I have a goodman gas furnace with ac. the motor caught fire, replaced the motor,turned the system on, the outside condincing unit comes on, the relay will click but the fan will not run. i checked the pronggs on the circuit board where the motor leads hook to have no power when checked with an ohm meter. help please. thank you Joe
  • laura Newman May 11, 2010
    Have you checked for power at the motor leads using a voltmeter?
    Novelist:
    Champion:
  • 246 Answers
First - you should be very careful when checking for 'power' with a ohm meter. I'm assuming you are pretty mechanical inclined (if you changed the motor yourself), but - just be sure to 'never' put an ohm meter (set on ohms) across power.
That being said - if you (indeed) have no power coming out of the circuit board - I would check and see if you have power 'into' the board - and generally speaking if you have power to the board but not out to your motor leads you are probably safe to assume the board is bad but not in all cases.
NOTE: Since your motor caught fire - I'm not sure I wouldn't have a "Service Tech" take a look at your problem and the entire unit just to make sure 'everything' is ok.
good luck!
Posted on May 07, 2010
AC unit does not kick in, NO hum from motor, blower on furnace comes on, Capacitor looks good, any other ideas? Could I have a bad motor?
There is a relay in the outside unit that is controlled by the furnace. You need to check that voltage is coming to it from the furnace. If it is then you need to change the relay. High voltage is present in the unit. Turn of the breaker before doing this
Jun 08, 2015 | Heating & Cooling
No heat from furnace
If this is the first time unit has been fired up, you likely have air in the lines to purge first. Also make sure the gas supply is on/open. and that if there is a fuse present on the control board (likely a 3 Amp fuse) make sure it has not blown (which can happen simply by close proximity lightning strikes.)
Letting the unit go through the ignition sequence several times will purge the line. If furnace "locks out" on third start attempt, shut it off and start cycling it again until the furnace comes on..
This assumes the installation was checked for leaks initially.
Oct 27, 2012 | Coleman 3.5 Ton 13 SEER Complete Split...
Open rollout or open fuse on Goodman
the fuse is located in the circuit board in the blower compartment and the roll-out is located in the burner section and can be a reset-able switch style or the one time fuse link style which is a a small silver cylinder and is mounted in a ceramic piece and is held in with one screw. Both of these are mounted around the opening of the your burner assembly near the opening. This will be near the area of the gas valve.
Sep 24, 2012 | Goodman Manufacturing Goodman R410A 13...
Burner ignites and goes out (Goodman Gas-fired furnace)
The problem you have is water in the exhaust pipe.
Check to see if the pipe has sagged anywhere or if there is a trap in the line.
If you hear gurgling then it is definetly water....
Some times can be hard to find, even a pipe 1/4 full will cause problems. They are very sensitive to flue problems.
Make sure that the flue pipe either runs back to the furnace or out to the outside, a continuos slope either way witha high spot in the middle.
Also check the bottom drain of the blower if it has one, have had them plug and trap water also..
I hope that this will help you to solve your problem!
Thanks for using Fixya!!
Heatman101
Dec 24, 2009 | Goodman GMS90703BXA Heater
No power to ac indoor fan motor
sounds like you might have a bad control board. try putting a jumper wire on the control board low voltage terminals R and G your fan should come on and run if you have 120v power to fan motor. double check that you do have 120 leaving board and going to motor. if no 120 bad board if you do have 120 bad motor. if it is the board it likely has a bad blower relay which is common in amana models and goodman equipment.
Sep 13, 2009 | Amana Heating & Cooling
I have a goodman furnace and ac unit the fan and heat work but every time i turn the ac on it blows the low voltage fuse ive replaced all low voltage wires to outside unit and thermostat i also replaced...
Look at the contactor on the condensing unit, remove the low voltage wires to the contactor and turn on the system. If the low voltage fuse doesn't blow, replace the contactor.
Jun 24, 2009 | Goodman CLQ36AR49 Air Conditioner
Goodman furnace
double check your wiring. R terminal on the furnace will provide 24 volts to the t-stat. W terminal in the t-stat will send 24 volts back to the furnace W terminal to turn on the heat. G terminal in the t-stat will send power to the G terminal in the furnace when the t-stat is switched to fan on. Y terminal in the t-stat will send power to the Y terminal in the furnace which in turn will send 24 volts to the A/C outside. The C terminal in the furnace should be connected to the c terminal in the A/C outside as well as to the T-stat. Check the fuse again
Jun 02, 2009 | Goodman GMS90703BXA Heater
Problems with Goodman heat pump.
it's powerd by a relay and only comes on ondemand.
Jan 02, 2009 | Goodman GMS90703BXA Heater
Goodman gas furnace power vent motor and housing replacement
You need to type GOODMAN GAS APPLIANCES into you browser to find you local servicecenter. I must tell you that Goodman only sells to authorized service companies in my experience. So you become EgKraft Company.
Nov 07, 2008 | Goodman GMS90703BXA Heater
Turn breaker on to furnace and the exhuast fon comes and ac will not come on
There should be two separate breakers for the cooling system. The furnace breaker you turned on. Now there should be a double breaker in the power panel labeled A/C or Air Conditioner. In addition there should be a disconnect at or near the outside unit. Make sure it is in the on position also. Set the thermostat to cool and the outside unit should start and run.
Jun 01, 2008 | Goodman Heating & Cooling
Heating & Cooling Logo
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen