Question about Intertherm P3RA-036K Air Conditioner
I have a T3BA-036KA the outside unit will not
I have a T3BA-036KA the outside unit will not kick on .you can push the contactor in and it will come on .so we replaced it and still doing the same thing.
    Guru:
  • 415 Answers
You need 24 volts going to the coil of the contactor. If you do not have 24 volts, you will need to trace the wiring back to see where you are losing it from. Try placing your voltmeter at C & Y coming from your air handler. If not, go to your air handler and test for 24 volts ac at C & Y coming from your thermostat. If you do not have 24 volts coming from your thermostat, there is either a problem with the thermostat or there is a problem with the wiring between the thermostat and the air handler. If you have 24 volts at the air handler coming from the thermostat but you do not have 24 volts at the outdoor unit coming from the air handler, then you have a problem with the wires between the air handler and the outdoor unit.
I hope you find this information to be very helpful to you moving forward. Please leave a rating. :-)
Posted on May 10, 2010
  • 82 Answers
There are 2 wires that go from the furnace inside to the unit outside. It is this 2 wires that carries the signal to close the contactor. Problems can be.....pump by furnace full and overflow switch tripped, no signal from tstat, 2 wire outside broken or weed wacked, furnace transformer not putting out 24v
Goodman ac unit ckl30-1l outside unit won't kick on
First check the breaker to the outside unit. some are on separate breakers. If you own a volt meter check top and bottom wires of the contactor . If you have voltage on the top and none on bottom, your coil isn't pulling the contactor in. If this is the case, you are not getting 24 volts to the coil. Check the fuse in the furnace case. Hope this helps.
Jul 26, 2014 | Heating & Cooling
My goodman central air unit quit working after a storm. The circuit breaker is not blown. The furnace fan kicks on when ac is turned on at the thermostat but unit outside does not operate. Is there an...
1 posible cause.the thermostat supplies 24 volts to the outside unit to control the contactor if you hear a ligth huming on the outside unit this is the being activated. if this is the case then
check to see if any ants are in or around the unit see video, they will usually climb to dry areas before during or after a storm and for some reason they like the contactor if this is the case cut all power to the unit and clean contactor spray the area around the unit with an insecticide ( not the contactor) replace cover and test unit. Best of Luck. raypena_4.jpg
May 30, 2011 | Goodman Heating & Cooling
Thermostat starts but outside unit will not kick on
Check the disconnect or circuit breaker for the outside unit. Use a voltmeter to make sure you have power on the Line side of the contactor. Set the thermostat to make the air come on check the contactor to make sure it is pulled in. When the contactor is pulled in check the load side of the contactor for power. If the contactor doesn't pull in, go to the thermostat and install a jumper between R and Y to make sure it isn't a thermostat problem. Also make sure you have power to the circuit board. Next you can check the capacitor. If it looks swollen, it's bad. Let me know what you find if this doesn't get it going and I can give you some more suggestions.
Sep 05, 2010 | Heating & Cooling
I have a Dometic A/C unit that is not functioning. The furnace won't fire up as well. Have checked all fuses etc, and installed a new thermostat and controller in the A/C unit last night ... still...
When you say your fan runs do you mean on the furnace or the outside unit? Double ck your themostat wires if you have a volt/ohm meter ck for 24 v at the contactor in the ouside ac unit. On most A/C units you can manually push the contactor in to make it contact be carefull 220v use an screwdriver to do this and push only on the plastic center if the unit kicks on your themostat/wires/or contactor is bad my bets on the wires. good luck
Aug 11, 2010 | Dometic 57915531 Air Conditioner
My outside unit will not kick on but in inside system will
Check the circuit breaker or disconnect for the outside unit. If it's not tripped then set the thermostat to make the a/c come on and see if the contactor in the outside unit is pulled in. If not then check the contactor coil. If it is then turn off the power and check the capacitor.
Jun 19, 2010 | Weather King 10AJA3001AH Air Conditioner
A/c on the inside is working (kicking on) but the outside unit is not doing anything what can be the cause
no power will not let contactor pull in on outside unit - if capicitor is for fan and compressor and bad - neither will come on when contactor pulls in - low freon press. switch or if outside fan tripped unit on high pressure - could be manual reset - thermostat wires bad would not let run signal get to outside unit
Sep 24, 2009 | Heating & Cooling
System fan does not come on.
if the out door unit has been working carefully jump red to green the fan should come on if not problem is bad fan motor or capicitor or fan relay hope this helps
May 24, 2009 | Heating & Cooling
I have a carrier infinity system. On the thermostat it reads "sens error" where the outdoor temp is normally displayed. The inside unit is running but the outside unit is not. Any suggestions?
A burned or pitted contactor will/can cause a unit to not run. Outside fan. Just thinking out loud. Start with low voltage check at t.stat then check outside low volt. Set t.stat to on. If fan engages at least your transformer is good. Next set calling for cool. Drop t.stat 68-70. If nothing happens go outside and with a screwdriver depress the contactor in. If fan and compressor kicks in change the contactor. If contactor is pulled in check outside fan. Remove the wires from the compressor and see if the fan will run . If it does you have eliminated start components as good. The compressor has to be check. It needs to be ohmed out. Turn off power at disconnect. Pull the cover on the compressor. Check between pins; then pins to ground. Open or infinite is good.Have you checked fuses. Like small 3-5 amp fuses
Jul 03, 2008 | Carrier Heating & Cooling
Ruud heat pump outside unit trips circuit breaker
Check your wiring between the contactor and compressor for a short to ground, or check the compressor windings for short to ground.
With the Tstat off, the contactor should be open so the only way for the compressor to be trying to do anything is if the 110 volts from the unbroken side are traveling through the compressor to ground. Since 110v is not enough to run it, the overload is kicking it out, cooling off, and repeating the cycle. When you kick on the Tstat, the contactor is supplying voltage directly to ground without going through the resistence of the compressor windings and kicking the breaker.
Post back and let me know what you find.
Nov 20, 2007 | Ruud Central System Air Conditioner
Intertherm P3RA-036K Air Conditioner Logo
636 people viewed this question
Top Intertherm Heating & Cooling Experts
Donni Steen
Dennis Boxerman
Dan Webster
Dan Webster
Are you an Intertherm Heating and Cooling Expert? Answer questions, earn points and help others