Heat pump not running
The outside unit for my heat pump does not turn on...either on heat or AC. The air handler works fine. I've checked the breaker in the main electrical panel, and i did a continuity test on the fuses in the outside box next to the unit. Do you have any other suggestions?
    Problem Solver:
  • 10 Answers
Depending on the age of the unit it could be several things, does it have a circuit board? Contactor could be bad, freon leak if it has a low pressure switch, burnt wires, connections, etc. Do a complete visual and check for 24 volts, does the indoor unit run? Transformer may be bad.... No indoor unit - no outdoor unit, most of the time the outdoor unit gets its 24 vac power from the indoor unit which runs them both, look for fuses (like car fuses)..
Posted on Apr 26, 2008
Lennox ac stops working after normal shutoff untill i shut off power to air handler turn power back on ac runs till nornal temp reached shuts off will not come back on untill i kill power to air handler...
The 13HPX is a Heat Pump. It has a control board in the outside unit that will lock out after a few trips from one of the controls, such as a low or high pressure switch tripping. Turning the power off is making this board reset. Take the door off next time. to the outside unit and look at the lights on the control board. There should a sticker on the inside the door that you have to remove that describes why the unit is hard locking out according to the light configuration.
Oct 24, 2017 | Heating & Cooling
My air handler fan does not come on, the outside unit turns on fine. Is their a way to reset the fan?
Check for fan operation by turning the fan control at the thermostat to "on". If the fan blows, it works. If not, check a circuit breaker or fuse.
If the fan blows when forcing it on with the thermostat but not in automatic, check the fan control circuit in the air handler. Danger: high voltage, beware! There should be a system wiring diagram inside the air handler somewhere.
Mar 30, 2014 | Rheem 4 Ton Air Handler - RHLLHM4821JA
I have a goodman gsc13 ac unit about 4 year old. When the temp gets around 90 or above outside the fan on the unit starts but the compressor does not. I had service check it out but that day they were...
It sounds like the unit may be over charged. Make sure the outside coils are clean and you have plenty of airflow coming out of the top of the outside unit. What could be happening is, when the temps get higher outside, so do the pressures in the system. The compressor has a thermal overload protection that will kick the compressor off if it gets to hot, which if the compressor is over charged, it will work twice as hard, over heat and shut off. You would need a technician to come out and get the refrigerant charge back to normal. Another thing that could be happening is a weak or faulty capacitor, which is a small round or oval metal object, found in the electrical compartment on the unit. This are fairly simple to change out if your comfortable with electric. I've also had to put what's called a hard start kit on compressors with the same problem, new and old. The hard start basically gives it that extra boost of power to get it up and going. I would start with the refrigerant charge and go from there. The electrical "humming" sound that you hear unless you turn the breaker to the furnace off, is the contactor on the outside unit having a call for cooling. The 24 volts come from the furnace, to the outside unit, and pulls the contactor in to power the unit with the 220 volts supplied. It is normal and you don't have to worry about that at all. I hope some of this helps and good luck!
Jul 05, 2011 | Heating & Cooling
I just turned on our heat unit "FA4A AC/Heat Pump"
There probably isn't a reset button=magic fix. With it in heat pump mode and tstat set above indoor temp, check your outdoor unit to see if it's operating. If not, check all breakers to it. Can you see any ice accumulated on the outdoor unit? If it is running and not producing heat, turn the tstat to emergency/auxiliary heat. and the heat pump turned off to prevent damage. You'll need a service tech.
Nov 04, 2017 | Heating & Cooling
Energy Knight heat pump refuses to blow!
Does this problem happen when the temperature is below 30 degrees? When it gets about that cold outside, the air outside is too cold for the heat pump to "steal" heat from. On the thermostat you'll find a switch labeled aux or emergency heat. Turning this switch on will operate a traditional coil heater inside the system, providing you with heat. The only downfall to this is that it uses more energy to heat this way. Try turning the fan switch from "auto" to "on". If the fan comes on, then we can rule that out. If the aux heat switch is NOT on, set the thermostat such that the system will try to heat. If the outside unit is running, the problem is either it being too cold like I said earlier, or there's a problem with the heat pump's mechanical system that needs to be serviced by a professional. If the outside unit doesn't run but it should be, check it's breakers at the panel, the breaker inside the electrical box that feeds it, and look to see if there's a reset button on the unit itself. Finally, check the air handler (part of the system inside with the fan in it) to see if there's any circuit breakers or fuses on this unit. Make sure they're not tripped/blown. If none of this helps, you definitely want to get a pro to work on your system.
Feb 27, 2010 | Heating & Cooling
Compatability of a R22 air handler and a R410a heat pump
1. The units should match up without a problem.
2. You will need a 40 or 50 amp breaker for the A/H and 5 KW heat strip. You will probably need a 20 or 25 Amp for the condensing unit. I would check the FLA (full load amps) rating on both units, total them and install a breaker with no more than 20% more rating than the total. You can install a small box at the A/H with a breaker for the A/H and one for the condensing unit.
Nov 15, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...
Heil Max Performance 10 Heat Pump not working
First check to see if you have afloat switch inside the air handler ar underneath the air handler. Its purpose is to shut the outside ac off if the drain stops up. Very common. If this is OK take cover off unit and with screw driver push in the contactor. It is located about the middle of the panel. It has main power at the bottom. If unit comes on you cave a control voltage problem. Meaning something is not allowing 24 volts to the contactor. If your out of Refrigerant the low pressure swich will have it off. Call a service tech. Rusty
Jun 09, 2009 | Heating & Cooling
3 amp fuse blows on a carrier 58mcb furnace board
Hi!!! Does your ac unit work fine?If not check your low voltage problem..You have a low voltage problem check the wire going out to your condensor make sure that they are not touching..Good luck..Check low voltage wires..short in progress..
Jan 04, 2009 | Carrier 52CQ-312-4 Comfort Series Heat...
Ruud heat pump question
Does the air handler take a minute or two to start, this would be normal so that it doesn't blow cool air into the house before the unit is warmed up. If not could be the fan relay is weak and needs replacing. As far as the outside unit it sounds like you need to check the refrigerant. In cooling they are 70/150 psi. This should be checked in cooling mode, once you turn it to heating mode the pressures switch bring heat inside the house instead of out. I hope this helps.
Oct 23, 2008 | Ruud Heating & Cooling
AC breaker trips after 10 minutes
Whats the amp breaker? Is this for the inside unit or the outside condenser? If the inside and gas heat you have a bad fan motor, If its an electric furnace , the same, but if its the outside unit, the fan could be going bad, locking up and the compressor still runs and pulls high ampsand tripps breaker or the compressor is just pulling too many amps due to plugged coils with dirt , grass or weeds blocking airflow.(koolbreezes74401@yahoo.com)
Jun 08, 2008 | Goodman CLQ36AR49 Air Conditioner
Heating & Cooling Logo
144 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster