The starter capacitor went out on my outside ac unit I had it replaced everything worked fine for about 2 weeks and the the red wire burnt off at the capacitor got that fixed and all was fine again 2 weeks after that the same thing happen but this time it was the yellow wire what could be the problem? I am leaning toward the compessor going bad any help would be appreciater it is a goodman 5 ton unit and it is only 5 years old
    President:
  • 1,515 Answers
Hi, and yes if this capacitor is getting hot enough to burn off wires, you are drawing to many amps at your compressor causing this. Did the old capacitor you replaced leak any oil, or was it swollen and deformed? I have seen a compressor last less then 6 months. If you had a amp probe the clamp around, you could check the running load amps, (R. L. A. ) at each leg of the compressor to see what each one was pulling. Like the R terminal, 11.8, C, 9.7, and the S or start, 8.9 amps and compare it to the data plate on the outdoor unit which tells you what it will be, like 21.7R.L.A., just a guess on yours. If it was much higher, you would know you have a problem. Whens the last time the outdoor coil was cleaned?? It should be cleaned every year as the head pressure will build in the system putting a load on the compressor and will cause these kinds of problems. Before I would condem the compressor, kill the power and take your water hose to the coil and give it a good washing. If dirty, it could bring the internal head pressures down by 50 p.s.i.! Do this to see if it takes care of the problem.If you had a service tech out to replace the cap, he should have put his manifold gauges on it and cleaned this coil for you. Be careful not to bend the aluminum fins down with to much pressure. If this is a dual run cap, it would be for the fan and compressor. It will have 3- sets of 3 to 4 spades coming out the top, 3 in a row marked Fan, C for common, and Herm for compressor. With a dirty coil, it will also cause this fan to run to hot and take out the capacitor. Do this for me and I believe this will solve the problem if the fan and compressor seem to be running quite and cooling good. Keep me posted on this. My gut tells me its a dirty coil causing this problem. Please be kind when rating me, that would be nice of you. I will be here if you need me.
Sincerely, and have a great 4th,
Shastalaker7
A/C & Heating Contractor
Posted on Jul 04, 2010
    Scholar:
  • 80 Answers
My opinion is simple! The wires went bad on the first capacitor and were not replaced. Now after a fresh capacitor was installed the wires just could not hold up any longer! Thats is why the red wire did not burn off the second time and it was a different wire....the yellow! The next wire that is going to go bad is the Brown wire if it was a three wire capacitor. Hope this helps explain the problem! Always replace the wires after a cap is blown!
Posted on Aug 29, 2010
  • 456 Answers
It sounds like the wires are not connected tightly, if you put the capacitor on yourself make sure you take a pair of pliers and crimp the male connector more snug. A burnt wire does not mean bad compressor,it
could mean poor wiring connections
  • 1 more comment
  • Frank Bryant Wetzel Jul 04, 2010
    80% of all AC problems are electrical, the unit not being on the 1st
    time is no reason to put a set of guages on and cause more problems. I have only seen a few capacitors blow up and others that looked perfectly fine and not work.
    After the capacitor was installed the 1st time and after the tech got
    the unit operating, he could probably tell by listening to the compressor, feeling the suction line, the discharge air out of the
    condensor if the unit was performing. If a condensor is that dirty
    he should have seen it and washed it.
    You can check the compressor out, but I doubt you will replace the compressor, you will probably replace the entire unit. I would not expect a homeowner to be able to do what you described as
    evident they called a service tech. Asking them to do what you
    just described could get them killed.
    Run it til it drops and dont let a contractor force you to buy one
    when it is not needed,just start getting prepared if you feel you
    are having problems with the compressor
  • Robert Horton
    Robert Horton Sep 10, 2010
    Looking back on what you said about not putting gauges on a unit causing more problems is not at all true. First thing I do, is look, listen, and feel. I can 99% of the time tell you what is wrong with your unit by just hearing out the complaint. The coil should be washed while you are on site anyway. You can't tell if the unit has the proper charge just by feeling the suction line or if its sweating?? If you are a real service tech, and not a wanna be, you should check the system out completely, amp. check on the compressor, condenser motor, evap. motor. Check the super heat, only takes a few minutes. Wash the outdoor coil. Look at all of the electrical connections. If I were to get a call back when working for the last company I worked at, and it turned out to be a burned connection on the compressor terminal causing the compressor to over amp, my service manager would have my a*$#%^@# in a sling!! Do it right, if you know what you are doing. Prevent call backs. You say I could get the customer killed by checking the amps? Yes, if he didn't fully understand, and crimping down connections on a run capacitor can kill a man if the capacitor hasn't been discharged either!! So, remember this if you can.
    Shastalaker7
  • Frank Bryant Wetzel Sep 10, 2010
    Apparently you do not put your gauges on first, the 1st thing you do is look,listen and feel. 99%
    of the time the complaint is usually its not cooling so now thats not hard to figure out. You also
    said you can tell if the unit has the proper charge by just feeling the suction line, so far another
    reason you have not put gauges on yet.
    If you clean the condensor 1st, your amp draw would be less on the compressor and condensor fan motor. So why even take the measurements unless you are predicting the
    unit will fail pretty soon.
    Are you going to tell the average homeowner your compressor has high amp draw, they will
    not even know what you are talking about. Besides a real service tech would also check
    the filter, a level thermostat if needed and additional heat sources that could be a problem.
    So and try and remember that if you can.
SPLIT AC CONDENSER TRIPS AFTER 1 OR 2 MINS, ONLY DURING THE DAY TIME
The condensor is not cooling fast enough. Try cleaning the condensor coil. Also check that the fan goes on. At night the outside temperature is cooler and does not need much work to cool down the condensor.
Jul 15, 2012 | Haier Heating & Cooling
My condensor fan and compressor on my Carrier AC (Model# 38ckc036350) stopped working, so I replaced my capacitor and they both work fine now. The problem is my house won't cool down. There is c
Often after a repair has been made, the air conditioner will take hours to readjust back to normal. When the system has been off for to long, not only does the heat in the house rise, but so does the humidity, which has to be pulled out of the air first before it really starts dropping in temp. You could have a low charge on refrigerant, dirty filters, etc. More than once I have ran into things that were just coincidence after a repair that showed up. Since you just replaced the capacitor, I would make sure the fan motor is turning in the right direction and there is nice air flow coming out of the condenser, some times if one wire is wrong, it can cause it to spin backwards, which will work, but just barely. The air needs to be pulled through the coils, not pushed. Hope this helps!
Jul 06, 2012 | Carrier 38CKC036 Air Conditioner
Hi, I have an older mobil home with a Colman AC
Your unit uses both the capacitor and a contactor (relay) to start your compressor and motor. With the indications you are giving it would either be the capacitor or the contactor - and since you have already changed the cap - then replace the contractor!
NOTE: We always recommend that you change the capacitor and relay at the same time, because they seem to fail at about the same time.
Jul 28, 2011 | Coleman Heating & Cooling
Outside unit will not come on
Check the starter capacitor, and di you remember to add oil?
Aug 27, 2009 | Goodman CLQ36AR49 Air Conditioner
Ac fan on, blowing air, but not cold
Check outside unit if unit and compressor are running feel the large line to see if it is cold. If compressor is running and line is not cold possible charge problems. You may have a capacitor problem outside. they go out quite often. You can change this yourself, Open up outside unit and the cap is the silver bullet with terminals out the top. Bad cap can cause compressor to not operate and also the fan. You need to clean the coil inside or at leat check the coil to see if it is clean. You can clean theis with a toilet brush do not go against the coil bit brush with the fins. You may need to call a service tech but try these options first. russ
Aug 15, 2009 | Heating & Cooling
I have an older Goodman CKB 18-1
FOR QUESTION 1: They do run independantly. What will happen when your compressor is running but your outdoor fan does not, the pressures in the system will go really high and compressor will overload. That outdoor fan is used to disipate all the heat that is transferred from the inside to the outdoor unit.
FOR QUESTION 2: If you hear humming it can be 2 things. FIrst one is that that capacitor went bad. Dependiing if its a dual run capacitor(which helps both compressor and fan motor) or they both have individual capacitors. The second would be a bad fan motor. OPen your service panel outside to the AC. Find your capacitor for you fan motor. if there are 2 , locate the one that goes to your fan motor. Check it out(if its blown physically youll will notice it like really bubbled, like swollen) then change itout. Or you will have a dual run capacitor that runs both compressor and fan motor. It will have the terminals marked (Fan, Common, Herm) Bsically check your capacitor mfd(micro fared rating, it will say on the capacitor what its rated) Get a multi meter and put in the "MFD' selection. Before you check any capacitor you have to discharge the the voltage charge it has. Use an insulated handle screwdriver and just place the metel part across the capacitor leads. Basicall short them out. Then proceed with checks...hope this helps( remember to always pull the disconnect out from the box outside to cut power)
Jul 30, 2009 | Goodman CLJ30AR32 Air Conditioner
A/C not working, outside fan not turning without assistance
is fan spinning fast enough it has to have alot of velocity to cool condensor coils if you haft to push fan to get going its probably shot and get new motor the ac is a sealed system and hardly ever will leak freon!!!Best of Luck to You!!! :)
Jul 02, 2009 | Bryant 462AJC021BA Air Conditioner
Compressor on my RV coleman ac unit bogging down
Take a look at your start capacitor. This the capacitor that kicks the compressor over when it tries to start. If the capacitor is bad, it cannot kick the compressor back over after the first cycle because the head pressure has not evened out yet. It is located in the upper unit on the side panel in a small box. Be careful, highly charged capacitors can zap you if you are not careful. Disconnect power and touch across the terminals with a meter or a screwdriver to discharge the capacitor.
Hope this helps,
Jeff
Jun 29, 2009 | Coleman Mach 15 Air Conditioner
Replacement of air conditioner's compacitor
I am assuming this is a split system with the condensor outside and the air handler inside. What is the model of your unit? Is the capacitor a dual run capacitor? Is the compressor running? If the compressor is running and your condensor fan is not you need to immediately shut power off to the compressor or you will probably ruin your compressor. If the power went off due to a storm and you don't have power to the condensor fan did you check to see if the circuit breaker to the condensor was tripped. I would check that first. Even if the circuit breaker doesn't look like it tripped go ahead and flip it off and back on again. Even you suspect it is the capacitor you need to determine if it is a dual run (controls the compressor and the fan) or does it just run the fan? If it is a dual run capacitor you will have to get the numbers off the capacitor and try and find a match at the local hvac supplier. If you have a Grainger's in your city they probably will have a match. When working on your unit don't forget you are working with high voltage that can KILL you, If you don't know what you are doing call in a professional. If you decide to tackle it yourself make sure you turn off the power to both the inside unit and the condenser. I always pull the disconnects inside and outside, flip the circuit breakers and turn off the thermostat just to be safe. Then I double check by using my digital multi-meter to ensure the power is totally off. The capacitor stores power so you will have to discharge it by using an INSULATED screw driver and touching the blade across the terminals. Discharge the capacitor AFTER THE POWER IS SHUTOFF. Before you pull the wires off the capacitor terminals I suggest you make a drawing of where the wires are connected. You should have markings with a "C", "F" and "Herm". Even better, I like to take several digital pictures from different angles of the connections. After you remove the capacitor, I would suggest you take it with you to your hvac parts supplier so they can match it. Once you get the right replacement capacitor it is just a matter of connecting the wires back to the original configuration. Then restore the power by flipping the breakers, plugging the disconnects back in and turning the thermostat back on. Most units will not start up right away. They have a 5 minute delay built in to protect the compressor. Good luck and post back and let us know how it goes.
Jun 25, 2009 | Carrier Heating & Cooling
Goodman CKL60-1 Condenser Fan Runs OK, then stops
check connections tightness or if you just change the connector will solve the problem that is if the motor has not burn out yet
May 28, 2009 | Goodman CKL60AR60 Air Conditioner
Goodman CLQ36AR49 Air Conditioner Logo
859 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others