Evaporator is not cooling, but compressur is ok and indoor fan is ok
  • 407 Answers
This happens when the charge of refrigerant isn't correct. If everything is working properly, then the best way to check the charge without the right equipment handy is to look on the big copper line on the outside unit, preferably in the heat of day, and it should have condensation on it while it is running. If you have no water forming on the big copper line set, then you are low on refrigerant. Hope this points you in the right direction and good luck!
Posted on Aug 04, 2010
How to troubleshoot thermostat wiring?
I'm not sure if the thermostat is wired correctly. First, the thermostat is wired directly to the outdoor unit (compressor/condenser unit). It is NOT directly connected to the indoor unit. It connects to a low voltage control panel in the outdoor unit that sends a signal to your indoor fan/evaporator. This wire is called the fan relay switch and physically runs between the low voltage controls of the indoor and outdoor units. If the fan relay is bad it's possible that the unit runs continuously. To prevent destroying your outdoor unit there is a safety feature that prevents the indoor fan from shutting down while the outdoor unit is running. If the indoor fan did shut down while the outdoor unit was running than you would slug your compressor. That is, your compressor normally sees refrigerant gas but is instead seeing refrigerant liquid. That would not be good since this scenario would destroy your compressor. It sounds like a faulty fan relay. The actual contactor portion of the relay is in the outdoor unit.
Aug 22, 2014 | Honeywell Electronic Programmable...
Flashing light the at says e6
Usually Indoor Unit Anti-freezing protection (Cooling
Mode) or Over-heating Protection (Heating Mode)
for Evaporator
A) Indoor room
temperature too low
under cooling mode,
Too high under
heating mode
B) Indoor unit filter or
evaporator too dirty
C) Indoor unit fan motor
blocked
D) Insufficient refrigerant
under cooling mode
E) Indoor unit evaporator
sensor wrong
connection or failure
Jul 28, 2014 | Samsung AQV12VBE Vivace Wall Heat Pump Air...
Too hot little cold
Very possible your condenser is extreemly dirty and is turning off on a high pressure cutout. suggest you clean out condenser with compressed air. Brushing is not enough. also, check if condenser fan(at the compressor) is working.
May 21, 2010 | LG Heat cool Window Air Conditioner
Evaporator coil continue frosting\build up ice
check the indoor fan motor, the indoor fan motor has to be running while condenser is on. make sure the filter is clean and the return vents are not blocked. Check charge.
Dec 16, 2009 | Carrier Heating & Cooling
Electric fans don't run, but checks Ok. Air condition not working. compressure checks Ok,but clutch not engageing but can jump wire clutch to engage. All fuses checks good,
FIRST IS CHECK ENGINE LIGHT ON....YOU SHOULD BE ABLE TO UNPLUG THE ECT... ELECTRONIC COOLING TEMP SENSOR.....A TWO WIRE SENSOR THAT TELLS THE COMPUTER THE TEMP OF MOTOR....WHEN THE MOTOR TEMP GETS HIGH THE COMPUTER GROUNDS THE COOLING FAN RELAY TO TURN FANS ON..IF FANS DON'T RUN WITH SENSOR UNPLUGGED THE GET A SMALL PIECE OF WIRE AND FOR A SHORT TIME SHORT THE TWO WIRES ON THE PLUG FOR SENSOR...IF IT DOES COME ON REPLACE SENSOR IF IT DOES NOT COME ON SUSPECT COMPUTER...ONLY IF ALL FUSES ARE OK LET ME KNOW
Sep 03, 2009 | 1994 Buick Century
I have a lg 1.5 ton split ac , problem is compressor trip in 5 to 10 minutes ang agin start in 10 min..i will call service centre , he wl change capactor and service indoor n outdoor unit ,but problem will...
first check the compressor amps and the condenser fan rotation are correct if ok check power come to the compressor without interuption (from control in the indoor unit)if the remote setting are ok correct voltage to the compressor may high pressure stop it or low pressure compressure overheat.and if this was repeated many time the best to change the compressor.
Aug 28, 2009 | Heating & Cooling
Goodman PGJ030075-1 Motor Not Spinning - No Cool Air Blowing
I assume you are talking about the evaporator fan motor. Check the capacitor. Replace if necessary. If cap shows good then it's most likely the indoor fan motor.
Jun 05, 2009 | Heating & Cooling
Compressor will not start.
Usually short cycling means that High side pressure is getting to high (due to not working condenser fan, or dirty condenser coil), or low side pressure is getting too low (might have low level of freon or restriction in sealed system). low side would drop dramatically if indoor blower is not running, so if air is not circulating thru evaporator coil, coil will freeze up and low side would be much lower then normal. Here is video how I found issue with package AC not coming on. Thermostat call for cool, but condenser would not come on, indoor blower runs ok.
Nov 02, 2008 | Ruud UAMB Air Conditioner
Amana heat/air conditioning pump
You are going to have to increase the amount of heat absorbed by the evaporator coil on the indoor section of your system. First change the filter. Second turn the power off to the outdoor section and leave the indoor fan running until all the ice on the evaporator coil has thawed this could take a few hours. Third you need to verify that you are getting adequate airflow across the indoor evaporator coil and the outdoor condenser coil both fans should be spinning at full speed and airflow should be unobstructed by dirty coil fins or debris Hopefully after you've done this you will have cold air blowing inside and the larger of the two lines entering the unit outside will be cool to the touch but not frozen or even frosted regardless of run time and the small one should be the slightly warm but not hot. If the larger line continues to freeze then it could indicate a number of problems but essentially your condensers cooling capacity is outrunning your evaporator coils ability to absorb heat from air stream circulating in your home.Hope it works out for you GL!
Jun 10, 2008 | Amana PTH123B25AJ Heat Pump Air...