Question about Weather King 12AJA3601AH Air Conditioner
Low charge? weatherking 14.5 seer, r-410, low side 135#, highside 255#, 85 deg. ambient temp, liquid line temp around 84 deg. suction line temp about 64. house thermostat at 78 deg. looking for 72 deg. register putting out about 62 deg. can we damage anything until we can get tech support? what should normal operating ranges be?
    Novelist:
  • 117 Answers
System is running a 24°F superheat and a 0°F subcooling at those readings. Saturation temperature is approx. 30°F lower than return air temperature.
Indications are of a low system charge. Ensure all your filters are clean and there are no obstructions that are limited airflow across the evaporator coil. Ensure the coils are clean and not frozen up.
Have it checked out. Looks like a low charge but can't tell without being in front of it. As far as normal ranges, that all depends on many factors. Based upon the info you have supplied, I would guesstimate that the operating pressures would be in the neighborhood of 350/160 to start and get the subcooling and superheat in check.
Posted on Aug 01, 2010
How do you put in 410a into Ac unit
You turn system on to cool setting and run temp down until outside unit comes on. Then you connect your suction side of your gauges to the suction side of your outdoor unit. Next you connect the liquid(high)side of your gauges to the liquid line on your outside unit(the little copper line). Connect the middle hose of your gauges to the 410a drum of refrigerant. Before opening the suction or low pressure side of the gauges you need to turn the drum upside down and turn drum of 410a on. Then you need a temp reading meter and clamp to read the temp of your liquid line(small line). While charging you want to make sure to release refrigerant slowly. The unit should call for a specified subcooling on unit plate. 7 to 10 degrees. You take the liquid line temp and subtract it from saturation temp on the high side of your gauges.(it'll be the pink numbers on the right side of your gauge.
Jun 05, 2013 | Heating & Cooling
Charging an air conditioning system
R22 systems should run a 68# to 70# suction pressue. If you look at the suction guage at 68# that is a 40 deg evaporator coil temp.
Nov 18, 2012 | Ruud Central System Air Conditioner
How 2 add r22
The best way is weigh in a charge. of course the type of unit will come into play as split systems have enough refrigerant factory for up to 15 ft lineset or so, depending on units make etc. If a charge exists already and requires adjusting due to lineset length, or repairs etc, youcan simulate a 95 degree day ambient outdoors by restricting the air flow a bit to artificaially raise the head pressure as do low ambient controls, thus bringing the head to around 270lbs in a r 22 system or ambient plus 30 degrees , converted to prressure, so a 95 deg day plus 30=125 deg converted to pressure is 269 lbs, the indoor air temp being clse to 80 degreees helps, the indoor coil will be 40 degrees cooler than the indoor ambient if all is normal and design conditions are met by God or you. If the indoors 75, go to a 35 d
eg coil temp this is ball park, as the subcooling (15 deg)and superheat (10 at the evap coil, 20 at compressor) will need to be monitered along with amp draw and Delta T or temp differntials suply vs return.2_25_2012_2_55_05_am.png
Feb 24, 2012 | Heating & Cooling
Hello, I have a Calvinator A410 unit that I am working on it is a heat pump, I had a leak remove freon and vacummed for around 5 hours. Having a problem charging the unit as a thermo protect on the...
There should be a name plate with the model and serial # which will tell you what the factory charge is for the unit plus 15 to 25 feet of line set. If you weight in the charge you should be pretty close...... In AC mode you should run around 125# suction and about 265 head pressure with 70 degree ambient F. If you have the right charge in the heat pump and you are still running 25# suction pressure in the Air Condition mode then you have a restriction filter drier or TXV locking up..... Did you replace the filter drier when you fixed the leak was the leak on the suction side if so then you definitely need to change the filter drier.
May 01, 2011 | Heating & Cooling
I have a pane heat pump during the summer it worked great but now the heat pump dont seem to be heating the temp on the suction line is 160 f out side air is 58 and in door temp is68 f . on my gauges the...
Is the reversing valve sliding ok?
sometimes they get sticky you can try taping it to free it into correct position to allow full heating mode.
Jan 25, 2011 | Heating & Cooling
Goodman Condensor cplj48-1 Air handler Modle
It sounds undercharged (needs more refrigerant). Based on the conditions in your post and assuming the indoor humidity is within 20-70% range, your target superheat should be 10degF. Your superheat (assuming you have an R22 system) is far too high. The pressures are not indicating a restriction; therefore, I have to conclude you have a low charge. A low charge will cause a gurgling sound due to the refrigerant in the liquid line is vaporizing prior to reaching the Cap tube at the Air Handler.
I hope you find this information helpful to you moving forward. :-)
May 10, 2010 | Heating & Cooling
I am working on a GE Weathertron Heat pump (Mod# BWB924A100C1; Ser# 264082948). The complaint is it is not heating as well as it once was(running a long time to heat up house). I checked the pressure, the...
It is very hard to charge a heat pump in the heating mode. The pressures are low. It also depends on the outside ambient temp. If you can turn to cooling if inside temp is above 70 degrees. Take a piece of plastic and block condensor till you get your head pressure to about 235. Not discharge temp but liquid pressure near service valve. You do not have a TXV inside I believe. Get your suction pressure up a little more It is not to low on gas. If you have temp meter attatch a lead to suction line. Temo\p should be about 10 to 14 degrees difference Between suction temp and Temp on your suction gauge. If you need a charging chart I can fax you one. Rus
Dec 04, 2009 | Heating & Cooling
Air conditioner in 1999 mercury tracer won't work. It's not the compressor nor does it have a leak. what could be the problem?
the tracer is the same as the ESCORT, right?? TRY THIS--I WORK ON PLENTY OF ESCORTS--LOOK UNDER THE AIR CLEANER/CONE ASSEMBLY--THERE WILL BE A BLACK METAL BOX(FULL OF RELAYS) ONE OF WHICH IS THE A/C RELAY--TRY TAPPING ON IT WITH A LONG SCREWDRIVER OR SOMETHING SIMILAR WHILE U HAVE THE A/C ON. IF THE A/C SUDDENLY STARTS WORKING U NEED TO GET A NEW RELAY BOX(I THINK ITS CALLED A GEM MODULE) i do have a question- does the blower motor work?? how do u know the compressor is good??do you have 12 volts going to it??? this relay box is pretty common to go bad--u have to remove the air cleaner in order to get to it.get back to me.
Sep 07, 2009 | 1999 Mercury Tracer
13 degree Delta T
I assume r-22 refrigerant by the pressure... you have a saturate temperature of approximately 41 degree and 71 degrees at the service port this equates to a 30 degree superheat. a condenser saturation temperature of 105 degrees and since the liquid line temp at the service valve is not given only the enterin indoor coil on the liquid line a 96 degree temperature this would equate to a subcooling temperatureof about nine degrees. You have too high of a superheat reading. verify that the bulb for the txv is correctly positioned and insulated. if it is then you need to remove the bulb from the suction line, hold it in your hand to warm it up and see if the superheat changes. you could also have issues with your ductwork. If the supply temperture is around 50-55 degrees then the unit is doing all it can.. Check the txv and the ductwork as the subcooling indicates that the condenser side is doing it's job, but the superheat readings indicate that you are starving the evaporator..
Jul 28, 2009 | Heating & Cooling
Air conditioning spilt system
I have to know what the outside temp is and I also need to know the seer of the unit. It would also help to know what the indoor temp is as well. Generally your suction pressure or what you are referring to as the indoor temp will be about the same. Let's say your indoor temp is 75, then your suction pressure should be around 75psi as well. Based on the suction pressure you just gave me, I would bet that the temp is not 38 degrees. With the suction at 38 and a low head or high side, you may be low on refrigerant. 110 is a little low but again, this depends on the seer rating of the unit. A higher seer will have a lower head.
Apr 08, 2009 | Heating & Cooling
Weather King 12AJA3601AH Air Conditioner Logo
153 people viewed this question
Top Weather King Heating & Cooling Experts
Tim Whalen
John Tripp
John Tripp
acrman404a
Level 1 Expert
Are you a Weather King Heating and Cooling Expert? Answer questions, earn points and help others