Tempstar furnace when the thermostat is fan on the fan from the air compressor turns on not the air circulation fan in the bottom of the furnace
  • mopar440man May 28, 2010
    what are the wire colors to the letters on the thermostat and air handler?
    Mentor:
    An expert who has written 3 tips or uploaded 2 video tips.
  • 195 Answers
Y or yellow and G or green are connected in the "auto" setting, as G is fan and Y is cool, the Y and G wires are somehow, energizing the Y wire that goes to the AC unit to run cool, take thermostat off exposing the thermostats sub base Y and G will be there along with R, red, 24volt ("hot leg" of 24 v power) W white= heat, and C common, 24 volt ("neutral leg" or "common" leg of 24 power) common is where all the various 24 volt circuits (cool, heat, fan,) terminate or return to complete the circuit, just as a AA battery nas a positive and negative side of power, so does the furnace and all electrical circuits, its common as all circuits terminate there , its the opposite side of power fro whish all circuits begin, red is the :hot leg" and enters on RED red to WHITE=HEAT
RED to YELLOW=COOL
RED to GREEN= FAN
auto =Y & G connected
on= R & G connected
if you jump red to green, which is fan on, no connection should exist to yellow in on ! only auto!
Posted on May 29, 2010
Can not get fan on to turn on. All else fine. heat only furnace. No air conditioning...only air circulation.I used to set it on "Cool" and "Fan On"and get air to circulate. Do I need new thermostat?
Since you have two thermostats that operate the heating unit and the fan, and the fact that neither will turn the blower on, I would suspect the furnace/ air handler. Turn the thermostat to heat and see if the heat and the fan comes on, if it does operate normally in heat, the fan relay or the high speed on the blower is most likely the culprit. (If the furnace is equipped with a circuit board, the fan relay is integral to the board, if it an older furnace it has a separate fan relay). If it does not operate normally in the heating mode, verify power to the furnace, see if the flame comes on, if it does: the fan motor, circuit board or the fan relay are most likely the cause. hope this helps!
Jul 20, 2015 | Heating & Cooling
Just installed a used tempstar nulk075dg03 turned on power and the blower fan wont shut off. turn the thermastat asking for heat the blower motor goes off and the glow comes on the fire lights for a c
its wired up wrong somewhere try to bypass the thermostat wires at the unit and confirm the unit works
then youll know more
other than this i would consult the installation guide and user manual first ...!!! get them from the makers site some makers manuals are not on the general google type search but readily available from the makers site
Dec 21, 2014 | Fasco Intercity Heil / Tempstar Furnace...
I have a Heil furnace (Temp star 9000 I believe) model number NUGS075BG03 that is not working properly. The inducer motor runs fine and I can see a blue flame through the sight glass but the circulating...
you need to check to see if blower motor runs in ac mode, if not then the first thing you want to check is the capaciter for that motor. if capaciter is good, motor may be locked up, you can check the amps of the motor by putting an amp clamp around wires going to blower motor, all ratings should be listed on motor
Oct 17, 2013 | Carrier Icp Heil Tempstar Furnace Blower...
Tempstar Air Conditioner wont come on
Sounds like you need a new contactor in the condenser. The low voltage is grounded. Remove the low voltage (likely 2 wires) at the condenser and wire nut the wires leading inside. With an insulated screwdriver manually push in the contactor and be sure both compressor and fan run. Then replace fuse and turn power on to air handler with a call for cooling. Obviously the outdoor unit won't run because you unhooked the low voltage but if fuse doesn't trip then it's likely the contactor. Good Luck
Apr 10, 2017 | Heating & Cooling
Furnace blower runs after temp is reached
Is your tstat fan selector in auto?? Does the fan ever shut off?
Jul 18, 2017 | Heating & Cooling
My indoor fan motor comes on even when the thermastat is off
Is your thermostat perhaps programmed with a circulation option. Many modern thermostats have this option. check your fan options. They may be On,Auto,Circ. If it has a Circ or Circulation option, your indoor fan will still periodically turn on according to ASHRAE standards, even if your stat is turned off. if you poke the fan button you should be able to choose auto and this will solve your problem. Hope this helps.
Dec 17, 2012 | Goodman Manufacturing Goodman GSC130181...
RVP 8000 A/C just experienced slight power surge. Compressor on.
I'm leaning toward sticky relay as well, but if you want to confirm it's not thermostat, remove thermostat from wall, and temporarily disconnect the yellow wire from thermostat (compressor) when/if, it happens again. If compressor stays running, I'd say relay for sure.
Just for future reference , Gray wire from thermostat is low fan, green wire is high fan, yellow is compressor, blue is ground. ( For cooling side) The red is 12 v + to furnace and white is negative to furnace.(heat side)
Jun 10, 2010 | Coleman Mach 15 Air Conditioner
Fan keeps running.
Some programmable thermostats have a circulate feature. This feature will allow your fan to run approx. 20 minutes per hour. This will insure better circulation, a better balanced temperature throughout the home & better air quality do to more air filtration. Read your thermostat manual to see if your thermostat has this feature and how to turn it off if needed. Another possibility would be on an older furnace with a fan limit control. If the temperature settings are set to low on the fan limit (or if the control is malfunctioning) you could experience a fan that runs a lot even if the thermostat is off.