Question about Goodman CLQ36AR49 Air Conditioner
My suction pressure is 90 psi liquid pressure 360 psi and my temperature ot te vent is 62 degrees f. what ismy problem?
  • Goodman Master
  • 43,501 Answers
I would say you are overcharged with freon...try dropping some of the gas out... with the proper equipment to recover the gas... it is illegal to vent it to the atmosphere...
You should be looking at 70-8- on the suction and 250-275 on the high side on a warm day and a good load on the the A/C say 75-80 inside temps...
Here is a tip about trouble shooting your air conditioner...
Air Conditioner Trouble -Review the Possibilities
http://www.fixya.com/support/r3571569-air_conditioner_trouble_review_the_possi
heatman101
Posted on Aug 07, 2010
Whatis ideal r22 gas pressure required in 1 ton split ac of BlueStar.
Doesn't matter how big the unit is, pressures remain the same. On a satisfied temperature, approximately 75 degrees, r22 should be around 65 psi. The hotter the house, the higher the pressure. Head pressure varies on outdoor temperature. 90 degrees outdoor temp, approximately 200 to 225 psi on high side.
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
Jun 05, 2017 | Heating & Cooling
How much r410 gas pressure in 1.5 ton inverter ac
Usually on any 410a freon system you can use a pt chart, and for any other freons also. At 120psig yours indoor coil temp is around 40°f. You want this temp/pressure above freezing. Your pressures are going to depend on indoor/outdoor temps. Hope this helps!
Mar 23, 2017 | Inverter Heating & Cooling
R22 unit running at 160/58. Took bulb out climbed to 61 on suction then right back to 58. Replaced txv. Charged to 220 head, suction stays at 60. Clean coil, no filter, good airflow. Ideas?????
Sounds like bad valves in the compressor.
A good indicator is how fast the pressure changes when you shut the compressor off. It should take several seconds for the suction pressure to rise. If it's immediate, then expect a bad valve.
Mar 07, 2016 | Heating & Cooling
On my 1996 ss impala what low side pressure should I see on the a/c with the system running
It all depends on the outside (ambient) air temperature. Your A/C low pressure switch is designed to turn the compressor off at 24 Psi. and turn it back on at 45 Psi. Most systems will normally run at between 25 and 40 Psi when the system is running on HIGH blower and "MAX" or "RECIRCULATE". A system that is fully charged may run at 25 Psi when the ambient temperature is 75 Deg. (F) and may run at 40 Psi when the ambient temperature is at 90 Deg. (F). (it can be even higher if ambient temperatures are higher than 90 Degrees.)
To properly diagnose a malfunctioning A/C system, the HIGH side pressure must also be checked. Restrictions in the system can make the low side pressure look normal while the high side pressure is high enough to blow hoses apart. (400+ Psi.)
Sep 04, 2011 | 1996 Chevrolet Impala SS
Actually a 2000 F-450, did not see a space for that year. 7.3 diesel. A/C issue. When first started up the A/C works fine, gets cold. But if I shut off the air for any reason the compressor will not cycle...
The A/C low side should read between 30 and 35 psi. Refrigerant pressure is indicative of its temperature, and 55 psi on the low side is too high and would only provide 60 degree air at the vents.
Aug 07, 2011 | 1999 Ford Super Duty F 450
When i was fixed a problem in central ac trane i found decreased in freon r22 and the suctione line was freezed, i charged the ac with froen gas r 22 then i found that the suctione line changed and begin...
You are still low on freon. Charging AC by superheat and subcool
First charging a unit by superheat, this is only for Acs with an orifice or capillary tube.
Optimum superheat is 12° to 15° at the compressor or suction line outside the unit.
Hook up your gages and put a thermometer on suction line (large line), start the AC. Measure the temperature of the suction line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant, (you can also use a temperature pressure chart), now read the thermometer, let’s say the suction temperature( the thermometer) is 67° and the saturation temperature (the gages or temp. press. Chart), is 55°, subtract the saturation temperature from the suction temperature, 67°- 55° = 12° superheat.
Charging by Subcooling, this is for Acs with a thermostatic expansion valve, it’s common to see a sight glass on the liquid line (on these units with a sight glass just clear it, when, indoor room is at approximate set point of the thermostat). Optimum sub cooling is 12° to 15° at the outdoor unit.
Hook up your gages and put a thermometer on liquid line (small line), start the AC. Measure the temperature of the liquid line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant,(you can also use a temperature pressure chart), now read the thermometer, let’s say the liquid temperature( the thermometer) is 100° and the saturation temperature (the gages or temp. press. Chart), is 114°, subtract the liquid temperature from the saturation temperature, 114°- 100° = 14° subcool.
Oct 05, 2009 | Heating & Cooling
Air conditioner in 1999 mercury tracer won't work. It's not the compressor nor does it have a leak. what could be the problem?
the tracer is the same as the ESCORT, right?? TRY THIS--I WORK ON PLENTY OF ESCORTS--LOOK UNDER THE AIR CLEANER/CONE ASSEMBLY--THERE WILL BE A BLACK METAL BOX(FULL OF RELAYS) ONE OF WHICH IS THE A/C RELAY--TRY TAPPING ON IT WITH A LONG SCREWDRIVER OR SOMETHING SIMILAR WHILE U HAVE THE A/C ON. IF THE A/C SUDDENLY STARTS WORKING U NEED TO GET A NEW RELAY BOX(I THINK ITS CALLED A GEM MODULE) i do have a question- does the blower motor work?? how do u know the compressor is good??do you have 12 volts going to it??? this relay box is pretty common to go bad--u have to remove the air cleaner in order to get to it.get back to me.
Sep 07, 2009 | 1999 Mercury Tracer
13 degree Delta T
I assume r-22 refrigerant by the pressure... you have a saturate temperature of approximately 41 degree and 71 degrees at the service port this equates to a 30 degree superheat. a condenser saturation temperature of 105 degrees and since the liquid line temp at the service valve is not given only the enterin indoor coil on the liquid line a 96 degree temperature this would equate to a subcooling temperatureof about nine degrees. You have too high of a superheat reading. verify that the bulb for the txv is correctly positioned and insulated. if it is then you need to remove the bulb from the suction line, hold it in your hand to warm it up and see if the superheat changes. you could also have issues with your ductwork. If the supply temperture is around 50-55 degrees then the unit is doing all it can.. Check the txv and the ductwork as the subcooling indicates that the condenser side is doing it's job, but the superheat readings indicate that you are starving the evaporator..
Jul 28, 2009 | Heating & Cooling
96 Tahoe no Cold Air
YOU NEED 28 PSI ON LOW SIDE AND ABOUT 190 ON HIGH SIDE.YOUR REFRIGERANT IS LOW THAT WHY COMPRESSOR CYCLING ON AND OFF.
Jul 22, 2009 | 1996 Chevrolet Tahoe
Goodman CLQ36AR49 Air Conditioner Logo
143 people viewed this question
Top Goodman Heating & Cooling Experts
Paul Carew
Tim Whalen
christian nielsen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others