Self-mode test indicates 'operation of compressor protection circuit' problem
  • rjdubroff May 31, 2010
    thanks for your comments
  • 8,404 Answers
Your machine is protecting itself from a fault of some type. More than likely, unless you are a AC mechanic, you will have to have this professionally repaired. Without a code, it is difficult to give you additional information.
I would expect it needs protection because of a coolant leak, air block, motor stall.
You may want to consider posting your question in the "local repair" section of FixYa.com. In that section, mechanics in your area can contact you directly to assist in the repair of your system.
Thanks for your interest in FixYa.com
Posted on May 31, 2010
  • 1 more comment
    I am not an AC mechanic but somewhat handy. I opened the outside unit and noted the solenoid does not actuate when power is turned on. I am going to try to replace the solenoid contactor for $25 and see if that solves the problem. If not, I'll have to hire someone to fix it.
    Thanks,
  • A Miller May 31, 2010
    I am somewhat handy also ...
    My question to you, in light of the new information you have presented, is ... this solenoid you are spending $25.00 on to replace ... because it is not activating ... is that because it is faulty or is it because the "protection circuit" is not allowing it to come on (for self preservation). Have you independently evaluated its mechanical operation - translation: if you turn off the power to the unit, can you apply an external power source to the solenoid and activate it? Have you performed a continuity test on the coil of the valve? If you can activate it independently from the unit, it is doing what it is suppose to do ... and you will have spent $25.00 to replace a perfectly good functioning part, and, you will have accomplished nothing. If there is no power going to the solenoid, you have to go back in the circuit and find out why the next component is not allowing power to come on. Low pressure - Hi pressure - no pressure - blockage - blown fuse - other condition)
    I can tell you my friend - I have LOTS of experience in this area - I have made LOTS of unnecessary trips to the store to purchase LOTS of replacement parts for parts that were not faulty to begin with. I AM NOT SAYING this is the situation in your case!!! I am saying that is my experience.
    Sometimes, the best way to communicate a idea by another example.
    In your automobile, there is a switch that reads pressure in your car's AC system. If it reads pressure, that switch allows other components of the system to operate. If there is no pressure, there is probably no or low coolant in the system. This switch prevents the AC from coming on. If it came on with low or no coolant, you could damage the system requiring expensive repair to expensive parts. You can short this switch out and make the AC work ... guess what happens next ... expensive repairs.
    I think there is some other trouble with your AC - I wish you good luck and I hope you are able to repair what ever the trouble is. Don't be afrade to call in a Pro to look at it. Handi as I am ... I call the pro when necessary (and hate every second of it - watch him like a hawk - and try to learn)
    I will leave you with this ... My old preacher buddy who spent most of his life in the bush in darkest Africa said 'Things are made to work. Things are not made to not work. Everything can be brought back into order if you will study them'
    Thank you for your interest in FixYa.com
    Thank you for your 4 thumbs up ... I need all the thumbs up I can get ...
    I hope you get your AC working before the hot season begins ...
    a
Outside unit is not working
Aside from checking the circuit breaker for the unit, the unit should be looked at by a qualified service technician. You would need certain test instruments and a working knowledge of the unit's operation system to find the problem.
May 26, 2014 | LG LSU307HV 30,000 BTU Ductless SingZone...
Inverter manuals
Model No Required below Model No AH-X18MEV Self diagnosis mode given
1. Indoor unit
(AH-X18MEV, AH-X18MEV-1, AH-X24MEV, AH-X24MEV-1)
To display the self-diagnosis, hold down the AUX button for over 5 seconds on the indoor unit when the indoor unit is not operating.
• The operation lamp (red), timer lamp (orange) and Super jet lamp lighter) flash to indicate the information of malfunction.
(Display of self-diagnosis result)
The operation lamp (red) and the Super jet lamp (green) flash in synchronization with the timer lamp (orange).
(AH-XP18MV, AH-XP18MV-1, AH-XP24MV, AH-XP24MV-1)
• The POWER CONSUMPTION indicator indicates the information of malfunction by showing the main category error (number) and the sub-category
error (-number) alternately in 1-second intervals.
Example: Compressor high-temperature error
Remark
• If the power cord is unplugged or the circuit breaker is turned off, the self-diagnosis memory is lost.
AUX
Operation lamp(red)
Timer lamp(orange)
Super jet lamp(green)
Oct 12, 2013 | Sharp Heating & Cooling
Problem with Air Conditioner
there will be an access panel where the motor is located. 1st thing to check is fuse or circuit breaker feeding the air handler. this is on seperate power from compressor unit outside and usually has a fused or breakered disconnect on the side of the unit. if fuses are good or breaker is not tripped then switch fan mode to on. if blower runs in on but not in auto then it is a thermostat problem. if still no go then turn off power, remove access panel and find the squirrel cage fan blade. make sure it turns freely. it is very common for these motors to go bad. it can usually be removed easily and taken to a motor shop. I use Roy's Electric in Richmond, Va. They can test the motor on the bench and replace it if it is faulty.
Sep 08, 2012 | Heating & Cooling
We have one of the ACC108PS air conditioners that is not cooling right - do we need freeon - if so is it rechargeable?
Start your window air conditioner troubleshooting with checking the different modes of operation to see which components operate. Turn the unit fan to on and the cool and heat modes off. If the fan does not operate, check the power supply to the unit. Check to see if the breaker or fuse for the unit is tripped. If the breaker/fuse is tripped, check to make sure that it is the proper size circuit for the unit you have. On some units, there is a current interrupter on the power cord to the unit. Check to see if it is tripped by pushing the reset button.
If the circuit is the proper size, then you can go ahead and reset the breaker/fuse. If it trips again, then you require further troubleshooting. Shut the power off and check all of the wiring in the unit to make sure that none of the connections is loose or damaged.
If the fan does not operate but the fuse/breaker is not tripped, you should check the run capacitor for the fan and compressor. If the capacitor is good but the fan motor does not operate, you can check the fan switch and the fan motor. Ensure that the fan blades spin freely.
If the fan motor operates but the compressor does not start, change the capacitor but first you should feel the compressor with your hand. If it is very hot, then you should allow it to cool.
Then, you should attempt to start the unit in the cooling mode. As you do so, listen for a clicking sound which is an indication that it is attempting to start. If the compressor starts but does not cool properly, the unit may be low on refrigerant.
If the compressor attempts to start but shuts off very quickly, the compressor could be bad. You could try installing a "Hard Start"
If the compressor does not attempt to start, ensure that the thermostat is set below room temperature. On units with a mechanical control, you will hear a click when you adjust the temperature. That is an indication that the thermostat is working properly.
Jul 12, 2011 | Whirlpool ACC108PS Air Conditioner
AC compressor wiil not turn on
You will have to find the contactor which is located in the outside unit. And check the voltage at the contactor, 26 v as this is the thermostat calling for the compressor to come on. You can also push in the contactor and see if the fan and compressor start. There should be an outside fuse box close to your condensing unit. Good luck
Jul 23, 2010 | Samsung AW1203B Air Conditioner
THE MONITOR OF INDOOR UNIT DISPLY ALL THE
This could be caused by a blown circuit breaker or fuse inside the unit, a damaged compressor or fan motor, faulty wires connecting the compressor or fans to the control board unit, a faulty or hung relay on the control board (this can sometimes be solved by tapping the relay with a screwdriver), or the starter capacitor for the compressor or fan motor.
Sep 17, 2009 | Samsung AQ24 Air Conditioner
Both inside and outside units did not come on in cool mode
hi there,
thermostat located on your evaporator is adevice where in if temperature set up is acquired the power source will cut off until on specific time that when small heat absorbed thermostat will activate again or this auto activated.meaning there is a differtianl temperature acquited to run this device.this depent how you set up your temperature setting.the over load protection device located mostly on control panel is one tripping off.this is the device you have to reset in order to run the unit again if malfunction., if short circuited or highr current occured on compressor this device protect your motor to burn it will trip off your unit.several factors you can consider in tripping unit,fan motor not running,dirty evaporator and condenser,loosen wiring connection and faulty wiring.sometimes circuit on panel board are envaded by insect mostly ants they need heat for there egg to hatch, they davastated the circuit.check on this.have a nice day don't forgert to rate me thank's.
Apr 12, 2009 | Friedrich QuietMaster Electronic SS12J30D...
Aprilaire 600 Humidifier
J-
I had this problem several years ago. In order for the water to flow, the outside temperature sending unit must indicate to the controller that it is less than 60F. If not, the unit will not operate outside of test mode. Check the temp outside where your sending unit is (could the sun be heating that side of the house?) and ensure that the circuit to the sending unit is working. I had a bad wire splice inside a wire nut stopping the circuit. Took me a long while to figure it out.
If the outside temp and your sending unit circuit is ok, I wish you luck on your troubleshooting.
adx_98
Nov 10, 2008 | Aprilaire 600 Humidifier
My colmen central air unit is not working properly. The Outside unit is not working. The problem initally arouse in June, but it "self corrected" after having the A/C unit turned off. Since that...
If nothing is running outside at times you probably have a weak contactor coil that is not pulling the contactor in all the time. If the outside fan comes on but not the compressor, the compressor is over heating and shutting off on overload protection. This could be a dirty condenser coil, low on refrigerant, the compressor it's self. The compressor comes with a 5 yr. warranty.
Sep 27, 2008 | Coleman Heating & Cooling
Ruud heat pump outside unit trips circuit breaker
Check your wiring between the contactor and compressor for a short to ground, or check the compressor windings for short to ground.
With the Tstat off, the contactor should be open so the only way for the compressor to be trying to do anything is if the 110 volts from the unbroken side are traveling through the compressor to ground. Since 110v is not enough to run it, the overload is kicking it out, cooling off, and repeating the cycle. When you kick on the Tstat, the contactor is supplying voltage directly to ground without going through the resistence of the compressor windings and kicking the breaker.
Post back and let me know what you find.
Nov 20, 2007 | Ruud Central System Air Conditioner
Toyotomi TIN/TIG-59AD Air Conditioner Logo
59 people viewed this question
Top Toyotomi Heating & Cooling Experts
hmca
Level 1 Expert
Andrew Taylor
Andrew Taylor
Tom Chichester
Are you a Toyotomi Heating and Cooling Expert? Answer questions, earn points and help others