Question about NRS Wayne Deep Well 4" Pump 2-wire 1/2 Hp 115v T51s10-4
How to wire 1/2 hp115 volt with two black wires and green
  • 760 Answers
Green is always ground. This gets connected to your equipment grounding conductor which is either green or bare copper. The other two black wires would connect to your black and white wires. Make sure the pump is labeled fot 115V. You didn't list your exact model number. Since this motor is for submerged operation, it does not have the neutral conductor bonded to any part of the motor. It is not polarity sensative. You can view a manual here: http://www.waynepumps.com/images/pdf/manuals/340600-001_0806.pdf
Posted on Jul 14, 2010
I have a new heater with diferant terminals from the old one so not sure how to atach the wires
There is no need to rewire the internal of the heater!
Just bring in the electrical supply to the heater, it can be either 120 or 240 volts.
If the heater you have is like the picture associated with your post, then all then have to do is change the supplied plug from 240 to 120. It comes pre set for 240. That plug is inside the cabinet.
If any other brand, then you need to change the wires at the transformer of the heater. All heaters need to be supplied with primary voltage: 120 or 240. Then the control system is supplied with secondary voltage out of the transformer. The secondary voltage is no more than 28 volts. and these wires are normally colored as blue or yellow.
Secondary power is already wired within the heater. NO need to change where they are. You will only need to deal with the Primary wiring.
There are many varieties of transformers that transform high primary voltage to a low secondary voltage of 28 volts. and these transformers have many wires: primary & secondary.
I will try to make this easy to understand.
If you have a Gas Heater Transformer with these colors:
  • Red
  • Black
  • White
  • Green
Or...
  • Red
  • White with Red Stripe
  • Black
  • White with Black Stripe
  • Green
These are Dual Voltage Transformers, you can bring in either 120 Volts or 240 Volts
If you bring in only 120 Volts...
1st example:
The Red wire will not be used! Hot wire to the Black, and the Neutral/Common, to the white wire. Green to ground.
2nd example:
Connect the Red wire with the White with Red Stripe together and connect these to the incoming Neutral/Common wire, normally White.
Connect the Black Wire with the White with Black Stripe to your incoming Hot Wire, which is normally Black.
Green to ground
If you bring in 240 Volts...
1st example.
1 Hot wire to the Red, the Other Hot wire to the Black, and White wire is not used. Green to ground
2nd Example:
Wire nut the two Striped wires together. then one incoming Hot wire to the Black, the other incoming Hot wire to Red.
Green to ground
Or This is only a Low voltage - 120 Volts Only
  • Black
  • White
  • Green
Or either any of these combinations...
  • 2 Blacks w/Green
  • 2 Reds w/Green
  • 1 Black, 1 Red w/green
This type will only be a high voltage, 240 volts only
Picture below is what a transformer looks like and it is where your incoming supply wires go. The smaller leads with the spade connections will go to a specific location & is the 'Secondary" .
Good Luck
Mar 14, 2015 | Pool & Spa
Tip
How to wire Intermatic T103 and T104 timers
VERY IMPORTANT: Understand that in US residential wiring the WHITE wire is _NOT_ ALWAYS_ the neutral wire. Additionally, prior to 1999 the National Electric Code (NEC) did not require that these white wires be re-identified with black tape or similar means when used for purposes other than neutral. The white wire is sometimes used as a hot, especially when wiring Intermatic T103 and T104 timers.
Also understand that the WHITE neutral wire and the bare (or green) equipment grounding wire are connected together ONLY at the main electric power panel and must _never_be connected together _again_. Once those two wires leave the main electric panel, the WHITE neutral wire must _always_ remain insulated from the bare or green equipment grounding wire. This is very important for safety considerations.
If your wiring is very old and does not have a bare equipment grounding conductor, you _must_ protect the circuit with a GFCI (Ground Fault Circuit Interupter). GFCI wiring is not difficult but is beyond the scope of this post.
DETERMINE WHAT CABLE YOU HAVE:
Usually one will find one of the three following scenarios for the incoming supply cables when wiring a T103 or T104 Intermatic timer:
1...A 120 volt cable with 3 wires: black, white, and bare. The black is LINE (hot), white is neutral and bare is equipment grounding. Black to white is 120 volts. This scenario can be used with the T103, but not the T104.
2...A 240 volt cable with 3 wires: black, white, and bare. The black is LINE(hot), the WHITE is LINE (HOT), and the bare is equipment grounding. Black to white is 240 volts. This scenario is used with the T104 ONLY.
3...A 120/240 volt cable with 4 wires: Black, red, white, and bare. The black and red are (LINE) hot, white is neutral and bare is equipment grounding. Black to red is 240 volts. Black to white is 120 volts. Red to white is 120 volts. This scenario can be used with either the T103 or the T104.
The only difference between the T103 and the T104 is the timer motor voltage rating. The T103 uses a 120 volt timer motor and the T104 uses a 240 volt timer motor. The T103 timer motor is connected to terminal "A" and terminal #3 during manufacturing. The T104 timer motor is connected to terminal #1 and terminal 3# at the factory.
Also, when connecting the bare or green wires to the "GR" terminal, it is best to wirenut the wires together with a pigtail, then connect the pigtail to the "GR" (GRound) terminal, WHICH IS THE GREEN SCREW ON THE LOWER PART OF THE CASE.
WIRING THE TIMER:
The wiring diagram for the T103 is here:
http://www.progressive-growth.com/wiring/T103.pdf
___________________________________________________________________
WIRING THE T103 USING AN INCOMING 120/240 VOLT CABLE WITH 4 WIRES (scenario #3):
Incoming (LINE) wires from 240 volt circuit breaker:
Connect the black (LINE)(hot) wire to terminal #1. Connect the red (LINE) (hot) wire to terminal #3. Connect the white (neutral in this case) wire to terminal "A".
Connect the bare equipment grounding wire to the "GR" terminal, which is the green screw on the case.
Outgoing wires to 240 volt load:
Connect one (hot) wire to terminal #2 and the other (hot) wire to terminal #4. The bare or green wire goes to the "GR" terminal.
WIRING THE T103 USING AN INCOMING _120_ VOLT CABLE WITH 3 WIRES (scenario #1):
Incoming wires from 120 volt breaker or source:
Black (LINE) to terminal #3. White (neutral) to terminal "A". Bare to the "GR" terminal.
Terminals #1 and #2 are NOT used in this case.
Outgoing wires to 120 volt load(s):
Black(hot) to terminal #4. White(neutral) to terminal "A". Bare to the "GR" terminal.
The wiring diagram for the T104 is here:
http://www.progressive-growth.com/wiring/T104.pdf
WIRING THE T104 USING AN INCOMING 240 VOLT CABLE WITH 3 WIRES (scenario #2):
Incoming (LINE) wires from breaker:
Connect the black (LINE) (hot) wire to terminal #1. Connect the white (LINE) (hot in this case) to terminal #3. Connect the bare wire to the "GR" terminal.
The "A" terminal is _NOT_ used.
Outgoing wires to load:
Connect one (hot) wire to terminal #2 and the other (hot) wire to terminal #4. Connect the bare or green wire to terminal "GR".
WIRING THE T104 USING AN INCOMING 240 VOLT CABLE WITH 4 WIRES:
Same as above, except the white wire is not used. Just tape or wirenut it off.
Comment by gotgeek2, posted on Jan 08, 2010ckuzkuz, I'm a licensed master electrician in 2 states with 30 years in the trade. I've installed a lot of Intermatic timers over the years. I wrote this tip because I saw that a lot of folks were having problems wiring them.
on Mar 07, 2010 | Garden
Tip
These instructions are for USA residential wiring only.
WIRING THE TIMER:
on Dec 28, 2009 | Hardware & Accessories
How to wire pentair whisperflow 011771
if 220 wiring from factory is ok 1 black or colored toL1 then 2nd black or colored wire to L2 then green to case or ground if 120 volt see side of motor for schematic to move brown and white wires or switch to 110 volt green to case or ground
Jun 08, 2014 | Pool & Spa
How to wire a t30 1 phase 230 volt in control box, they used white black green, are the white and black both line voltage for 230 volts? its a model 2475
yes white and black are both line voltage in.each wire will have 110 to 120 volts. Attach one wire to top of starter contactor left side the other to top of starter contactor right side. Attach green wire to ground.
Jun 01, 2011 | Ingersoll Rand Type 30 Reciprocating Air...
Need to know speaker wire colour config for 1994 4runner (toyota) as well as power and earth wires
A Right Front Speaker (+) Green Gray B Left Front Speaker (+) Pink White C +12 Volt Ignition Wire Gray Red A B C D K L D +12 Volt Battery Wire Blue w/ Yellow Stripe Yellow E Right Front Speaker (-) Blue Gray w/ Black Stripe E F G H I J M N O P F Left Front Speaker (-) Purple White w/ Black Stripe G Ground Wire Black Black H Power Antenna Wire 1 Blue (join wires 1 & 2 I Power Antenna Wire 2 together to this blue wire) AS VIEWED FROM MATING END OF CONNECTOR Do Not Use J K Right Rear Speaker (+) Red Purple L Left Rear Speaker (+) Black Green M Right Rear Speaker (-) White Purple w/ Black Stripe Do Not Use N Do Not Use O P Left Rear Speaker (-) Yellow Green w/ Black Stripe
May 29, 2010 | 1994 Toyota 4Runner
Dont know if you can help but....I just bought an older model pick up(1989 toyota)it had no radio in the dash, I have a Kenwood CD player i want to install but I dont know the color codes of the wires in...
Nice radio installer link HERE
Check out the lower wiring guide.
J Do Not Use
N Do Not Use
O Do Not Use
Dec 14, 2009 | Car Audio & Video
Im lookin fer the radio wiring diagram for my 1996 geo prizm because someone cut the standard clip for the stock radio out
Under the center console/dash you should has two connectors.
LARGER CONNECTOR
C Right Front Speaker (-) Blue Gray w/ Black Stripe
D Left Front Speaker (-) Purple White w/ Black Stripe
E Ground Wire Black Black
F +12 Volt Ignition Wire Gray Red
G Power Antenna Wire 1 Blue (join wires 1 & 2
H Power Antenna Wire 2 together to this blue wire)
I Do Not Use
SMALLER CONNECTOR
J Right Rear Speaker (+) Red Purple
K Right Rear Speaker (-) White Purple w/ Black Stripe
L +12 Volt Battery Wire Blue w/ Yellow Stripe Yellow
M Left Rear Speaker (+) Black Green
N Left Rear Speaker (-) Yellow Green w/ Black Stripe
Dec 02, 2009 | 1996 Geo Prizm
12 volt system
The wires you have are white for common, 1 black for slide in, 1 black for slide out, and green for ground. Verify the direction that each of the black wires moves the slide before wiring. You will need a 3 position switch also.
Jul 03, 2009 | 2001 Chevrolet Silverado 1500
NRS Wayne Deep Well 4" Pump 2-wire 1/2 Hp 115v T51s10-4 Logo
61 people viewed this question
Top NRS Home Experts
john h
Bill Boyd
Mike
Mike