Question about Carrier 38CKC036 Air Conditioner
Installed new compressor on Carrier 3 ton a/c unit. Compressor comes in, but only runs for about 2-3 minutes and then trips out. Have installed new compitcor. Have 24 volts coming in. Will not take freon charge. Liquid line coming back to compressor behind dryer is extremely hot. Do you think the dryer may be stopped up causing unit not to take charge?
  • 532 Answers
The trpping off may be as a result of dirty condenser. please clean the condenser to stop this problem.
The dryer may be stop up causing unit to take a charge.
Thanks
Posted on Jul 14, 2010
  • jackiemar830 Jul 15, 2010
    Coils have been cleaned and a new dryer put in. Any new ideas?
    Genius:
  • 1,478 Answers
The liquid line coming back to compressor behind dryer should not be hot in any way, it should be cool because of the freon going through it, the problem is the dryer is stuck not allowing the unit to take charge.
Take care.
Posted on Jul 11, 2010
  • jackiemar830 Jul 11, 2010
    Will try this tomorrow and get back with you. Thank you very much for responding so quickly.
  • jackiemar830 Jul 14, 2010
    Tried your suggestion, didn't work. Since then have installed new set of coils, new thermostat system still doing same thing. Any new ideas on this problem. Sounds to me some type of restriction, but don't know what.
Brand New 2 weeks old 4 ton Trane compressor leaks a lot of water onto pad
If the unit is running in cold weather than there is ice building up on the coils located outside. This is normal in that the unit is running in heat pump mode heating inside and cooling outside, After the unit detects the ice build up it briefly reverses the cycle heating the outside coils melting(defrosting) the ice which you observe as water on the pad.
The video gives you an example of the defrost cycle!
2012 Trane XL15i Heat Pump Defrost Cycle Steam Show
Dec 21, 2015 | Heating & Cooling
Had 16 xi Trane heat pump installed 3 years ago. It ran well for the first couple of years. It began to stop heating and would blow cold air only. Have tried both aux heat and reg. heat to run and neither...
That's a complicated system that needs a qualified technician to service it. Lots of people can install them and they run fine, for a few years. Your indoor unit, operating on 2 heat elements, will feel like its blowing cold air even though its heating, just not so well. And not like you are accustomed to. Each element (5kw)=22.7amps, on average. So 3 elements operating should trip a breaker. Its probably been operating on 2 heat element plus the heat pump. And now you have trouble with the heat pump. If you can't TRUST the guys working on your equipment, try someone else. A second opinion. Normally a 3 or 4 ton unit will have 15kw heat installed, heatpump or not. 5 ton, 20kw. If yours is a 3-4ton, cooling, the 100amp(or normally two 60 amp) breaker should have been installed upon equipment change out. If yours is blowing cold all the time, something is wrong with your heatpump. The electric heat inside operates only when the heatpump can't keep up(real cold outside), the heatpump is in defrost(then it's actually in cooling mode), or if you have the tstat in aux/em. heat. Try a local trane dealer? Of a technician with 15-20 yrs under their belt. A trane dealer should have trane tech support also. BIG HELP!!!
Mar 01, 2017 | Haier Energy Star ESA3183 Air Conditioner
What is the HP rating if a 3 ton air conditioner?
Hi, this depends on the compressor that is installed in this unit. It may be a Copeland scroll, a Tecumseh, its hard to say. Most compressors are around 2 hp for a 3 ton unit. On the data plate it will tell you the h.p. of the blower and condenser fan motors such as 1/4 h.p., or 1/3. If you can get the name and model numbers from the top of your compressor, you can call a a/c, Refrigeration parts house, wholesale and they will have it in there manuals. The B.T.U. rating for your compressor is 36,000. There are 12,000 BTU's per ton of cooling, this is something that almost no one knows, but now you do. If it were a smaller unit such as a 2 and 1/2 ton, it would be 30,000 B.T.U.'s. You can look at the model number of a unit and you will see numbers like this, 024, 2-ton, 030, 21/2 ton, and 036 a 3 ton unit and so on. Your compressor alone will be in the range of a 2 horse unit, which ever the brand of compressor they installed in it. Please don't forget to rate me on this as I know you will be kind. I will be here if you ever need help on repairs or trouble-shooting your unit in the future, just use my user name below.
Sincerely,
Shastalaker7
A/C, Heating, & Refrigeration Contractor
Sep 04, 2010 | Heating & Cooling
We installed a new TCJD36 (3 TON) unit with new A coil. The unit works fine from morning until 4:30 PM. from 4:30 PM to 9:00 PM the compressor does not come on. Inside fan goes on and outside unit fan...
This really sounds like the unit is over heating the compressor to the point of triping the internal high limit switch and just taking that long to cool off before it resets. If it continues to do this go outside and run your water hose over the compressor for at least 30 minutes to cool the compressor down and see if it starts for you then. If so then your unit could be over charged and creating very high head pressures!
Aug 11, 2010 | Goodman CLQ36AR49 Air Conditioner
Carrier Desert Master AC trips the fuse
1- check the fuse must support the current of the unit not less than (rla of the unit)
2- check freon pressure may below or toohigh causes compressor winding over heating
3- check fan motor winding
Sep 20, 2009 | Dometic Rooftop RV Air Conditioner
Compressor kicks out and it's new
First of all, clean your outside coils so that you are assured of good cooling air. The compressors have an overtemp device that is usually internal to protect them against heat. If you have an air compressor use it to blow out the coils good. If the compressor will start, the capacitor is good so it sounds like a cooling problem with the compressor
Jun 25, 2009 | Ruud UAMB Air Conditioner
New Goodman condenser unit run almost contiously using too much e
I'm not sure of the kilowatts. The 10 min on and 5 off is telling me there is to much heat by the thermostat or you house needs more insulation. The new compressor is designed for more efficient run time. The other thing is the unit to big for your house? It should run 10 -15 min when low humidity is in the house. Otherwise longer if its pretty warm inside.
Jun 11, 2009 | Goodman Heating & Cooling
Compressor not doing much
I am assuming that you are talking about a central ac unit. On a central air unit the outside fan must be running whenever the compressor is. If it's not the compressor will shut off from overheating withing minutes. First you need to shut off the unit for several hours and let it cool completely down. Then turn it on briefly to see if the compressor starts and see if the fan tries to start.( I am assuming the compressor starts and runs.) If the fan won't start try testing the capacitors. There are usually two one for the fan one for the compressor. Sometimes there will be one combo one. Mark the wires and remove the capacitor. Get it tested and if bad replace it. This will probably do the job. If not test for current at the fan motor. Also test to see if it turns freely. The motor may need to be replaced. This will run about $50. The capacitor should always be replaced when the motor is changed anyway.
Jul 09, 2008 | Carrier 38BRC060 Air Conditioner
I recently had a new outdoor unit installed on my central heat and air conditioning sytem. I have had the installer out 3 times and the system still does not operate correctly. Sometimes when it cycles...
It sounds like the compressor needs starting components installed on it. All a/c units have a run capacitor for the compressor and another one for the condenser fan motor. These motors use these capacitors all the time when the motor is running. However, in some cases, this capacitor isn't enough to get the compressor spinning initially. Starting components consist of two parts, a start capacitor and a potential relay. The starting components are wired in in series with the compressor run capacitor. When the compressor turns on, the start capacitor gives the compressor an extra "kick in the pants" to get it going, then as soon as the compressor is spinning, the potential relay disconnects the start capacitor from the circuit for the duration of the run time and resets when the compressor turns off. Most likely, your indoor unit has a thermal expansion valve (commonly known in the trade as a TXV). This valve maintains a somewhat substantial differential between the high side and low side of the compressor after the system turns off which can be difficult for the compressor to overcome without help. Right now the compressor is trying to come on, can't overcome the pressure, and is tripping it's internal overload to protect itself. Eventually, as the overload repeatedly trips and resets over and over, the compressor will finally get around to a position where it will start once in a while. I am not a gambling man and I would bet you money that this will solve your problem. If you would be so kind as to rate my solution "Fix-Ya".
Jul 03, 2008 | Heating & Cooling
Carrier 38CKC036 Air Conditioner Logo
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others