Question about Teledyne Laars Laars Lite2 Heater 175000 BTU NG Elec Ign
Heater burner will not light even though pilot is lit.
  • kejones05 Aug 06, 2010
    The capacity stated is incorrect. My heater is rated at 399000btu/hr.
  • 11,896 Answers
If the pilot is on, then it is getting gas. Like the control unit is not kicking on.
Sequencer or heating relay acts like a 24 volt x 120 volt contactor to make the 24 volt thermostat current to allow 120 line voltage to the inducer, for the very first function of the furnace. Without that inducer running, the 24 volt safety circuit cannot function to allow current to get to a control board or module.
Other components include: ignitor, flame sensor, bad pressure switch, dirty burners, bad gas valve, or bad filter can also cause this.
If you have a combination NO, NC 3-wire pressure switch that requires the pressure switch to close current when the inducer is NOT running yet (to thwart people who put jumper wires on one), that pressure switch may be sticky or bad contact inside it, and not closing down(or making good contact) after the furnace shuts off sometimes!! You could jumper the NC terminal and see if at least the inducer runs. Or even **** or blow on the pressure switch tube, into the pressure switch, to see if the pressure switch is sticky. You'd know if by doing so, the inducer were to start up. And by doing repeat tests with and without it, to rule out coincidence, then you'd know if the pressure switch was faulty or not.
Posted on Aug 06, 2010
Burner won't light, pilot is burning just fine.
Once you get the pilot to light and stay lit did yall move the burner knob to the ON position? Is the temp knob all the way up?
If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61
Nov 27, 2011 | Procom Heating & Cooling
I have a Model CGN250TE.The pilot light stays lit but when you turn control valve on it stays lit for 5 seconds and then shuts right down,even the pilot light goes out.I have tried venting the room and...
I would first check the gas pressure to your furnace. Then make sure that burners are clean and watch flames when burner first ignites. I have seen burners that were dirty cause delayed ignition that would create a suction when they came on and extingush pilot and burners.
The next thing I would do is change gas valve. Thank you
Dec 19, 2010 | Williams 2509612 Ceramic Mid-Size Heater
The pilot light & will stay lit. untill the burner cycles on/off
MAKE SURE THE BURNER TUBE AND ORIFICES ARE CLEAN. MAKE SURE YOU HAVE THE PROPER LP PRESSURE.
Oct 05, 2009 | RTO Atwood Water Heater - 6 Gal LP
Water heater pilot wont stay lit
try cleaning the top of the pilot light jet if you can get to with small brush then blow it clean with a compressor.
Aug 30, 2009 | Rheem 50 Gallon FVR NATGAS Water Heater...
Pilot lit clicking noise no burner
make sure knob on gas valve(inside heater)is turned to on position.3/4" should be fine as long as heater is not larger than than 175,000 btu
Jul 14, 2009 | Jandy Lite 2 Natural Gas Pilot Light...
Water heater pilot light
it also sounds as though the pilot injector could be blocked so when the boiler comes on it extinguishes the pilot & then when the burner goes off boiler shuts down, or also the pilot rate maynot be set right, so when the main burner kicks in it robs the pilot of the gas it requires.
It could be that, or there is lack of ventilation for the boiler, so you get flame lift off when the boiler fires?
Dec 14, 2008 | Water Heaters
Teledyne Laars Laars Lite2 Heater 175000 BTU NG Elec Ign Logo
48 people viewed this question
Top Teledyne Laars Pool & Spa Experts
Paul Carew
Craig Butler
Craig Butler
Jay Finke
Jay Finke
Are you a Teledyne Laars Pool and Spa Expert? Answer questions, earn points and help others