Question about Goodman GMS90703BXA Heater
I have Goodman 2 speed NG furnace that will not heat or circulate air (manual mode). The LED trouble lite blinks 3 times indicating a pressure switch or clogged line problem however, the inducer blower is NOT operating. I checked for power to the motor and got no power (115V). All the air lines are clear and the pressure switches seem to operate normally using my Ohm meter (normally open, then close when I blow air in the line). Does this sound like a circuit board problem? Thanks, Steve
  • Goodman Master
  • 2,523 Answers
Try jumping out the pressure switch see if it works then
Posted on Jun 08, 2010
Goodman Gas Heating A/GPG13 Not Heating - Pressure Switch Stuck Open
Clear the little hole where that hose go to the inducer case
Feb 10, 2013 | Goodman Manufacturing Goodman...
Goodman furnace has 3 blinking lights, indicating pressure switch stuck open. Any help?
The flame sensor needs to be cleaned. This video might help you understand how to clean the flame sensor.
Oct 05, 2012 | Goodman Manufacturing Goodman GMH950704CX...
I installed a new goodman unit this past spring. It seems to work ok to good in the day time but the tempature is warmer so we do not need as much heat. At night I know the thermostat is coming on. I...
Heating Mode (Goodman Service Manual)
· The furnace control checks for an open main limit (this
limit is normally closed). If the limit is open, the furnace
will remain inoperable until the limit is closed. During
an open limit the circulating air blower will be
energized. The status light will blink four (4) times.
· The room thermostat reacts to a demand for heat.
· The control will then check to insure that the vent
pressure switch is open. If, at this point, the vent
pressure switch is closed the control will blink two (2)
times and will remain inoperable until this situation is
corrected.
· The venter blower is energized.· The vent pressure switch will close when it detects a
pressure in excess of its setting. If the pressure switch
fails to close the status light will flash three (3) times.
The sequence cannot continue until the pressure switch
closes.
· After a pre-purge of about ten (10) seconds the electronic
ignition device will be energized.
· After a slight delay the gas valve will open.
· The burners will ignite and the flame sensor will detect
the presence of flame. The ignition device will
deenergize. If the sensor does not detect the burner
flame, the gas valve will close and the ignition cycle
will be repeated for a total of three attempts. If, after
the third attempt, the presence of flame is not detected,
the furnace will go into a lockout condition for one (1)
hour. It will then repeat the ignition cycle. This one (1)
hour lockout and retry will occur indefinitely.
· Thirty (30) seconds after the main valve is energized
the circulating air blower will be activated.
· The furnace will remain in operation until the demand
for heat is satisfied.
· Once the demand is satisfied the venter will shut off,
and the circulating air blower will shut off after the field
selectable time off is attained.
· The furnace will remain dormant until the next demand
for heat.
Dec 03, 2010 | Goodman GMS80903BNA Heater
Goodman GDS80904BNA LED Blinks 3 Times
had similar problems with same furnace. I think the 3 blinks is high limit event. either way with the power off to the furnace remove the board from the 4 clips holding it on one at a time then turn it over and look at it you will be able to tell if the board is bad because it will appear scortched and the resin will be bubbled up where it went bad. replace board and you will be fine. went through 2 in 2 years all of a sudden they are being made by a different company from the original and the 1st replacement. now all is fine. Take a good picture of the board close up so you can reconnect all the wires properly. Friend of mine got it from a wholesaler for $55.00
Dec 12, 2009 | Goodman GMS90703BXA Heater
RED BLINKING (6TIMES) ON FURNACE
THE ROLL OUT SWITCH IS LOCATED IN THE BURNER COMPARTMENT MOST CAN BE RESET
Jul 20, 2009 | Goodman GMS90703BXA Heater
Goodman furnace went out. Light blinks four times
Your main limit switch is activated. Maybe for good reason. This switch keeps the furnace from overheating. I have the same problem right now and I think my a/c coil may be blocked, limiting air flow through the heat exchanger and the furnace. Does your gas and main circulating fan come on for a few minutes before the switch activates and the light begins blinking?
Check your furnace filter and any return air ducts in your home - see if they are blocked or restricted.
Jan 14, 2009 | Goodman GMS90703BXA Heater
Goodman furnace blinked 1 time
Furnace attempted to start but failed after so manay tries. This may help you.
Sequence of operation, Gas Furnace.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
This is why we technicians earn the big bucks!
Dec 05, 2008 | Goodman GMS90703BXA Heater
Goodman GMS90904CXA Wont ignite, light blinks 3 times
I had the same problem, I had to remove the lower black rubber stopper right next to the exaust fan and hook up a drain to the unit, as soon as the water drained out the furnace fired right up.
Nov 19, 2008 | Heating & Cooling
GOODMAN CMA80905CXBA FURNACE. INDUCTION BLOWER NOT ENERGIZING. GETTING 3 "BLINKS" FROM DIAGNOSTIC LIGHT (LOW PRESSURE SWITCH OPEN). THE A/C WORKS & THE BLOWER FAN COMES ON WHEN THE STAT IS IN...
the pressure switch is closed before the draft motor closes it.the board is telling you that this is not right.pull the wire(either) off of the pressure switch to see if furnace tries to light.if it does,you should replace the pressure switch.
Oct 02, 2008 | Goodman Heating & Cooling
Goodman GMS90703BXA Heater Logo
115 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others