My Mr slim runs about 5 mins then it shuts off
The on light blinks after it shuts off. I took pressure redings and the suction pressure is 75 psi with a high side pressure of 110 psi. The outside temp is 91*. What do you think the problem is?
22yooper
  • 828 Answers
SOURCE: ac freezes up
Exactly how much refrigerant did you charge into the system when you recharged it? If the suction pressure is varying that much you most likely over charged the system and got a liquid flood back which took out the compressor valves.
Posted on Jul 07, 2008
burzerko
  • 254 Answers
SOURCE: mr slim 12,000 btu 110 volt
Sounds to me like yo have dirty condenser coils (outside unit) After this runs and gets hot it loads the compressor because it can not release heat out of the condenser coil it also may have a restriction somewhere on the high side that could cause this maybe in a txv or in a line filter.
Hope this helps Ya
please rate me
Posted on Jul 20, 2008
t1m130
  • 86 Answers
SOURCE: Mr Slim unit "spits" water/dust mixture
some of those units are equipped with a condensat pump you could have a loose connection or a small crack in the line
Posted on Jul 08, 2009
  • 146 Answers
SOURCE: working on a pu24ek mr
is the distributor inside the condensing unit on this system? it sounds like it is under charged also check the fan operation on the evap along with the filters and evap not dirty. if all is good i would say low on charge. i never had a restriction in a mini split. check the orifice in the condensing unit
Posted on Jun 05, 2010
AcJim
  • 107 Answers
SOURCE: What do we do if
Try to vacum out the condensate outside with a wet dry vac.
Posted on Aug 11, 2010
Reset low tire pressure light
have the new tps sensors been programmed to your taco?? if not they need to be..also please join www.tacomaworld.com
May 25, 2017 | Toyota Tacoma Cars & Trucks
The compressor run for 5 min but the fan still on for mitsubishi slim
the compressor run for 5 min but the fan still on for mitsubishi slim
Oct 04, 2011 | Mitsubishi Mr. Slim MXZ30TN Air...
A/c shut down /how to reseset
Reset the power with a 5 min gap on the outdoor isolator and indoor isolator (if applicable) then return with any fault codes/light flashing sequences which will be the fault coce, if it occurs again :)
Jul 04, 2010 | Mitsubishi Mr. Slim MXZ30TN Air...
Pressure readings
the metering device is in the outside unit on mini splits that is why the liquid line sweats. pressure reading depend on load high load high readings i would shoot for arount a 40f suction saturation temp
Jun 26, 2010 | Mitsubishi Mr. Slim MXZ30TN Air...
Working on a pu24ek mr slim the suction is being pulled down to 5 psi yet the high side coming out at 140 psi on other side of cap tube i cleaned the screen going into evap distibuter possible restricted...
Jun 05, 2010 | Mitsubishi Mr. Slim MXZ30TN Air...
P8 eroor code
P8 error is abnormal pipe temperature indoor. If you are running it on heating P8 error will appear because the disc pressure is too high. It could be overcharged.
May 31, 2009 | Mitsubishi Mr. Slim MXZ30TN Air...
Pressure in both lines fluctuate from 140psi to below 30psi
The foreign made market is different than the USA.
First if the unit doesn't get a change or input from a manual command (on the remote on mine) it will shut off because it assumes there is no one there.
2nd if it is in the timer mode it may be different in orientation than what you are used to looking at.
TO make sure these are not your problem review the instructions.
If this is R22 or R410A there is not a pressure switch that will cut it "OFF" at 140#. And if your fluctuating tween 30 and 140 It is almost sure its low on charge especially if its new. Now I assume you mean 140 on the high side, right?
May 14, 2009 | Mitsubishi Mr. Slim MXZ30TN Air...
Right Indicator light blinks; left is solid; nothing in manual about this pattern
that is an error code.
count how many blinks after a pause and that would be the error code.
could be 4 , 5, 7, or 9.
you could reset it by un plugging or removing power for ten minutes and try it again.
if the problem would re-occur, then there is something wrong with the unit.
as it runs, observe everything and keep me posted. see if the fn outside is running, if the filter is clean, or if the compressor is running, etc.
tnx 4 using fixya,
drcool
Oct 04, 2008 | Mitsubishi Mr. Slim MXZ30TN Air...
Ac freezes up
Jul 07, 2008 | Dometic Rooftop RV Air Conditioner
Mitsubishi MS17TN Air Conditioner Logo
102 people viewed this question
Top Mitsubishi Heating & Cooling Experts
D. E. Hev
MightyMikeJr
Are you a Mitsubishi Heating and Cooling Expert? Answer questions, earn points and help others