jun 28, 2009 | Sears Craftsman LiftMaster Chamberlain...
Whirlpool GU2500XTP dishwasher went dead in mid-cycle.
"Wondering if this model has had reliability issues with the circuit card." ...If by circuit card you mean the electronic control board, that part number is used in many other models as well. In my experience with these control boards, I believe they have a low failure rate.
Make these checks if you haven't done so yet...
Check for 120V (breaker). Look for loose/shorted wiring connection at the dishwasher's junction box. Check all wiring connections to the control panel, electronic control and thermal fuse. Test the continuity of the thermal fuse (part # 8193762). If that's ok, you have already replaced the control panel so the problem is likely with the electronic control board (part # 8564546).
Good luck.
Mar 12, 2009 | Dishwashers
Sony kv-36xbr400
hi there, check-up the CRT board circuit. a video section problem, there maybe an electronic part defective. do some test and see any cold solder or loose connection on the crt board circuit. ty
Nov 15, 2007 | Sanyo HT32744 32" TV
High voltage surge
We regularly repair these GE / Samsung boards from customers nationwide with just such problems for $32.50. If it's too bad off, we can get this board (# WB27X10466 remanufactured) for $145. A new board runs about $180. We would need the full model number with suffix.
Sep 04, 2006 | GE JVM1490 Convection/Microwave Oven
Fahrenheat Electric Convector Baseboard Heater, 240 Volt Logo
212 people viewed this question
Top Fahrenheat Heating & Cooling Experts
butch welch
Paul Carew
Are you a Fahrenheat Heating and Cooling Expert? Answer questions, earn points and help others