Evcon furnace, 3 red flashes indicates that the "pressure switch open". Thermal stat is set to automatic and set to heat. It sounds like it is trying to start but then turns off then will sound like it is going to start again, when the thermal stat is turned to "on", cold air will blow with settings set to heat. Have turned off the furnace and turned back on but no luck.
  • 3 Answers
I have 2 of these furnaces in my mobile homes. The booster assembly that has thea clear hose attached to it has a small wheel in it. Remove the 4 screws to this assembly and give the wheel a push. For some reason these tend to hang up after a few years. Freeing this wheel will allow the motor to engage. Simple solution to spending big bucks on unneeded parts :)
Posted on Sep 18, 2012
  • Coleman Master
  • 8,220 Answers
If the hose is blocked to the inducer motor housing, then the pressure wont drop enough to close the pressure switch. Remove the hose and check for holes or restrictions. If it is ok check the blower itself. I have seen the whole blower disentergrated from rust. and I have seen water puddle inside draft inducers from stopped up acoil drain pans. I have a video of how it woks on these particular furances. Knowing how it all goes down gives a better way to look at stuff. The way it works is the fan cons on and causes a suction in the proving /pressure switch, this allows the igniter to glow and when the sensor feels the heat or a timer counts down then the BOOM the gas valve opens and the sensor feels the heat and the gas valve opens giving raw gas to the burner and BOOYA houston we has ignition.
Posted on May 12, 2010
Coleman Evcon furnace blower runs w/ no call for heat. Temp is 5+ degrees above thermostat setting. (Programmable tstat)
When you say door are you referring to the front door or the furnace door? If the unit kicks on AND off by itself I would say it's in the tstat or the tstat wire. If it were internal I would think the blower relay or heat contactor/relay were getting stuck AND THE FAN WOULD NOT TURN OFF until you flipped the breaker. Good luck
Mar 21, 2017 | Coleman Heating & Cooling
Error code= two red flashes, lockout/ no flame
Trane XV80 hard lockout, 2 flashes, Can't be reset - DoItYourself ...
www.doityourself.com > ... > Gas and Oil Home Heating Furnaces
Jan 10, 2013 - The only way I can get diagnostic Red LED light to reset is to switch ... a2 flash with absolutely no operation from the furnace does seem to ..... inducer gets a demand you should get a pressure switch error code 3. ... the flame sensor wire and giving the furnace a heating demand after resetting power twice. Luxaire Furnace Blowing Cold - 8 Red LED Flashes
Mar 1, 2010
Winchester furnace diagnostics
Feb 14, 2010
American Standard Freedom 80 - Cold Air - Getting Error Code 9 ...
Nov 20, 2009
York ignition lockout due to retries
Dec 29, 2008
More results from www.doityourself.com
7 Tips and Tricks to repair your Furnace DIY - YouTube
? 13:25
https://www.youtube.com/watch?v=rAtcvPqUsBA
Dec 18, 2012 - Uploaded by JRESHOW .
cause this fault. 2 RED FLASHES: This indicates that thenormally open pressure ... The furnace will lock out for one hour and then restart. 7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light ... problem. Bothheating and cooling operations will be affected. Check
Jan 23, 2016 | Heating & Cooling
Coleman Evcon Furnace. Why do I keep getting three flash code?
You might try viewing this YouTube video which shows a way to unstick the pressure switch. https://www.youtube.com/watch?v=Wc_oFIL2aRY
Nov 28, 2015 | Heating & Cooling
Indicator blicks 3 times replaced combustion air switch but did not resolve problem. what do i do now?
There should be a diagnostic chart on the furnace door by the wiring schematic. If so see what the code reads for three blinks.
By the term "air combustion switch" I guess you are referring to the pressure switch. Most diagnostics blinking three times is just a dirty flame sensor. If this is the case the burners will light and go out within 4 seconds. If this is the problem carefully remove the flame sensor and clean gently with emery cloth, fine sandpaper or fine steel wool. Reinsert the sensor and enjoy your heat.
Feb 14, 2014 | Coleman 7990-319p Evcon Gas Furnace...
Furnace wont work
Have to know the model and serial of the furnace.
locate code list usually inside or on the back of a door.
Operation sequence= call for heat--inducer blower motor--makes pressure switch--signals board to bring on hsi--after a set time gas valve opens and you have ignition--main blower motor comes on after a set time
Coleman evcon furnace
Sounds like it isn't getting a call for heat. If you have a digital thermostat it could be the problem. I have seen them look like they are working but burn out. A simple way to check is take the stat off the wall. There is 2 wires. It's low voltage so don't worry about shock. Touch and hold them together. If it fires up change the t stat. On a . 2 wire it makes no difference which goes to W or R
Oct 16, 2013 | Heating & Cooling
I have a Coleman/Evcon furnace model #DGU08016UB that has a concern. In my attempt to check my furnace before we need it for the winter; the following condition occurred. Condition: Flashing code of...
jump out pressure switch see if it lights check hose to pressure switch see if they are split or connections are not good ,cut off ends and put back on presure switch.
Sep 21, 2011 | Coleman Heating & Cooling
I have a Coleman Evcon gas (propane) furnace. When the t-stat is switched to heat the furnace heats up but the blower will never turn on. The unit then shuts down and tries to cycle again. I have replaced...
If the unit fires but the main blower fan doesn't come on the the unit is shutting off on a temp high limit switch and it sounds like the problem is the main blower fan motor or control
Jan 18, 2010 | Coleman Heating & Cooling
Heating & Cooling Logo
531 people viewed this question
Top Coleman Heating & Cooling Experts
Bill Long
paulcarew
Dan Webster
Dan Webster
Are you a Coleman Heating and Cooling Expert? Answer questions, earn points and help others