Question about Electric Intermatic T171 24 HOURS 40 AMPS 125 VAC 1 SINGLE ELECTRIC TIMER SWITCH
I want to connect a single phase 24 amp kiln under my waterproved pergola. What electrical work needs to be done and how much would it cost approxmatly?
  • 565 Answers
That kiln requires a 30 amp circuit, minimum. 24 amps x 125%= 30 amps per National Electric Code (NEC).
Without more info, I'll need to make a few assumptions. For the sake of estimating the cost I'll present the following scenario:
1...The distance from your electric panel to the pergola is approximately 100 feet.
2...The circuit will be underground. I'll assume that you will be able to hire someone to dig an 18 inch deep trench from the electric panel to the pergoda for $10 hr. While this should only take 3 or 4 hrs, depending on soil conditions, it could take all day. So I'll assume $80 for this.
3...This will be a 240 volt, 30 amp circuit (see why below).
4...Since you posted under the Intermatic T171, and since that is a 120 volt timer, that the kiln is 120 volts.
5...Unless the pergoda is fully enclosed, NEC still requires a weatherproof installation.
For starters, I don't recommend a 120 volt kiln. Most people I've known who had a kiln always seemed to want a bigger one ;-) Again, I'll do the estimate for a 240 volt, 30 amp kiln, as the price difference compared to a 120 volt circuit is about the same.
Also, I strongly recommend using 3/4 inch PVC conduit as opposed to 1/2 inch PVC or UF (direct burial) cable. 3/4 inch conduit doesn't cost much more than 1/2 conduit and will allow you to install wire up to #6. UF cable, in my opinion, is out of the question because if you ever decide that you want a larger kiln the direct buried UF cable is _not_ easily replaceable. A conduit and wire installation is about the same price as UF anyway.
Here's the breakdown (US dollars):
$ 10 - 30 amp, 2-pole circuit breaker
120 - 300 feet of #10 THWN COPPER wire (40 cents a foot)
20 - 1 bundle (100 feet) 3/4 inch PVC conduit
10 - 3/4 inch PVC elbows, fittings, straps
20 - Weatherproof box and weatherproof cover
+15 - 30 amp receptacle
______
$195
+100 - 2 hrs labor @ $50 hr. (possibly 3 hrs.)
______
$295
+80 - labor for trench
______
$375
+140 - Intermatic T172R (weatherproof) 240 volt timer
______
$515
Other considerations are that, if indeed, the circuit is 100 feet, you should consider using a #8 THWN COPPER wire to account for voltage drop (add $60, @ 60 cents a foot) Using a #10 wire at that distance may not allow the kiln to get to the desired temperature.
If you are anticipating things like lights, 120 volt receptacles, fans and such, the best way to do all that is to install a subpanel at the pergoda.
That should get you in the ball park as far as price. Of course, you can make adjustments accordingly. Remember that prices can vary greatly depending upon geographic location. Also, if you call a contractor for an estimate, _after_ they give you the price, _then_ ask how much they will knock off if you dig the trench.
A contractor price of $600 would not be unreasonable.
Hope this helps.
Posted on Jun 02, 2010
I purchased a 3 phase electric motor by mistake. but i needed a single phase, anyway to wire it down?
You cannot make a 3 phase motor into a single phase motor.
You could, ( as you suggested), buy a single phase to 3 phase inverter. Even a 'variable speed drive' VF (variable frequency drive) inverter for greater flexibility, but depending on the size and purpose of your motor the cost might prove to be prohibitive.
May 14, 2018 | Microwave Ovens
Tip
How to Reverse the Rotation of Single Phase Capacitor-Start Electric Motors
Reversing the rotation of electric motors can be done easily with 3-phase motors. This can be easily achieved by swapping the connection of any two motor leads. But 3-phase motors are usually found and used for industrial purposes. The ones found and used in our homes, from water pumps to electric fans, are single phase capacitor-start type motors. Unlike 3-phase motors, reversing the rotation of single phase electric motors is no easy task. Swapping any two motor leads will not result in the reversal of the motor rotation. Analysis of the motor windings and connections are necessary before any modification can be done to achieve the desired result. Let's take a 3-speed single phase capacitor-start electric motor with electrical diagram shown below as an example. Make sure the motor is disconnected from the power supply before attempting to follow this tip. This tip is intended only for individuals with electrical knowledge, necessary tools, and understand the risks associated with handling electrical equipments and devices.
The first step in the process is determining the start winding which is connected to the line (AC white) and to one side of the start capacitor. To accurately determine the start winding, disconnect all motor leads from the start capacitor and the speed switch for multi-speed motors and then setting your ohmmeter to the lowest scale (R x 1), measure the resistances between the AC white line and each of the motor leads connecting to the start capacitor. The one with the least resistance is the starting winding lead.
Once the start winding lead going to the capacitor is determined, reconnect the capacitor then connect the black AC line to the found start winding lead (marked X). Connect the white AC line to L of speed switch, the motor lead formerly connected to AC white to 3, red to 2, and white to 1 as shown below. Leave the green/yellow ground wire connection as is.
Below are the wiring modifications for 2-speed and single speed single phase capacitor-start electric motors.
on Jan 11, 2011 | Dryers
The daikin RYYQ28t has a maximum circuit amps of 31amps and 24amps on 400v Is the amperage over each phase as in 31 amps 10 amps per phase and 24 amps 8 amps per phase
Circuit amps is 31 amps per phase and 24 amps per phase at rated voltage. Phase current should all be very close to equal on all 3 phases, unless there is a second, single phase load on two lines, or one phase to neutral.
If you need further help, I’m available over the phone at https://www.6ya.com/expert/craig_3fa289bf857b1a3c
Jan 24, 2018 | Electrical Supplies
I am buying a ceramic kiln. What is the max Kw output I can use with standard single phase UK household supply?
You will get that information from the company you are buying the kiln from in there specs
Jan 18, 2017 | Heating & Cooling
Single phase or 3 phase
Hmmm. Good question. Like anything, it varies depending on how the equipment is going to be used and in what environment. We could really get into the weeds, but let's just ask the couple of key questions.
1. Is this a commercial or residential environment?
2. What's the horsepower of the motor(s) in use?
3. What's the availability of 3 phase power?
1. If your saw is in daily, commercial use, then 3 phase may offer some distinct advantages: While it's expensive to convert (assuming you don't already have 3 phase available) it allows for smaller, less expensive wiring, and lower voltages making it safer and less expensive to run.
Single phase, otoh, is much more available, and runs motors up to 5hp with little difficulty. It does actually cost more to run a lot of single phase equipment so if cost is an issue and you have quite a few motors, this may be a large determining factor.
2. As I mentioned, if you're only running one or a couple smaller motors, up to 5hp, single phase should work just fine. I have several pieces of machinery with 5 hp motors them on single phase 220 and they perform great. I don't recommend 110vAC for motors under significant load. They run too hot and are not all that efficient, as well as under-powered.
3. Installing a 3 phase electrical system can be very expensive. I would look into this carefully, get a few estimates before moving ahead. You'll need to find out if it's even available, cost of transformers for 110 in the building as well as whether they'll charge you commercial rates for your electricity once it's installed.
There is no simple answer for this question, I fear. There are simply too many factors to consider.
This is the short answer. A simple web inquiry will give you more answers than you actually need.
Good luck.
Jan 02, 2016 | Saws
The set Code button on my Cress E27 kiln quit working, so I need a wiring diagram to determine if q wire is disconnected or corroded
Could you let me know if its the stock Cress controller or other controller. I have the schematics to a Skutt controller. They operate some what the same. Knowing the voltage and phase of your electrical supply connection would tell me what to send you.
Stevan
spiescic@cogeco.ca
Mar 09, 2014 | Cars & Trucks
I need to run a contactor ( 40 amps 3 phase ) with the help of thermostat..i have connected L1,L2 n L3 and output coneccted in T 1 T2 T3 . now how to connect A1 and A2 .... i want that contactor should...
1) Copy following links for illustrations showing timer controlling contactor in 3-phase environment:
http://waterheatertimer.org/How-to-install-3-phase-timer.html
http://waterheatertimer.org/images/3-phase-timer-diagram-24Vac-865.jpg
2) Substitute thermostat instead of timer for switching control.
3) I don't know what thermostat you have, or if it's functioning or the rating.
4) Which contactor do you have?
Do you have a 3-phase contactor??
Or two-pole single phase contactor?
5) Match thermostat output voltage with contactor voltage:
Thermostat output is 24 volt? Then use 24Volt coil on contactor.
Thermostat output 120 or 277 > then use contactor with same coil rating.
6) More information is needed.
I don't understand description of your wiring.
Add a comment and compare with illustrations sent, so I can visualize ... or attach photo and/or give product numbers so maybe I can locate wiring diagrams.
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
Jan 31, 2013 | Connecticut Electric Electrical Supplies
Wiring diagram for three phase power with two 200 amp service boxes inside building
This work requires a license (or qualified person) everywhere that the National Electrical Code is enforced.
If you're asking how to wire a single phase 200 amp panel from a larger, 3 phase panel of the same voltage - ONE way is to install a 2 pole - 200 amp breaker into the 3 phase panel. Provide 4 correctly sized conductors with the correct insulation in a cable or conduit between the 3 phase panel and the 200 amp single phase panel. Two of these conductors should be black and red (for 120/208 volt system) and connect to the 2 pole - 200 amp circuit breaker terminals, the third should be white and connected to the neutral bus bar. The forth should be green and is connected to the neutral bus bar as well but *only if* it is "service equipment" If it is a "main or sub panel", the green wire should be connected to the ground bus bar. The other end of the conductors should be terminated in a "main lug only" 200 amp panel. The back and red connect to "line 1" and "line 2" bus lugs, the white to the neutral bus bar that is NOT electrically connected to the panel enclosure (do not install the screw or strap between the bar and enclosure). The green must be connected by installing a separate bar that is securely fastened both mechanically and electrically to the enclosure for ground connections.
There is a great deal going on here - and plenty of variables that can change how to do this work, safely and correctly. This is an example of just ONE of many different ways to do the work for a particular installation. There is no one way that works for all situations. If your situation does not support this method - you will have an unsafe installation and subject the building and people in it to a dangerous fire / safety hazard.
Please, consult a licensed electrician before attempting this work.
Nov 17, 2011 | Square D Qo 200 Amp 40 Circuit Indoor...
I have a 220 440 electric motor on my 4 post 3 ton car lift which ran on 3 phase, how can i run this motor from a single phase supply, regards dave
You need to either change the motor to a single phase or check into a single to three phase converter...I would do which ever is cheaper myself. You could go single phase, but the cost of operation would be higher depending on the duty cycle.
This link may help: http://www.phaseconverter.com/starting-load.html
HTH
Mike..
Nov 20, 2009 | Plumbing
Electric Intermatic T171 24 HOURS 40 AMPS 125 VAC 1 SINGLE ELECTRIC TIMER SWITCH Logo
201 people viewed this question
Top Electrical Supplies Experts
ashburton
Steve
epangan29
Are you an Electrical Supply Expert? Answer questions, earn points and help others