I have a Coleman Central Air Conditioner/Heat Pump. On the cooling mode the coils inside the unit in the basement continue to freeze up causing no air flow. I relpaced the filter thinking it might have been restricting the flow causing the freezeup but it still freezes up. What are the suggestions on what could be wrong with my unit
Anonymous
Level 2:
Novelist:
  • Expert 246 Answers
  • Posted on Jun 20, 2010
Anonymous
Expert
Level 2:
Novelist:
Answers
246
Questions
0
Helped
78767
Points
462
The most common reason for freezing up is 'air flow,' and since you've already changed your filter - have you checked out the coil (the one that cold air comes from) to see if it's clean? If the filter you changed was really 'bad dirty' then it's a good bet the coil could be dirty also - thus restricting the air flow.
If you're satisfied that the coil is clean - about the only other thing it could be - is 'low on refrigerant,' which of course will take a Service Tech to find the leak, repair it and then re-charge the unit with refrigerant.
One other thing you might think about - are you running the blower motor on 'low speed?' If you are then put it on 'high' and see what happens.
Again, the most likely cause of your problem is air flow or 'low load,' - so I would really look hard for an air flow problem of some sort.
hope this has helped a little
Testimonial: "I had replaced the filter on this unit with one recomended by the local hardware store and the model of my unit was on the box but the new filter was to restictive of air flow - I called the service tech who installed the unit and he immediately noted the filter that I had purchased and replaced it with a filter that he normally installs and since he put the new filter in, it works perfectly. The filter I used looked like a paper type filter and the one he used had more of a fiberglass appearance. Needless to say - his filter was the answer."
tip
Why your unit is freezing up.
To understand why your AC or heat pump is freezing up, it helps to know how your system works.
There are 7 major parts to an AC system, 9 with a heat pump.
1 - Condenser/heat pump (The outdoor unit)
2 - Air Handler (the indoor unit unless the system is a package unit, then all is outside in one system. The air handler is usually found under the home, in an attic, or in a closet.)
In the condenser are the following major parts.
3 - Compressor
4 - Condenser coil
5 - Condenser fan
6 - (HPs only) reversing valve
In the air handler are the following major parts.
7 - Blower motor
8 - Evaporator coil
9 - (HPs only) electric heat strips
Some systems known as "dual fuel systems" use another heat source in place of the heat strips, usually a gas furnace. I will address gas furnaces in another post.
When an air conditioner is operating properly several things are taking place.
1 - The compressor is compressing or "pumping" refrigerant through the system.
2 - through changes in pressure, the refrigerant makes the evaporator coil get very cold, and the condenser coil gets very hot.
3 - The blower motor/fan circulates air across the evaporator coils, as the room temperature air (Also known as "indoor ambient") goes through the cold coil, it exits, cooled approximately 15 to 20 degrees cooler than when it entered. (In a ducted system, the blower is also the fan that circulates the air throughout the home.)
4 - The condenser fan circulates air across the condenser coils. As the outdoor air goes through the condenser coil, it removes heat from the coils that are very hot. This in turn removes heat from the refrigerant so it can run its cycle again, and through pressure changes, cool the evap coil.
5 - With a heat pump, the reversing valve reverses the flow of refrigerant in the condenser and evaporator coils.
In AC mode, the evaporator coils get cold, and the condenser coils get hot. But in heat mode, the evaporator gets very hot, and the condenser very cold.
Now, whichever coil is getting cold will freeze up if there is inadequate air flow across the coil, as the refrigerant in it is far below freezing, and there is not enough airflow to keep the humidity in the air from freezing on the coil.
Things that can cause poor airflow are,
1 - Dirty/clogged coils
2 - dirty/clogged filter (will only effect evaporator coil)
3 - Closed/blocked vents (will only effect evaporator coil)
4 - Malfunctioning or dirty fan
Low refrigerant will also cause a coil to freeze up, reduce efficiency and cause the system to run for long periods of time. Not to mention, shortening the life of the unit.
With a heat pump, in heat mode only, the condenser (outdoor) coil will routinely begin to freeze up in cold temperatures. This is due to the fact that the refrigerant is below freezing, and the cold outdoor ambient temp is not warm enough to keep the condensation in the air from freezing on the coil.
Note, a properly working AC should never freeze up.
A heat pump is equipped with defrost controls to prevent ice buildup.
Some are controlled by timers, some by temp.
When a HP is going into defrost mode, the condenser fan shuts down, the reversing valve reverses the flow of refrigerant and the once cold condenser coil now gets very hot, defrosting the coil. (Many people have said this process sounds like the unit is coming apart, or about to explode and are frightened by the "smoke" which is really just steam from melting ice that comes off the unit.)
During defrost mode, the secondary or "auxiliary" heat comes on to ensure that you are still getting warm air from the vents. (Again, this can be electric heat strips or a dual fuel system)
If you are experiencing cold air from the vents during defrost, that means your auxiliary heat is malfunctioning.
The auxiliary heat is used for three purposes.
1 - during defrost mode to maintain warm airflow (automatic)
2 - when the HP cannot maintain the set temp due to extreme outdoor temps. It comes on when the indoor temp drops several degrees below the set temp on the thermostat (automatic)
3 - For emergency heat source when the HP is not working. (Manual)
To recap....
Iced up coils?
Poor airflow
low refrigerant
Malfunctioning fan
failing defrost system
There are two things that can be done in a pinch to help de-ice frozen coils. This may get you by until the repairman can get there, or you can fix the system if you are a do-it-yourselfer.
HPs frozen outdoor coil in heat mode, not going into defrost?
Cover most of the vents, and turn the system onto cooling mode until the outdoor coil is thawed. then uncover vents and return to heat, or emergency heat. (this usually takes 15 min or less)
Frozen coils in AC mode with a heat pump?
Turn the system to heat with the thermostat on just high enough to get the system to come on. (again, usually takes 15 min or less to thaw.)
AC only, with frozen evap coils? (this can sometimes be seen frozen all the way outside to the compressor on the copper lines.)
Turn the system off, and the fan switch from "auto" to on".
This will usually defrost the coils within 1 to 2 hours.
(If your system has the furnace in line before the evap coil, turn the system to heat, and the furnace will defrost the coil within minutes.)
Ice on coils of heat pump not cooling
Which coil?, indoor or out? Indoor coils freeze due to clogged filters, low freon, blower motor not working. Outdoor coil freezing could mean, in rare cases in cooling mode, reversing valve not shifting.
Should the LG LS-K-1830CL outdoor unit ice over on the coils when operating in the heat pump mode? Would this cause the unit to not properly heat the room?
Running the heat pump in low outside ambient temps. will definitely cause the coil to ice up. An ouside temperature senor or a wind baffle should be installed in climates that get below freezing. This would definitely cause the heat pump to operate at lowered efficency and maybe not at all. It should go into defrost mode if the sensor is working correctly when the coil ices up.
1helpful
2answers
18 year old Janitrol Heat Pump freezing up.
i would get someone to check your refrigerant levels have you ever had the evaporator coil flushed and cleaned? proper refrigerant levels and proper airflow across coils are extremley important not to scare you but 18 yrs is a long time on a heat pump 9-12 years is the point where they really loose there efficiency going for a newer one would probably cut your operating cost in half if not more depending where you live there are a lot of people not familiar with heat pumps so i suggest finding a company that specializes in them to service your unit
Im at an rv park, approximately 90 degees in the sun, air was cool for about 2 hours, fan continued to run but no cold air. When I change the thermostat I can hear it click but nothing changes.
Take air filter off , look up inside & see if coils freezing/frosting up when starts to blow warm air.
Is this a new unit, and has it always done that or just recently?
Vibration when heat only is on inside and out
Is it noisy always when running in heat or only for intermittant periods? Depending on where you live every 45-90 minutes of run time the heat pump goes into a cycle called defrost. The fan on the outdoor unit will shut off. the compressor will continue to run but in actually cool mode. this heats the outdoor coil and allows any frost or ice that is built up on the outdoor coil to melt. The compressor can get pretty loud in this mode and you may actually see steam coming off of the unit. This is normal. However if it is noisy all of time in heat check/clean your coils. If this doesn't remedy it have your refrigerant charge checked by a NATE certified Service Technician. Good luck.
My central air unit keeps freezing up on the inside
1) locate the A-Coil (A-frame) inside the furnace. It is usually located in the furnace supply plenum located on the "down" side of the furnace plenum. If it is very dirty, there will be poor air flow generally in the house. This can cause the A/C to "freeze up" as the refrigerant is not getting enough heat to convert the refrigerant to a gaseous state.
2) The unit may be low on freon (or whatever refrigerant you are using). Contact a serviceman to check the unit.
Amana heat/air conditioning pump
You are going to have to increase the amount of heat absorbed by the evaporator coil on the indoor section of your system. First change the filter. Second turn the power off to the outdoor section and leave the indoor fan running until all the ice on the evaporator coil has thawed this could take a few hours. Third you need to verify that you are getting adequate airflow across the indoor evaporator coil and the outdoor condenser coil both fans should be spinning at full speed and airflow should be unobstructed by dirty coil fins or debris Hopefully after you've done this you will have cold air blowing inside and the larger of the two lines entering the unit outside will be cool to the touch but not frozen or even frosted regardless of run time and the small one should be the slightly warm but not hot. If the larger line continues to freeze then it could indicate a number of problems but essentially your condensers cooling capacity is outrunning your evaporator coils ability to absorb heat from air stream circulating in your home.Hope it works out for you GL!
Central unit freezeup when on
If you are running the unit in the A/C mode with the fan in the automatic position it could be the cause of the freezing of the coil. Try operating it with the fan in the on position and see if the problem goes away. When in the automatic operation the fan shuts off when the cooling unit shuts off and air circulation stops. Hence no defrosting of the cooling cycle in the off cycle. In the evenings when the outside temperature drops after sundown the pressures in the system drop in proportion dropping the temperature of the cooling coil sometimes causing ice formation on the cooling coil.