Question about Amcor AMD243HX Air Conditioner
Amcorair 2-zone mini-split ac not cooling, compressor cycling
I have 2-zone mini-split ac; 2 indoor model AWM123HX & 1 outdoor model AOM243HX. Bought in july 2009, put in storage and finally installed May 30, 2010. Installed per manufacturer instructions. Pressure tested using nitrogen - no leak. Vacuumed for 10 minutes; vacuum leak tested for 15 minutes - no leak. Opened service valves and ran okay. First 2 days, units were cooling properly. Later, when on cooling mode, P4 flashes about 20 times and then temperature setting return. On auto mode, no P4 flashing but not cooling adequately. Compressor runs for 2 minutes and cycles. I suspect it's lacking 410A refrigerant. What do you recommend?
SOURCE: amcoraire / aos241hx / code p8 / unit shut down will not restart
for all error codes. http://www.digelair.net/pdfs/TECHLIT/MITSUBISHI/MrSlim_P-SERIES_Troubleshooting_TIPS.pdf
Posted on Jul 13, 2009
  • 288 Answers
SOURCE: AC unit Amcoraire AOS241HX
these should be seperate circuits so lets forget the condensing unit for a moment. It should not come on because it gets the control voltage for the contactor from the indoor unit. Check your circuit board for a 3 or 5 amp fuse and make sure it hasnt blown. If it has you will get nothing past the board. If that isnt the case, you will have to start checking for supply voltage from the panel to the disconnect at your furnace, disconnect to board(transformer may also be bad) the blower motor. transformer, and circuit board are the only components indoor that effect the outdoor unit.
Posted on Jan 08, 2010
  • 73 Answers
SOURCE: Split AC system not cooling.
P-7 Error Code means: DC Voltage Problem in the outdoor unit.
Bad PFC & IPM Circuit Boards.
The Pridiom Group
201-266-8234
Posted on Nov 03, 2010
richroth
  • 9472 Answers
SOURCE: Have AMCORAIRE mini-split purchased in
Try this link. They will be able to help you with your concerns.
The FixYa Team
Posted on Dec 28, 2010
hvac1960
  • 2133 Answers
SOURCE: I have a 24 ton
Code P8
Error detail Abnormality of pipe temperature.
Inspected unit Indoor. Due to non condensable gas/over charged/condenser dust blocked.
For non condensable gas, remove gas and flush out and then recharge gas./remove over charged gas/clean condenser coil
Posted on Jan 01, 2011
WHAT IS REFRIGERANT SUCTION PRESSURE OF MY 1 TON SPLIT AC?
R22= 70-80psig
R410a=120-130psig
Depending on many variables such as blower speed, coils clean, indoor/outdoor temps.
Aug 05, 2015 | AMVENT 18000 Btu 1.5 Ton Ductless Mini...
E 7
Multi Splits and Multi V = indoor unit is set to run in a different mode from the master indoor unit. Set ALL indoor units to cooling or ALL to heating to clear.
Splits = Compressor Over Current (CT2), Check loose wiring/condenser coil for clean
Jan 10, 2011 | AmcorAire UCHW-H24AF2 Split System Air...
The Pridiom Group
201-266-8234
Jul 26, 2010 | AmcorAire UCHW-H24AF2 Split System Air...
Hello im trying to trouble shoot two split systems the electrical wires were crossed for the two units I fixed it the compressors wont come on, wall unit says e7? This is on the Amcoraire ac split systems.
E7 indicates an "External Feedback Problem" which sounds like a communication problem. I believe there is a sensor cable that runs from the outdoor unit to the indoor unit also. Check that all cables are properly run to the appropriate unit and check all connections for tightness. Here is the link to a manual that includes installation and wiring instructions.
http://www.acwholesalers.com/EasyEditor/assets/amcor%20duo%20uchw-h12%20owners%20manual.pdf
Mar 16, 2010 | AmcorAire UCHW-H12AF2 Split System Air...
AC unit Amcoraire AOS241HX @ startup i have power to the L1, L2 power inlet terminals to the outdoor unit but no power to the lines going up to the indoor unit. What can I do to correct problem?
Jan 08, 2010 | AmcorAire UCHW-H24AF2 Split System Air...
York Mini-Split Not Cooling? : (
This can only be a gas problem.
the split units goes on on and off if a shortage of gas is involved, the chances that you would here it wont be that big for the fans would make too much noise.
get a repair man for a re gas and all is well.
Good luck.
Wouter.
Oct 21, 2008 | Sanyo 09KS51 Mini Split Air Conditioner
Sharp Air Conditioner. Model # AF-S85NX. Does this A.C. fan cycle on & off in the auto cool mode or does remain on continuously. I need a small A.C. that cycles off and on with the compressor.
If you set you r AC to FAN mode the unit will not cool, it only runs in the indoor but the outdoor will off. If you set to AUTO the unit will cool but the indoor blower will automatically run slower when the room is cool or attain the room temp. setting. If you set it to COOL the fan speed is fix depending on your setting and it also operate in cool.
Apr 19, 2008 | Heating & Cooling
Amcor AMD243HX Air Conditioner Logo
59 people viewed this question
Top Amcor Heating & Cooling Experts
AJMAL KHAN
Donni Steen
Bill Long
Are you an Amcor Heating and Cooling Expert? Answer questions, earn points and help others