New goodman 2.5ton and 2.5-3.5 airhandler installed 8weeks ago, worked well for about a week, then the problems begain, heatpumps reversing value replaced already, but unit still does not cool well,when first install air coming out of inside vents were between 55-60, now air coming out of vents cane range anywhere between 64-70, the hotter the day outside the worse it gets, also on hot days the unit runs all the time in three hot days only shut off once or twice and that was for only 3min at a time, any suggestions would be helpful, the company that installed the unit has been great, out numerous times, have contact Goodman, with no luck to date.
    Scholar:
  • 66 Answers
There could be several things wrong. The unit could be undersized but since it worked fine in the beginning, we'll rule that out. There could be a refrigerant leak. Check and see if the evaporator coils (inside furnace) are sweating all the way to the top. The new refrigerant in these units makes it absolutely critical they be charged correctly. The expansion valve also requires adjusting sometimes, if so equipped. Just keep talking to the installers. It sounds like they will eventually get it right for you. Sometimes it takes several trips to get everything adjusted perfectly.
Posted on Jul 28, 2010
WIREIN HEAT PUMP FOR COOLING ONLY
You must wire Orange from heatpump low voltage wire to gether with your yellow s and you must have a common wire usealy common comeing out of heatpump should be black color than what ever color wire you have connected to common at t-stat and airhandler connect that to black wire at heatpump. To make sure blablack I s common follow wire up to board and it will be connected to C terminal now you will have ac all time. If you want heat remve Orange wire from reds at heatpump and you will get heat only.note when doing your wireing make sure high voltage is off to heatpump and airhandler hope this helps
Feb 27, 2015 | Carrier 52CQ-312-4 Comfort Series Heat...
Goodman SSZ140481AG, what is it? is it 14 seer or 15 seer? I paid for 15seer but the unit has a decal on it reading 14 seer??? Thanks
It is federal law that each new piece of A/C equipment have the yellow SEER rating.
The higher the SEER, the less electricity the system uses to operate.
You need to follow up since it appears your contractor installed a less efficient/expensive system than what you paid for.
Good luck.
Sep 15, 2013 | Goodman CACF048B2A Air Conditioner
We just installed a dometic heat/air pump .#630515.321/65151.301co .the thermostat is not reading the heat pump and it also will not stay lite. Can you help?
It sounds like you have a problem with your wiring. You have to make sure that all signals are complete through out wiring. Ex. Y goes to the outdoor unit on usally yellow, G goes to the g signal on the airhandler, W goes to he w signal in the airhadler and outdoor unit. O/B goes to the oudoor unit, R goes to outdoor and airhandler, C goes to outdoor and Airhandler. Check your wiring and also make sure you have the correct thermostat, meaning you have a heatpump thermsotat.
May 08, 2011 | Dometic Heating & Cooling
New heatpump suction line gets hot when ac is calling hooked to new 95% goodman furnace
Is it blowing out hot air? If so, unit could be wired backwards or you are having problems with reversing valve
Jun 11, 2010 | Heating & Cooling
Thermostat Wiring Problems!!!
. your blue is probably common and if you hooked it to Y you shorted the transformer or blew the low voltage fuse. Green is fan, yellow is AC, Red is 24volt. Is it a heatpump or just ac? I think its probably a heat pump and your brown is your Reversing valve it needs to be hooked to O on the new stat. If its a heatpump your tstat must be a 2heat 1 cool stat w/ aux heat. Without knowing what terminals the wire were hooked to on the old stat you may have to look at whats hooked up at airhandler( furnace) and on A/C (heatpump) tobe able to determine what goes where on the new one.
Sep 20, 2009 | Heating & Cooling
When your compressor on heatpump burns out how do you clean the system before installing new compressor
Flush the system with Nitrogen. Then R-11. Then install low side and high side filter driers. Then replace the low side filter drier after 2 weeks running time.
May 19, 2009 | Goodman CLQ36AR49 Air Conditioner
Heatpump A/C not working
First,Turn on the heat cycle (Not Emergency)and see if the outside unit come on,If not,and you don't have low voltage outside,Go to the inside unit and test the transformer,If you have low voltage from the transformer but not outside,It is the low voltage wires,If you don't have low voltage from the transformer,It's the transformer.If you have low voltage outside when in heat mode,but the unit won't come on,It's the contactor.Let me know if you need more help.
Please take time to rate this fixya
May 13, 2009 | Goodman CLQ36AR49 Air Conditioner
Goodman heatpump. Crazy pressure in heat mode
Check the TXV valve on the outdoor unit, it could be stuck closed. We have been experiencing the same problems with the 410 systems and the TXV was the culprit. Good Luck
Dec 19, 2008 | Goodman CLQ36AR49 Air Conditioner
Disconnecting green wire from thermostate did allow furnace to run properly but every time I want to switch back to heatpump I must reconnect green wire again.Here is how wires are connected to...
Try this.
A T-stat.
Orange = O
Red = R (with existing jumper)
Black = C
Yellow = Y
White =W1 (Or AUG)
Green =G
At airhandler/furnace.
Green = blower wire (usually green, double check with schematic)
(Green should not go to the HP.)
Orange to HP
Red to red and to HP
black to blue (or C) and to HP
White to W
Yellow to HP. (It may also go to a "float switch" if installed. but that will just be a safety switch on the drain pan in case the line clogs and it overflows.)
The green is typically used for the blower motor. (furnace only)
The orange is used for the reversing valve. (changes from AC to heat, is located in the HP only)
Blue is typically used for common (or "C") but they may have changed it to black due to a broken wire, or other problems.
The only wires going to the HP should be
Red
Blue/black
orange
yellow
Orange should not be going to the furnace at all.
HP wiring should be
Orange to orange or O
Red to R or red
Blue/black to blue or C
Yellow to Y
Dec 09, 2008 | Heating & Cooling
Goodman Heat pump
GOODMAN HAS A PROBLEM WITH A FAULTY REVERSING VALVE. THEY IMPORT VALVE FROM CHINA AND ITS NOT GOOD QUALITY, THEY ARE IN PROCESS OF CHANGING VENDOR.