Question about Raypak Free Hydraulic Lift Gate Delivery - No L...
Pilot ignights, keeps sparking then goes to lockout
Raypack pool heater. mod no cr 265 en. btu input 264-100. we have a good strong pilot flame, but the flame is not being sensed.
I have the exact same model with the exact same problem. Did you ever figure out what the problem was? I just picked up a new gas valve, but maybe i should check the flame sensor first. In my systems case the electronic ignition fires, which lights the pilot, but it keeps firing even though the pilot light is lit. So I think it could be the flame sensor, how do I remedy that or check it out. I would like to check this out first before dropping in the gas valve, cause they arent cheap and I can still return it before its installed.
Posted on Apr 12, 2012
    Scholar:
  • 78 Answers
Model A or AL? A is atmospheric..AL Lo Nox... Anyway...Does the pilot remain lit? Go out on call for heat? 1st, check continuity through all components (pressure switch, roll out switch, thermostat, etc). I would think the pilot assembly first. (possibly flame sensor). if all components check out.Jast would be the gas valve....Here is a link to the manual with a handy flow chart..... Raypak here
Posted on Jul 12, 2010
Rp2100 raypack pool heater pilot will not stay lit
Several issues can cause a pilot to go out. The flame must be stable and high enough to prevent a wind gust from blowing it out. There is an adjustment screw on the gas valve that can adjust it up or down. If there is dirt in the orifice it may be a weak flame. In addition, if the thermocouple is worn out it may not provide enough current to keep the pilot pulled in. In addition things can go wrong in the valve that prevents the pilot solenoid from holding in.
I would first look at the flame and see if it seems weak and easy to blow out. Turn it up a little and see if it is harder to blow out. If you are not successful and it still goes out then it is probably something in the thermocouple/pilot valve that is defective.
I hope this helps.
Sep 04, 2011 | Raypak Rp2100 Pool & Spa Heater Lonox 407k...
Installed new ignighter and getting 3 red light flashes for lockout. Ehat do i do now
3 main possibilities.
1- ignitor
2- bad ignition control module
3- bad flame sensor (flame rectifier)
its probably the flame sensor.
Mar 14, 2011 | Pentair MASTER TEMP HEATER 400 000 BTU NG...
Codes for model 335B Raypack Gas Heater
Codes should be found inside of the cabinet in the uper left corner.
If they are not there, here are the basics
EOL = Testing mode
BDI = BOARD FAILURE
EEP = MEMORY CHIP FAILURE
PRS = PRESSURE SWITCH FAILURE
HL1+HL2 = HIGH LIMIT EXCEEDS 135F
SPR = AUXILLIARY INPUT FAILURE
ROL = ROLL OUT SENSOR TRIPPED
SNS = TEMPERATURE BELOW 36 OR ABOVE 110F
FFL = FALSE FLAME SIGNAL
GCO + GVC = POWER TO GAS PV OR MV WHEN NOT SUPPOSED TO BE
FAN = AIR SWITCH OR FAN FAILURE
TAB = TAB FOR LO NOX NOT BROLEN OFF OR AIR PRESSURE SWITCH FAILURE
ILO = PROPANE GAS LOCKOUT AFTER 90 IGNITION TRIAL
IGN= LOSS OF FLAME OR FLAME SIGNAL
Sep 12, 2010 | Raypak Rp2100 Pool & Spa Heater Lonox 407k...
Pool heater
This is an old, but good heater. Power is either stopping thru the safety loop, high limits or pressure switch, or the pilot generator is tiring out and not sending enough power to keep the gas valve open.
May 06, 2010 | Pool & Spa
Raypack pool/spa heater works intermittently
You can try pulling your pilot assembly out and clean it. Sometimes it will get sooted up and cause the sensor to short so the heater get's a falce reading and shuts the heater down. Then sometimes the heater will start and sometimes it won't. If this dosen't help check the ignition wire for any cracks or anyplace it may be shorting. Good luck.
Feb 17, 2010 | Raypak Versa 130,000 Btu Above Ground...
Charmglow ventless gas fireplace burners won't ignite
is pilot flame on the thermopile good, pilot flame should cover the thermocouple and thermopile if unit has both
Jan 07, 2010 | Blue Flame Charmglow 30K BTU Propane Vent...
Pool pilot keeps tripping,what might be the problem ?
One of the most common problems will be the flame sensor. If it doesn't sense the flame, it shuts down the burner. Good luck...Lee
Nov 09, 2009 | Teledyne Laars Laars Lite 2 Pool Heater...
Trys to ignight flame shoots out of top and then error code IF
Try cleaning the heat excharger, make sure the combustion air isn't blocked. Flane rollout is caused by a lack of free air.
Sep 06, 2009 | Hayward H Series Pool & Spa Heater 400k...
Hayward pool heater pilot won't stay on
a short circuit in the heater wire will cause an immediate loss of all flame, pilot and main; check the wiring diagram and make sure your pilot wires go to the PP and PP/TH terminals; make sure the terminals are clean and the connection is good; you are dealing with .320 volts DC, any bad connection drops the voltage below the required minimum.
Jun 27, 2009 | Hayward H Series Millivolt 250,000 Btu...
Pool heater will not flame
sounds like a flame rectification probelm...look in the manual for solutions
May 30, 2009 | Hayward H Series Millivolt 250,000 Btu...
Raypak Free Hydraulic Lift Gate Delivery - No L... Logo
505 people viewed this question
Top Raypak Pool & Spa Experts
Bill Jordan
paulcarew
Are you a Raypak Pool and Spa Expert? Answer questions, earn points and help others