Question about Samsung Heating & Cooling
My outdoor unit is # US18AORCD. The problem that I have is that the compressor don't start but the fan is running well.
  • 2,272 Answers
There are few possibilities that has to be checked. a bad capacitor,contactor,or other electrical device in the compressor power line could also be the problem . Check for the coils.If they are dirty or very old clean them properly and recheck.Check the compressor connections.Check power to the compressor.If the power is low then there is open circuit between any two terminals on the compressor.Re check all the connections and then see. If there is 24v at coil of contactor and 240volt at line with contator closed...then [if neither compressor or condensor fan are running]:
1. Faulty contactor or
if fan running but no compressor then
2. Faulty run
capacitor if compressor running but fan not running then, 3)The fan motor is faulty.
You need to identify if you have both line voltage [240v] and control voltage [24v] at outdoor unit before identifying
this as a problem.
Thanks. Keep updated for any more query. You can rate this solution and show your appreciation.
Posted on Jul 18, 2010
How to troubleshoot thermostat wiring?
I'm not sure if the thermostat is wired correctly. First, the thermostat is wired directly to the outdoor unit (compressor/condenser unit). It is NOT directly connected to the indoor unit. It connects to a low voltage control panel in the outdoor unit that sends a signal to your indoor fan/evaporator. This wire is called the fan relay switch and physically runs between the low voltage controls of the indoor and outdoor units. If the fan relay is bad it's possible that the unit runs continuously. To prevent destroying your outdoor unit there is a safety feature that prevents the indoor fan from shutting down while the outdoor unit is running. If the indoor fan did shut down while the outdoor unit was running than you would slug your compressor. That is, your compressor normally sees refrigerant gas but is instead seeing refrigerant liquid. That would not be good since this scenario would destroy your compressor. It sounds like a faulty fan relay. The actual contactor portion of the relay is in the outdoor unit.
Aug 22, 2014 | Honeywell Electronic Programmable...
My condenser fan runs and blows cool air but isnt cooling down the house. Any help.
Check the outdoor unit (condensing unit). Keep in mind, because the condenser fan is running it's not an indication that the compressor is working. On a split system,there's a dual capacitor that serves the fan and the compressor. The capacitor has three terminals.
1. common
2. fan = fan
3. Herm = compressor
This is a common problem; The outdoor fan (condenser fan) runs, but not the compressor (you have to know the sound of a running compressor or you'll mistake it for the sound of the fan) doesn't, because the compressor side of the capacitor is too weak to give it that needed phase angle that it requires to start. If you're referring to the outdoor fan spinning, but no cooling, I can bet the compressor isn't working and needs a new capacitor. Very common problem, I see it all the time. Before you change the capacitor, make sure that you cut the power to the unit, and then use an insulated tool such as a screwdriver and short the terminals together first. A capacitor holds a charge even after being de -energized.Buy the new one with the same exact rating written on it as the old one. Do not mix up the wires when replacing. Write it down or take a picture with your phone
Aug 20, 2013 | Heating & Cooling
Indoor fan barely turning
the three post capacitor has c for line voltage in, the f or fan is for the outdoor motor,and com or comp goes to start winding compressor.youll have to follow wires from indoor motor to find capacitor. to find wires to outdoor motor to capacitor you have line voltage and capacitor wires .look for schematic it would help or send colors of wires from both motors and compressor common,start .run.
Jun 07, 2013 | GE Zoneline AZ55H07D Air Conditioner
My ac central air is blowing air but not cold
Problem #1:Outdoor condensing fan motor has stopped running. This problem could be caused by a bad motor run capacitor. If your motor capacitor is not the problem, then more than likely you need a new motor. Is the fan blade tight, stiff or hard to turn? If the fan blade is hard to turn then you probably need a new motor. Problem #2: Air conditioner compressor will not start. When power is applied to the air conditioning outdoor unit the fan starts, but you hear a sound like the compressor is trying to start, "UGGG"..., for about 5 to 10 seconds and then all you hear is the outdoor condenser fan run. The compressor is locked and will not start. What is happening is the compressor is trying to start, but because the compressor motor is locked it tries to start for a few seconds and then because of the high amperage being drawn goes off on internal overload. The internal overload protects the compressor windings from overheating and burning up. I see this many times during the start of the air conditioning season. Some compressors just have a hard time starting after sitting all winter long. Some compressors are locked up so bad that I can not start them and must tell my customer that they need a new compressor . Many times I can get the compressor started again without having to buy a new compressor or new air conditioning system by using the device known as a "Super-Boost." I keep two or three of these on the truck. They have saved many of my customers from having to buy new air conditioning compressor. Another good device is called a "5-2-1" kit.
Jun 22, 2011 | Goodman CKL36AR36 Air Conditioner
My carrier 38CKC (60) is blowing hot air. The fan seems to be running fine. Is it the condenser coil, or just needs freon? How do I know? The unit is about 8 years old and never been serviced (I know...I...
Assuming the outdoor unit is running, make sure the fan motor on top is turning and the compressor is running. They both must operate for the unit to function.
The easiest and most common problems:
1. Condenser coil is stopped up with dirt. The condenser coil is the radiator looking coil that wraps around nearly the whole outdoor unit. It can be washed out with water and a sprayer, just make sure you don't bend the aluminum fins and disconnect power before washing it out.
2. Low on refrigerant. If you don't have guages you can't check the refrigerant on your own. If the fan and compressor are running , feel the bigger copper line coming from the outdoor unit going into the furnace. It should be cold. If not you can either be low on refrigerant or the compressor valves are weak.
Hope this helps. If the unit is not running outside, repost and I will try to diagnose differently.
Jun 16, 2011 | Heating & Cooling
AC is not cooling
Problem #1:Outdoor condensing fan motor has stopped running. This problem could be caused by a bad motor run capacitor. If your motor capacitor is not the problem, then more than likely you need a new motor. Is the fan blade tight, stiff or hard to turn? If the fan blade is hard to turn then you probably need a new motor. Problem #2: Air conditioner compressor will not start. When power is applied to the air conditioning outdoor unit the fan starts, but you hear a sound like the compressor is trying to start, "UGGG"..., for about 5 to 10 seconds and then all you hear is the outdoor condenser fan run. The compressor is locked and will not start. What is happening is the compressor is trying to start, but because the compressor motor is locked it tries to start for a few seconds and then because of the high amperage being drawn goes off on internal overload. The internal overload protects the compressor windings from overheating and burning up. I see this many times during the start of the air conditioning season. Some compressors just have a hard time starting after sitting all winter long. Some compressors are locked up so bad that I can not start them and must tell my customer that they need a new compressor . Many times I can get the compressor started again without having to buy a new compressor or new air conditioning system by using the device that is called, "Super-Boost." I keep two or three of these on the truck. They have saved many of my customers from having to buy new air conditioning systems.
Jun 11, 2011 | Carrier 38CKC036 Air Conditioner
The ac unit is blowing cold air on th inside but the motor fan on outside unit is not working
The outdoor fan motor can fail and also the start capacitor that helps it start can also fail...if the compressor is running then the motor should be getting power...
Change the cap. first and if that don't do the trick, then change the motor...
Heatman101
May 28, 2011 | Heating & Cooling
Unit will not start up evaperator fan runs
Hi, if your indoor unit is running and you have high voltage to the outdoor unit as the compressor runs, I would check the control wires at the indoor unit, coming from the outdoor unit, and from the thermostat terminals to see if the condenser is wired correctly. I'm not sure what relay you are jumping out to get the compressor to run, and no fan, but if you look at the contactor where your high voltage leads connect, you can energize the contactor by pushing down on the plastic part of the contacts and the outdoor unit fan and all will start. Carefully, use a insulated screwdriver, or I have pushed them down with my finger to see, but be careful! You do have high voltage there or the compressor wouldn't have come on. If all runs when you do this, the thermostat control wires to the contactor have no 24 volt control voltage to it. Check your red and yellow wire connections. If you have a meter, check across the 2- for 24 volts. If you have no low voltage, this is your problem. Go to your indoor control section. If this unit has a circuit control board, look for a plug in type fuse like you would find in your car, a 3 to 5 amp fuse. Make sure its not blown. If the led light is on, it will be good. You have lost the low 24 volt power to run the outdoor unit. Check the wiring there, Red and Yellow. Make sure they are terminated. If none of this helps you or your not at ease doing these checks, call out the contractor and tell them that the outdoor unit will not run if it is new and just installed. They should have done a start up on it. Check the contactor first by pushing it down, it will spark but don't jump as it may scare you some. If all runs, check everything I have told you and you should find the problem. If you have any questions, contact me through this site by my user name, shastalaker7. Keep me posted.
Sincerely,
Shastalaker7
Jun 16, 2010 | Fujitsu 24C1 Air Conditioner
Indoor unit freezing up
THE OUTDOOR UNIT HAS A CONTACTOR WITH THE CONTACTS WELDED TOGETHER THE CONTACTOR CONNECTS TO THE COMPRESSOR AS IT TYPICALLY PULLS A SURGE OF 20 -30 AMPS OR MORE..WITH THE INDOOR UNIT IN FAN ONLY THE COMPRESSOR SHOULD NOT BE RUNNING. THE CONTROL WIRES GOING TO THE UNIT HAVE 24 VOLTS TO THE CONTACTOR TO PULL IN THE CONTACTS TO SUPPLY 220 TO COMPRESSOR.
Mar 09, 2010 | Heating & Cooling
Inside unit runs left light blinks compressor will not start
In your out door unit you will have a dual capacitor. One side will be used to help start the outdoor fan and the other side is used to start the compressor. I have a fluke 187 volt ohm meter and can read uF. You probably have a bad capacitor. Its easy to change and by far the cheapest thing to do before calling a tech. It is out side where the electrical enters the outdoor unit. Be sure to kill all power to the outdoor unit and ground the capacitor before you remove and test. This has been the summer of capacitors here in SW Missouri. I have replaced several in the area.
Aug 15, 2009 | Mitsubishi Mr. Slim MXZ30TN Air...
Heating & Cooling Logo
182 people viewed this question