Question about Intertherm P3RC-042K Air Conditioner
Outside fan motor won't come on. I can depress the contactor and it will run but will not run via the thermostat. Perhaps the control board is bad. Where can I find schematic?
  • 674 Answers
Does the indoor fan come on? At the thermostat take the fan from auto to run. If the indoor fan doesn't come on then the problem could be the transformer. It could also be the coil in the contactor. Both of which are a lot cheaper than a control board. It could also be your thermostat. With the thermostat calling for air check for 24vac on the coil of the contactor. If you have it then the contactor coil is probably bad. If you don't have it I would suspect the transformer or and overload or pressure switch. Check for 24 vac at the transformer. If you have 24 vac there go to the thermostat and place a jumper for R to Y and see if it comes on then. If it does replace the thermostat. Let me know if this helps or if you have more questions.
Posted on May 05, 2010
Intertherm MGHA-070ABFC-05 will not run/cool
Multiple problems. Eliminate thermostat first. Remove face from wall and turn on breaker. If fan still runs you have a bad board or bad relay. If fan outside is running compressor should be too. These operate on same contactor. Verify you are getting 24 volts to coil side of contactor. If odf stops working and contactor remains pulled in you have a bad motor. If odf motor stops working the compressor will shut off due to overheating.
Jun 07, 2016 | Intertherm Heating & Cooling
No cold air
sounds like you need a new contactor but check to make sure you have 24v at the control wiring side of the contactor first. If you don't have 24v check the condenser low voltage wiring and the thermostat wiring.
Jun 02, 2014 | Ruud Central System Air Conditioner
The outside fan in my carrier unit will not stop running when temp inside has been reached?
There can be multiple problems with your situation, one being a stuck condenser fan motor contactor/relay, a shorted motor, bad control board, etc. If you could at least check the contactor that controls the CFM and see if it is pulled in that could help narrow down the search for the answer.
Sep 23, 2011 | Carrier 50TJ028 Rooftop Electric Cool Air...
My air conditioner will not run, the fan will not run in auto or in run mode, the compressor will not start. The thermostat clicks on but the air unit does not. this is a Goodman cplj18-1b unit.
Hello, if the outside unit is not running check tje power supply to make sure you are getting 240 volts, also make sure the contactor coil is receiving 24 volts, if you are not getting 24 volts at the contactor then it may be a bad thermostat, control board or the thermostat wiring is loose or perhaps cut somwhere. If you have 24 volts at the contactor and does not energize than replace the contactor coil.
May 12, 2011 | Goodman Heating & Cooling
My air conditioner won't stop running. The fan won't stop on the upstairs unit unless we remove the thermostat from the wall. The condenser runs constantly. It does cool when the thermostat is plugged...
Does the compressor also run constantly? If it does, the problem with the outside unit may be a stuck contactor. You can remove the cover where the power goes into the outside unit and the contactor should be located near there. If it is stuck, turn off the power to the outside unit and tap the contactor to try to free it, depending on how bad the contacts look, or replace the contactor. As for the indoor fan, you could have a bad fan relay, if that is what your unit has, or a bad fan sequencer, which is what some units use. These components will be located in the air handler. Hope this helps. Let me know what you find if this doesn't help and I can offer more advice based on that.
Sep 08, 2010 | Heating & Cooling
Outside will not come on
First check the circuit breaker or fuses. Remove the cover on the outside unit that covers the contactor, circuit board, and capacitor. Check for voltage on the line side of the contactor. Set the thermostat to make the air come on then check the contactor to see if it is pulled in (contacts closed). If it isn't pulled in then check for 24 vac on the contactor coil. If the contactor is pulled in check for voltage on the load side of the contactor. If you have it there then check the capacitor(s). Some units have 1 that runs the fan and compressor and some units have 2 ( 1 for the fan and 1 for the compressor). If you don't have 24vac at the contactor you can install a jumper at the thermostat between R and G if it is just an air conditioner or R and Y if it is a heat pump and see if the thermostat is bad.
Aug 13, 2010 | Goodman CKL42AR42 Air Conditioner
Fan and compressor on outside unit not working.
If you read 24 volts at the contactor and it does not pull in, the contactor is bad. If you do not read 24 volts at the contactor the problem is with the thermostat, thermostat wire or a defrost board and pressure switches if so equipped.
Aug 09, 2009 | Heating & Cooling
Split straight air system with outside unit comes on and air handler does not whether on auto or on position with temp down or up
Either the thermostat, fan relay on circut board or blower motor bad. Jumper the R and G terminals together on the circut board, depress the door switch and see if the blower runs, if not, check for power to motor, capacitor and motor windings. If it runs then you have tstat/control voltage wiring problem.
Jul 26, 2009 | Goodman Heating & Cooling
Amana 1 ton Residential AC / Outside unit comes on for a sec
open the service panel to check for control voltage of 24volts when tstat calling, The contactor should be pulled in, if contactor is down,and contacts appear to be clean, and the unit is still not running, it is a bad compressor. to test this unplug the black wire from the compressoror at contactor,w/ power off! Turn on power if fan works normally it's a bad compressor. However if you see a swollen split cap(5 wires to a soup can looking w/ the terminal C,F,and Comp), switch it first and start at square one.
You also need to consider the high pressure switch if its cycling on off on off.
Mar 12, 2009 | Heating & Cooling
I have a carrier infinity system. On the thermostat it reads "sens error" where the outdoor temp is normally displayed. The inside unit is running but the outside unit is not. Any suggestions?
A burned or pitted contactor will/can cause a unit to not run. Outside fan. Just thinking out loud. Start with low voltage check at t.stat then check outside low volt. Set t.stat to on. If fan engages at least your transformer is good. Next set calling for cool. Drop t.stat 68-70. If nothing happens go outside and with a screwdriver depress the contactor in. If fan and compressor kicks in change the contactor. If contactor is pulled in check outside fan. Remove the wires from the compressor and see if the fan will run . If it does you have eliminated start components as good. The compressor has to be check. It needs to be ohmed out. Turn off power at disconnect. Pull the cover on the compressor. Check between pins; then pins to ground. Open or infinite is good.Have you checked fuses. Like small 3-5 amp fuses
Jul 03, 2008 | Carrier Heating & Cooling
Intertherm P3RC-042K Air Conditioner Logo
98 people viewed this question
Top Intertherm Heating & Cooling Experts
Donni Steen
Dennis Boxerman
Dan Webster
Dan Webster
Are you an Intertherm Heating and Cooling Expert? Answer questions, earn points and help others