Unit is fully charged but suction line freezes
  • Brian Niten May 14, 2010
    How do you know it's fully charged?
  • 374 Answers
this sympton persist in over charging of freon it is call super charge,exessive charging of freon resulted to freeze your suction line,this is bad for the cycling process.to reduces freon charging purge out exessive freon on low side charging port.make sure service charge pressure gauge valve was installed.to determine the exact operating pressure. have a nice day fix my rate,thanks a lot.
Posted on May 14, 2010
Fridge/freezer not cooling but copper pipe near the compressor freezes up
If freon was needed at all, then your system must have a leak, it is never advised to add freon because of this. If your suction line is freezing up to the compressor shell, you are most likely over charged and the evaporator is flooded/saturated with freon and unable to cool/freeze properly. The freon should be added by weight or volume as noted on the model/serial sticker on the unit only, if the sticker is not present, than an experienced technician will need to charge by temperature/pressure using a set of gauges. Prior to charging, the system needs to be fully evacuated to ensure all non-condensables are removed from the system. Pleazer Appliance...
Apr 17, 2014 | Refrigerators
My goodman unit is freezing up. It is frozen from the line running out of my house than if u look down into unit, the freeze continues inside
Hello, the suction line will freeze either due to low airflow such as dirty air filter, blower wheel, evaporator coil or a weak blower motor. Also, a low refrigerant charge can cause the suction line to freeze up.
Jul 16, 2012 | Goodman Heating & Cooling
All the coils on the unit outside froze up
Hello, if the inside fan was not running then the evaporator coil cannot absorb enough heat to vaporize the refrigerant, and the suction line will freeze including the compressor. Liquid refrigerat instead of vapor passes thru the suction line into the compressor. Lack of airflow or a low refrigerant charge is what will cause the line to freeze. In your case it was no airflow
Jun 14, 2012 | Goodman Heating & Cooling
Ice on suction line
hello, usually the suction line will form ice when there is low airflow due to a dirty filter or plugged eveaporator coil, also if the unit is clean then it is possible that the unit is low on refrigerant charge due to a leak. Inwould also check the thermostat on the unit to make sure it is fuctioning properly, I have seen may units where the thermostat cause the compressor to run continously and cause the suction line to freeze.
Jun 14, 2011 | LG Electronic Window Air Conditioner
We just installed a new Goodman HVAC and the compressor lines freeze up. The technician that installed the unit cannot find the problem
Not to be critical, but not much of a technician if he cannot properly troubleshoot the issue.
Several issues can cause the freezing problems:
1. Refrigerant charge issue.
2. Improper equipment sizing.
3. Air flow issues.
4. Metering device issue.
First is under charge. But before making this determination several other things must be diagnosed and resolved.
Was the unit sized properly using a heat load calculation? You may not know what this means but a reputable, knowledgable contractor does. If the unit was oversized, it can cause the unit to freeze. If the indoor fan & motor were undersized. it may not be moving enough air across the coil and this will cause the coil & suction line to freeze.
Air flow issues, such as obstructions in your ducting or across your evaporator coil will cause the coil to freeze, thusly your suction line will freeze as well. Is the filter and evaporator coil clean? Are there any obstructions in the air passages (duct)? Is the duct work sized properly. Improper sizing of the duct work may choke down the required return air flow, and cause the coil to freeze.
The last issue could be a problem with the metering device. If it is an adjustable thermostatic metering device, was it setup to maintain a 12 degree suction superheat? If it is a fixed metering device, such as a cap tube device or bullet (orifice) device, it mat have a restriction (ususally a piece of solder or flakes from the soldering process clogging up the inlet screen). To easily check this, thaw the system out, start it back up when thawed and look for frosting or ice accumulation at the metering device outlet side. I fit does this rather quickly, then the system must have the refrigerant recovered (or pumped down into the condenser) and the blockage removed.
If it is air related, this must be fixed prior to properly trying to charge a system. Unless the proper airflow has been established, charging the system, or checking charge cannot be properly performed.
Sep 03, 2010 | Goodman Heating & Cooling
When i was fixed a problem in central ac trane i found decreased in freon r22 and the suctione line was freezed, i charged the ac with froen gas r 22 then i found that the suctione line changed and begin...
You are still low on freon. Charging AC by superheat and subcool
First charging a unit by superheat, this is only for Acs with an orifice or capillary tube.
Optimum superheat is 12° to 15° at the compressor or suction line outside the unit.
Hook up your gages and put a thermometer on suction line (large line), start the AC. Measure the temperature of the suction line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant, (you can also use a temperature pressure chart), now read the thermometer, let’s say the suction temperature( the thermometer) is 67° and the saturation temperature (the gages or temp. press. Chart), is 55°, subtract the saturation temperature from the suction temperature, 67°- 55° = 12° superheat.
Charging by Subcooling, this is for Acs with a thermostatic expansion valve, it’s common to see a sight glass on the liquid line (on these units with a sight glass just clear it, when, indoor room is at approximate set point of the thermostat). Optimum sub cooling is 12° to 15° at the outdoor unit.
Hook up your gages and put a thermometer on liquid line (small line), start the AC. Measure the temperature of the liquid line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant,(you can also use a temperature pressure chart), now read the thermometer, let’s say the liquid temperature( the thermometer) is 100° and the saturation temperature (the gages or temp. press. Chart), is 114°, subtract the liquid temperature from the saturation temperature, 114°- 100° = 14° subcool.
Oct 05, 2009 | Heating & Cooling
Samsung side by side mod#rs2454sh The coils inside freeze and ice builds up and in abut 2-3 months there is about 1-2 inches of ice build up.to a point where the frig is not cold enough. I havr to take the...
1. First check if your door rubbers seals properly. if not, try and adjust yor doors so that they seal properly.what happens sometimes is that moisture leaks into your fridge.
2. It is also possible that your unit is overgased. you can buy yourself a valve that can be screwed onto the suction pipe line to your compressor. at the back of your fridge you will find a condenser unit that is directly connected to your compressor. that is called the discharge line and you will notice that the discharge line is thinner than the suction line to your compressor. get yourself a set of fridge gauges that you will connect to your valve that you just connected to your suction line. check your psi reading of your suction line under normal running conditions. to get a compartment temperature of minus 18deg celcius your psi reading depending on gas your fridge is charged with should be more or less 4,5 psi. if you have ice build up at the back of your fridge on your suction line your unit is overgased. if your reading on your guage reads less than zero psi then your unit is undergassed. good luck.
Sep 06, 2009 | Samsung Refrigerators
Freezer has lost its suction & no longer freezing!
Depending on the age of the unit it does take a 134a freon charge or 12 or 22. when fully charged unit should cool properly. need to check door seal for suction issue. the unit does need a good charge to cool. it could also be a restricted sealed system issue.