How to install a S84-17 TRANSFORMER FAN CONTROL 40VA for gas furnace- need to know if the yellow wire connects to the upper black wire (in back) or the lower black wire...
2 Suggested Answers
  • 74 Answers
SOURCE: We are working on wiring a new S84-17 transformer
is this the yellow wire from the thermostat? if so it will go on the terminal Y along with one of the wires that go out to the a/c unit outside the other wire from the a\c unit will go to C
Posted on Jun 15, 2010
I need to install a White Rodgers transformer thermal control relay combination on my gas furnace but I am not sure of the wiring connections.
This is going to be a tough one to explain, but from the schematic I found, this is a transformer/controller all in 1. So we are using this 1 module for 2 purposes. The R terminal should connect to the wire that's connected to R at the thermostat. And the C terminal should connect to the C wire coming from the C terminal at your t-stat(if used), as well as your common that returns power from your contactor at the o.d. unit. You'll have 2 wires going to the o.d. unit, 1 connects to Y and 1 connects to C to the 8a501 box. The G and W should also be connected to the wires that connect to G and W at the t-stat. That is your low voltage side. Now, this line voltage side is more difficult. You'll need to know what wires are your fan speed taps on your blower motor. And also, does your unit close the N/O(normally open) contacts for heat or cool? Normally it closes for cooling, so your high speed wire would connect to the n/o wire, and your line voltage supply would connect to the bulk/yellow. And then your medium or low wire from your blower would connect to the N/C wire. The schematic is there on the side of the module. This may be beyond your experience and may cause motor winding failure with in seconds of operation. Also, ensure with a volt meter that all power is disconnected! And all run capacitors are discharged! I've not wired 1 of these modules but from the schematic, seems simple, AS LONG AS YOU KNOW WHAT THE MOTOR SPEED TAPS ARE. Hope this helps, and if you're unsure, call a professional. The labor should be less than the cost of a damaged motor.
Aug 20, 2017 | Heating & Cooling
I hooked up a coleman electric furnace to a janitrol condenser heat pump . The t-stat wires on electric furnace are red white green and yellow. I added a blue for common off of transformer for digital...
Hi, first of all you need to get a hand full of 5 amp auto type fuses and install one on the hot leg of the 24 volt secondary side of the transformer. Just use 2 female crimp on connectors and put the fuse in the middle of the hot wire. Saves $$$$ on replacing transformers when you have a dead short on the low or high voltage side of any transformer, just a trick of the trade, food for thought. Fuses are much cheaper. On your electric unit, you may not need the common on this to operate the digital stat if it has batteries. This may be your dead short. On the Janitrol condenser, the red is your 24v as you no. They are using blue in place of yellow for cooling. Red is hot, W is heat, G for fan, and blue is cooling on this Janitrol. Keep in mind you are connecting to a heat-pump also, so make sure the wiring is correct. Are you installing this for secondary Heat?? More then likely, the blue common you have added is the dead short as the janitrol uses the blue for a cooling relay in place of yellow. Anyway, use the 5 amp fuse, trick of the trade to save on the transformers. Please keep me posted, as I know know you have this under control.
Shastalaker7
A/C, Heating, & Refrigeration Contractor. Good Luck!
Feb 09, 2011 | Coleman Heating & Cooling
How to set a NOMA HTM311A thermostat
Go to the furnace, and see what the black is connected to. If it is not the Y terminal, disconnect it from the Y terminal at the thermostat. While you have the furnace open, check for a blown fuse inline to the transformer or on the control board. If the black was connected to the common or the transformer, and you connected it to the Y, and turned the thermostat to cool, you would have a direct short across the transformer output. You can use a black wire to control the A/C, but both ends need to be connected to a Y terminal.
If you still remember the where the 4 wires were connected to the White Roger thermostat, take note of the name of the terminals the 4 wires are connected to. That may help as sometime the colour of the wires are not always correct.
Or you really want to test it out:
connect RED wire to GREEN wire should turn on the fan
connect RED wire to WHITE wire should turn on the heat
Did you disconnect the power at the furnace first? Maybe you blew a low voltage fuse.
Make sure you increase the heat setting to go above the room temperature.
Thermostat wire color codes explained.
Please note. Not all installers use the proper color codes when they install or replace equipment. It may be necessary go go to the furnace or outdoor unit to verify what wires are for what purpose. Also be sure there are no splices in the wire that could change the wire colors between components.
R (red) or Rh (Red heat) 24 volts from equipment.
Rc (Red cooling) 24 volts from transformer in cooling equipment.
Note: If only furnace has a transformer and cooling equipment does not jumper Rc and Rh.
W (White) sends 24 volts to furnace control to start the heating cycle.
W2 (no standardized wire color, usually whatever wire color is available) controls second stage heat.
Note: W2 is most often used for heat pumps to control what is called emegency heat or Auxillary heat, and most often will use the white wire.
Y (yellow) often (blue) is used, controls cooling unit (outdoor condensing unit) also is used for heat pump heat.
Y2 (no standardized wire color, usually whatever wire color is available) controls second stage cooling.
G (Green) controls the fan "on" operation of the furnace/air handler. Also often is used to start the blower for many electric furnaces.
C (common) most often brown but can also be black or other color available to installer.
O (orange) Energizes heat pump reversing valve for cooling (Trane and most other brands).
B (Blue) Energizes heat pump reversing valve for heating (Rheem, Ruud and Weatherking).
Hope it helps.
Thanks for using fixya.....
Nov 29, 2010 | Heating & Cooling
We are working on wiring a new S84-17 transformer fan control 40VA to our ancient Rheem furnace and had forgotten to label one of the wires. Trying to figure out if the yellow wire ties in with the upper...
Jun 12, 2010 | Heating & Cooling
Installed dayton nat gas hanging furnace in garage and have 2 wires dont know where they go one came from the back side of the transformer it was twisted with the other wire
Hopefully there is a wiring diagram glued to one of the panels to verify but on the transformer you will have 2, 110 volt wires. One is the power coming in (usually black wire) and the other is a common (white wire) and will be connected to other common leads. On the low voltage side of the transformer one wire will go to the thermostat then from the thermostat to the gas valve. The other side will connect to the gas valve. When the thermostat calls for heat it completes the circuit from transformer to gas valve back to transformer.
Dec 11, 2009 | Dayton Gas Furnace Heater
I WANT TO HOOK IT UP TO A FAN,BUT ARE NOT SURE WHICH CONNECTIONS TO ATTACH TO.
In order to hook this up to the fan on your furnace, you will need to either have or install a Fan center @ the furnace. (Unless it is gas, and has a circuit board that will simplify the process) All this is, is a transformer, a relay, and a set (or two) of NO and NC contacts. You will need to run 3 wires from the thermostat back to the furnace, if you do not have them already. If you have a gas furnace with a circuit board then all you have to do is connect the three wires from the thermostat to the board. (R to R; W to W; G to G. If you are using an older furnace, or a oil fired appliance, power should go out of the transformer (secondary side) to the thermostat on R. It should then come off W and another wire off G back to the furnace. Connect to the appriately marked terminals on the fan center. Hope this helps
Nov 19, 2009 | Honeywell International Honeywell&...
I need help with my central heat and air unit, it has a heat pump. the model number is GQ3RA-036K. I am changing the theromstat out and the wires are connected to it. there are eight wire colors that are...
Normal 0 MicrosoftInternetExplorer4 /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman";} Thermostat wire color codes explained.
  • R (red) or Rh (Red heat) 24 volts from equipment.
  • Rc (Red cooling) 24 volts from transformer in cooling equipment.
  • W (White) sends 24 volts to furnace control to start the heating cycle.
  • W2 (no standardized wire color, usually whatever wire color is available) controls second stage heat.
  • Y (yellow) often (blue) is used, controls cooling unit (outdoor condensing unit) also is used for heat pump heat.
  • Y2 (no standardized wire color, usually whatever wire color is available) controls second stage cooling.
  • G (Green) controls the fan "on" operation of the furnace/air handler. Also often is used to start the blower for many electric furnaces.
  • C (common) most often brown but can also be black or other color available to installer.
  • O (orange) Energizes heat pump reversing valve for cooling (Trane and most other brands).
  • B (Blue) Energizes heat pump reversing valve for heating (Rheem, Ruud and Weatherking).
May 07, 2009 | Heating & Cooling
Need wiring diagram for a carrier 383kav11048075? im replacing the icm281 control module. gas furnace
There should be a wiring diagram on the panel of the furnace. In the box of the icm 281 is step by step instructions.
Maybe this will help
Take notes on your low voltage wires from the thermostat and condenser. W Y R C G. Write down what color wires go to above terminals.
On your high voltage wiring,
Take the black wire from the transformer and put it on PR-1.
Take the white wire from the transformer and put it on PR-2
Take the black power wire from the panel interlock switch and connect it to L1
Take the white neutral power wire and connect it to L2
Take the black fan motor wire and connect it to HI
Take the red fan motor wire and connect it to LO
Take the white fan motor wire and connect it to COM
Then reconnect your low voltage terminal wires to W Y R C G.
Thats it.
May 03, 2009 | Carrier Heating & Cooling
Air handler
This should be doable: First get pen and paper-start at the furnace, theres a group of 5-8 wires leaving the furnace anfd going to the thermostat and a group of 2-3 going to the condenser outside that all need to be identified and the location in the furnace recorded if your furnace has a control board simply right the letter and the corresponding wire color:and whether it belongs to the condenser grp or the T-stat grp.
Furnace
R-red-to t-stat
C-yellow to cond
Y-red to cond and yellow to t-stat
G- green-to t-stat
W- white- to t-stat
If you dont have a circuit board youll be doing the same thing but using the components rather than letters;
Transformer 24v- red to t-stat
transformer 24v com -yellow to cond
Red from cond connected to yellow from t-stat
fan relay - green to t-stat
gas valve - white to t-stat
K then go to you t-stat and simply connect the corasponding component or leter to the thermostat gterminal
Cond Furnace Thermostat
yellow com- blue -C or B
gas valve or w-white -W
fan relay or g -green -G
trans 24v or R -red - R
red connection to cond or Y on board -Y
Hope this helps.
Jun 12, 2008 | Quasar HQ2052UH Air Conditioner
No y connection on furnace module to connect a.c. This is on a goodman model gmp075-3 furnace. I bought the b18099-13 replacement module and still no y terminal. I dont know were to land the t-stat...
"Y" terminal at the stat feeds condensing unit outside, common from the condensing unit to common on the furnace transformer.
"G" terminal on the stat brings the fan on for air circulation. In cooling mode "Y" terminal also brings the fan on. If this furnace was not A/C ready check the VA capacity of the transformer. Should be about 40VA. Make sure there is a fan relay to bring the fan on in the cooling mode.
May 01, 2008 | Heating & Cooling
Heating & Cooling Logo
83 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen