I have a ruud centralac unit, i keep burnning up blower motors.im looking for a wireing diagram to fix the problem.diagram of signal wires to unit from thrmostat,also diagram of the internal wireing.can you help me?
  • 28 Answers
What's the model number? You can try going to this site and looking for your manual:
http://ruud.com/productSearch.aspx
Good luck.
Posted on May 27, 2010
WIRING DIAGRAM FOR RUUD URGG-07E37JKR
Just go to the following web address. Hope this helps!
https://www.google.com/search?q=Ruud+model+URGG-07E37JKR+wiring+diagram&rlz=1C1SKPL_enUS
Jan 17, 2015 | Ruud Central System Air Conditioner
Need to change a broken blower motor in RUUD central air unit. Old central air blower motor (GE electric) was connected with brown and orange wire to 15 MHD capacitor. Another orange wire from central air...
on the motor should be a diagram detailing the wires. brown white goes to either side of the capacitor and brown wire to other side of capacitor. hi speed goes to normally open contact on the indoor fan relay and the wire designated common on the motor goes to the other side of power from the relay contacts.
Oct 03, 2012 | Heating & Cooling
Ruud AC unit outside won't start, furnace and blower inside work.
It sounds like your at the point where you need an electrical meter to check out the problem. Make sure you have the proper voltage to the outdoor unit. Could be a bad contactor in the outdoor unit
Mar 01, 2017 | Ruud Heating & Cooling
Ruud achiever 10 inside blower motor burning
Check fan cage to make sure it turns freely. Check voltage to IFM make sure it is correct for the application. Make sure the motor turns the fan cage in the correct direction. IFM will have high and low speed make sure when you change from fan on to auto that the motor changes speed. If you have an amp draw meter check to see when running the motor pulls the amp load it is rated for. Recheck all wiring.
Feb 29, 2012 | Ruud Matching Split Air Conditioner
Transformer keeps blowing on the high side after about 15 Min? Have changed out many transformers and blower motor.
Replace the transformer with a 75va resettable transformer.
Check all wiring for a loose connection at the unit and the disconnect and the breaker panel.
Double check ground wires.
Check the low voltage side for a back feed short from a faulty component.
Could be caused from a bad thermostat wire.
Do a continuity reading on stat wires to look for a short.
Do an amp draw reading on the unit to determine an increase in amperage.
Jul 18, 2011 | Ruud UBHC Air Conditioner
Ruud Silhouette II Gas Furnace, the furnace lights but will only stay on for a few seconds?? What could be the problem??
Bad or dirty flame rod.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jan 09, 2010 | Ruud Heating & Cooling
Ruud furnace Model URKA A030jK08 Code opt 589
Flip the lower panel over and look for a wiring diagram. On that diagram there will be a diagnostic chart. Let me know what 5 blinks represent. Then I want you to read on.
Nov 23, 2009 | Heating & Cooling
Replacing the fan motor on RUUD model # UHBC-21J14SFC
remove control make sure make diagram where motor wires go on board. some models have 2 screws to pull out entire blower assemebly
Feb 18, 2009 | Ruud UBHC Air Conditioner
WIRING
why did the wiring burn?Id have the heat exchanger inspected before rewiring.better to be safe.
Sep 17, 2008 | Intertherm P3RA-048K Air Conditioner
Ruud air handlers
Check the name plate amperage on the air handler. The air handler only has the blower motor as its main current draw. #12 wire is rated for 20 Amp service. If the amp draw by the unit supplied by the disconnect is under 15 amps it should be fine (but) once again check the name plate for ampacity rating.
May 27, 2008 | Ruud UBHC Air Conditioner