I have just fitted an fuji electricAWF18ui. the machine faulted within 10 minutes of first running. a technician was dispatched and said that the vacuum wasn't done for long enough and that moisture was in the system causing the machine to fault. he vacuumed an regassed and the machine worked for 3 days. the technician was recalled when the machine stopped working. he again re-gassed after vacuuming and the machine worked for 4 hours. the 3rd time he came he said the problem was still moisture in the system. i discconected the pipework like he instructed and used nitrogen to purge the system. i then vacuumed for 26 hours and re-filled with gas. the machine worked in cooling but when i switched to heating the mcahine outside run but the tubes got warm and then cooled. can you help

Posted by on

2 Answers

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

    Genius:

    An expert who has answered 1,000 questions.

  • Master
  • 1,665 Answers

It may be defective As your Quarranty has not expired better refer this problem to supplier.

Posted on Apr 20, 2008

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

    Genius:

    An expert who has answered 1,000 questions.

  • Master
  • 1,142 Answers

May i please know the model and the make of the product in details so that it can help me resolving the issue is a more prompt manner

Posted on Apr 20, 2008

  • Maanita Chadha
    Maanita Chadha Apr 20, 2008

    overall its a faulty equipment as it is requiring service every now and then and even after getting regassed for 2-3 times it is still giving a problem..i would suggest you to get it replaced

×

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

How do i override the stuck in fault mode on a mitsubishi electric MSH18NV


If you are a technician, then the first thing to do is to see what the actual fault that caused the lock out is. This is found on the control board in the outdoor unit. There should be LED's on the board that will give a trouble code. The fault MUST be corrected or the logic in the board will just keep locking the system out. The issue may be due to a failed component, low charge, faulty sensors, power outages, etc. It is really difficult for anyone to give a specific fix without looking at it to see what the fault is. I would definitely NOT recommend attempting a fix if you are not a trained technician due to the high voltage hazards and the specialized tools needed to work on the system. If you are a homeowner, I would recommend recycling power at the indoor and outdoor unit, then if it faults out again....call a technician. Leave the power off for 5-15 minutes to allow the system to completely de-energize, then turn it back on. Hope this helps.

Jul 23, 2016 | Mitsubishi Air Conditioners

1 Answer

Buffalo 85 ems system, not working. we have tried to restart from outside. it switches on then turns off within 2 mins


have a technician check the unit as problems include insufficient gas ( leak) faulty start/run capacitor , blown power boards , failed compressor motor

Oct 13, 2015 | Air Conditioners

1 Answer

My compressor continues to run even when I turn unit off. It runs in all settings as well. Is this a control board issue?


Hello David Forgey, thanks for your post!

Based off the information you have provided the compressor within your Frigidaire air conditioner continues to run when turned off and in different settings. It could be an issue within your control panel or a problem within the wiring harness. I would perform a reset on your air conditioner by unplugging the power cord for ten minutes. If that does not correct the issue you may want to consult with professional technician for proper repairs. Hope this helps. -Matt

Nov 03, 2014 | Frigidaire Air Conditioners

2 Answers

Panasonic a/c


F90 = PFC control
Abnormality judgement: 4 times occurrence within 10 minutes
Location to verify: Voltage at PFC

Jan 26, 2014 | Air Conditioners

1 Answer

I have a electra split system which has has developed a fault which is that when it is switched on the compressor and cooling runs for about 15 seconds and then switches off, if left it will try again...


Several things will cause this, the first I can think of is a bad capacitor for the
fan on the outdoor unit
(If the capacitor fails the fan will not run and the
compressor will go into thermal overload almost immediately and restart after
the internal thermal limit resets itself).

You should shut off system until it can be checked out.

You may also have low refrigerant, if this happens then the "Low pressure switch" will
shut the unit off as well.
Third would be possibly the contactor which controls the compressor, especially if a bug
gets between the contacts or they are burnt.
I would recommend having the unit serviced by a licensed technician .
Hope this helps.

Feb 27, 2011 | Air Conditioners

1 Answer

When running on cooling, runs for ten minutes then shuts down showing error messgae C6


C-6 Indoor unit coil sensor fault. Disconnect from PCB measure resistance. 10 kOhm at 10C and 4 kOhm at 30C. if not replace sensor. Split = text 21

Dec 14, 2010 | LG Air Conditioners

1 Answer

Set thermostat to auto switch unit to heat. Unit lights runs for a minute then shuts off. Fault light blinks4 times, msg. Open high limit.


Check air filter for blockage, clean off flame rod found in the flame pattern of the last burner that ignites, check high limit switch with multimeter to see if good (found above the burner box). Make sure room air blower turns on within 90 seconds of first flame.

Nov 28, 2010 | Goodman CLQ36AR49 Air Conditioner

1 Answer

I have a 18000btu LG mini split heat pump installed about 1 year ago in vacation home. In heat mode the unit cycles on and off when room temp is within 2-3 degrees of set point. Cycle on time varies...


Hello.I think they are on to something with shortcycling on temp sensor.I think it should be sampling the return air instead of (inside coils ?).A 2*f dead band use to be built in (factory installed) to thermostats to prevent on/off, but not sure in this case.Try a new sensor location(return air) and see if anything changes.

Oct 26, 2010 | LG LS-L1210CL Mini Split Air Conditioner

1 Answer

Air condit. runs for ten minutes , shuts off and displays E1


You should first look in the instruction/operation manual usually in the back pages for trouble shooting or code faults (errors). There should be a list of faults such as E1, E2, E33, E44 etc. and an explanation of each code. If you cannot find this info, call the manufacture ; they will tell you exactly what the E1 fault code stands for and possibly what will correct it. Ask for technical support. The fact that it runs for 10 minutes and stops; if you unplug it or turn the control to off, will it start again when you reenergize it ? This could indicate low voltage from the electric source. Are you running it with an extention cord or is the electric circuit line a very long run and robbing power before it gets to the unit? Have you checked the filter so that it is clean enough for good air flow, otherwise the unit will detect the low air movement from a dirty filter and shut itself down.

Aug 10, 2010 | Sharp AF-S100FX Comfort Touch Air...

1 Answer

DeLonghi Planus quick connect split heat pump.


I was told by a delonghi technician that it does this to defrost the unit.
Hope this helps.

Apr 16, 2009 | DeLonghi Air Conditioners

Not finding what you are looking for?
Air Conditioners Logo

Related Topics:

44 people viewed this question

Ask a Question

Usually answered in minutes!

Top Air Conditioners Experts

Dan Webster
Dan Webster

Level 3 Expert

8147 Answers

Bill Long

Level 3 Expert

577 Answers

Tim Whalen

Level 3 Expert

3056 Answers

Are you an Air Conditioner Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...