Question about Samsung AQ24 Air Conditioner
Wiring diagram wiring connection from the power source to the outdoor and indoor unit
koolbreezes
  • 540 Answers
SOURCE: new installation
Check the power to the door switch and make sure the door around the fan motor is on tight. and pushed in.
Posted on Sep 06, 2008
SOURCE: ac split unit indoor an ouydoor unit electrical wiring diagram
machine off
Posted on Apr 25, 2009
SOURCE: panasonic cs-pw9gke i need wiring diagram
Split A/C-Cold:
You need four wires(two #10 and two #12) to the outdoor unit, leaving you house, and three wires(#10) coming from the breaker to tye indoor unit inside your house.
Split A/C-Cold and Hot:
You need five wires(two #10 and three #12) to the outdoor unit, leaving your house, and thee wires(#10) coming from the breaker to your indoor unit inside your house.
This ypical arrangment(all of them use three wires fro the breaker), yet there are other units which may require 6-7 wires connected to the the outdoor unit depends on the added features to the unit.
Regards,
Gulftecheng
Posted on May 02, 2009
  • 68 Answers
SOURCE: indoor an outdoor unit wiring diagram
have you tryed to look it up on the net.a lot of the time you can get that sort of info off the web
  • 1250 Answers
SOURCE: Airforce 12000BTU Air Conditioner wiring problem
The outdoor unit should have 2 small wires connected to the contactor coil. This delivers the 24v "Signal" to energize the coil. The wire from the t'stat for cooling are usually yellow, in almost every case. When you put the t'stat in the cooling mode and set the temp lower than the room temp, the indoor and outdoor unit should come on. Check for voltage on the terminal block for 24 volts accross the yellow and common wire. Common could be ground on some handlers. If you have the 24 volts, then check for 24v on the 2 small wires (usually 18 to 22 gage wire) on the contactor coil. If no voltage, trace the 2 wires back to the indoor unit and see where they go. If they are the ones that are not attached, put one on the yellow wire terminal and the other on the common terminal. This will send power to the indoor unit and then piggyback to the outdoor unit. Do not remove the yellow and common from the terminal block. Don't be too concerned about the colors from the outdoor coil wires. Just make sure they are hooked up right. Good Luck and hope this gets it going.
Posted on Jun 07, 2009
A/C Unit SAMSUNG -Outdoor unit model= MH080FXCA 4A was connected to 3 indoor units:
It's possible you have a bad data wire on one of the systems. Swap the data wire or both if two with a different wire. (1&4--2&3) whatever. Whatever you do inside obviously do outside. Might have extra resistamce that is throwing the error but will be fine for a ground wire.Or do one system at a time, being sure to change your dip switch settings until you figure out the problem unit. Good Luck!!
Apr 19, 2017 | Samsung Heating & Cooling
Carrier ckc outdoor unit not starting automatically after installation
It is important that the connections from the outdoor unit is wired to align correctly with the indoor unit where the main control panel is located . The outdoor unit compressor is switched on from the processor here and so it is marked in detail to connect the wires.
Now the if the indoor unit is not powering then there is fault in the main control panel and you need to get help as this is a new unit and warranty should not be compromised.
It is possible that the new unit has a damaged control panel or power and so does not power. take help.
Aug 22, 2011 | Carrier 38CKC042 Air Conditioner
How to solve u4 alarm in daikin inverter 24000btu unit
Sounds like an interconnecting wiring error. Check wiring connection i.e. wires are connected in right order 1 to1 2 to 2 etc. from indoor terminal board to outdoor terminal board. Also check for slack or loose connections.
Feb 08, 2011 | Heating & Cooling
What does error code p8 mean
P8 means Abnormality in outdoor unit.
Check:
1) Wrong wiring of indoor/outdoor
connecting wire
2) Reversed phase
3) Protection device is working
4) Damaged outdoor coil thermistor
Solution:
1) Check the indoor/outdoor connecting wire.
2) Change the connection of electric wiring.
3) Check the protection device.
4) Measure the resistance of the outdoor coil thermistor.
If the resistance is normal, replace the
outdoor controller board
Hope, helpful.
Feb 03, 2011 | Mitsubishi Heating & Cooling
We have a P8? CAN'T FIND MANAUL
P8-Abnormality in outdoor unit.
1.Wrong wiring of indoor/outdoor
connecting wire.......................Check the indoor/outdoor connecting wire.
2) Reversed phase......Change the connection of electric wiring.
3) Protection device is working........ Check the protection device.(LP,HP)
4) Damaged outdoor coil thermistor.....Measure the resistance of the outdoor coil thermistor.If the resistance is normal, replace the outdoor controller board.
5) Check out door coil is cleaned. If not do it.
thanks.
Jan 30, 2011 | Mitsubishi Mr. Slim MXZ30TN Air...
I have an LG split system air conditioner model number LSZ244VN-4 it is coming up with a fault code of CS after it has been running for approx 5 minutes
There is no CS code. Please read as C5.
Fault Code 05 and 53 (CH05 is displayed at indoor unit, 53 is displayed at outdoor unit)
This fault code indicates a communication error between the indoor and outdoor units; this is usually caused
by wiring errors or condensate pumps connected to the inter-connecting cable.
The communication between the units is a fluctuating DC voltage commonly called a serial signal, it can be
easily lost if the wiring is not done correctly. If there is a communication error fault CH05 will appear within 5
mins of powering up the system.
Testing
• Check Outdoor and Indoor Power Supply Voltages ( 230V ±10% ) and correct as necessary.
• Check for any mis-wiring or loose connections and correct as required.
• Check the resistance between communication line and GND. (Normal: Over 2M).
• If one Indoor unit operates normally Outdoor PCB is generally normal.
Turn on the power and start the indoor unit in cooling, set the temperature to 18ºC; the serial communication
signal will only be present for the first 3 mins of operation.
Set your meter to DC Volts, Test between terminals 5 (Red probe) and 2 or Earth (Black probe) of the outdoor
unit, you should see a fluctuating 0-72 Vdc.
If the Voltage is not present disconnect the terminal 5 cable, test the Voltage between this wire (Red probe)
and 2 or Earth (Black probe), you should see a steady voltage in the range of -0.1 to -10.0 Vdc. If No Voltage
is present either the cable or Indoor PCB must be faulty. This can be determined by checking the voltage
output on the Comms terminal of the Indoor unit, with the Comms wire disconnected. If No Voltage is present
the Indoor PCB must be faulty, if present, cable must be at fault.
Jan 19, 2011 | Heating & Cooling
Outdoor unit fan always runs even when indoor unit is off. I have disconnected all control wires from the headunit (at the outdoor end to rule out faulty signalling). The fan runs all the time, with just...
I have had this problem with a Fujitsu unit before. If the power is supplied to the outdoor unit first but unit is meant to have power supplied to indoor unit first, outdoor will only stop when power is cut off! In that case, you will have to run the power cable to the indoor unit first and then connect from appropriate terminal back to outdoor unit. (Often the indoor will stop outdoor unit by just cutting the power to it via use of a relay on the pcb.)
Jan 16, 2010 | Panasonic Heating & Cooling
Air conditioner shuts off
C5
Communication Error
• Wrong or missing wiring between indoor and outdoor unit cable
• Defect of communication components in indoor pcb assembly
• Defect of communication components in outdoor pcb assembly
• Defect of power supply components in outdoor pcb assembly
• No ground connection in air conditioner unit
(affected by noise in power source)
Jun 30, 2009 | LG Heating & Cooling
May 14, 2009 | Heating & Cooling
Heating & Cooling Logo
Top Samsung Heating & Cooling Experts
Nyte_Ryder
gbob59
billconfused
Are you a Samsung Heating and Cooling Expert? Answer questions, earn points and help others