Question about Goodman CLQ36AR49 Air Conditioner
Can not get Goodman 3-ton heat pump out of heat mode and into cooling mode
  • Lisa
    Lisa May 11, 2010
    If this is a new install... disconnect thermostat wiring from the inside unit ...bring thermostat right to the unit and connect it right there... Lets see if its got to do with the house wiring first... we don't know if someone put a picture nail or something thru the thermistat cable
  • 674 Answers
The reversing valve may be stuck. It allows the unit to switch between heating and cooling. You may be able to give it a tap but only on one of the ends, not the sides, and only lightly. You could also unplug the reversing valve from the circuit board. Some reversing valves are energized in heat mode some in A/C mode. When you unplug it, if it shifts, you will hear a loud hiss as the valve shifts and the pressure equalizes.
Posted on May 04, 2010
4 Suggested Answers
SOURCE: have a goodman 3 ton heat pump - ac worked
You are reversing the flow of refrigerant in the heating cycle. Since liquid is now flowing through the suction
line it has less volume than the gas from the cooling
cycle that was flowing through it.. Making sure the outdoor unit is soundproof might eliminate this.
Posted on Feb 14, 2010
  • 189 Answers
SOURCE: extremely long time to get cool air with 5 ton 13
Check your filter. Make sure it is clean. Make sure the outdoor unit is operational. (power on). Clean your condenser coil with a garden hose. If possible check your evaporator coil. If it is dirty clean it. Your furnace (or air handler) blower speed should be set on high. All of your registers (supply & return) should be open and unobstructed. Check for proper thermostat settings. If none of this information solves your problem , then your units charge needs to be checked. You could be over or undercharged with freon.
Good luck......
Posted on May 06, 2009
  • 3 Answers
SOURCE: My 5 ton Goodman Heat Pump won't go into heat or a...
Easy: Turn the "fan" switch to on at the thermostat and see if the blower starts. If no start, check breaker at breaker box. Check service disconnect at or near the air handler. With the breaker and/or service disconnect OFF check the 3 or 5 amp fuse inside the top cover in the air handler.
Not so easy: (You must know what you are doing for this part or let an HVAC Tech do it for you) Open thermostat and firmly jump the Y and R terminals to see if you get the compressor to start for no more than 30 seconds. (don't do it more than once.) Jump the G and R terminals to see if you get the blower to start. If so, u have a bad thermostat. If not, check the transformer inside the same cover in air handler for proper voltage. (24V. Make sure you also get 220 on the opposite side of the transformer)
If the blower comes on, but the heat pump doesnt start, open the side cover of the heat pump, with the thermostat on cool, and the temp. setting as low as possible for at least 10 minutes see if the contactor is pulled in. If so, check the capacitor and see if it's blown out. Be super careful these systems operate with 220v and the amperes are enough to kill you if you make a simple mistake.
Posted on Aug 28, 2010
CPJ18-1B Goodman heat pump. has a slow leak. I need to know what Ton or BTU to replace it with.
you have a 1.5 ton. 12000 btu's per ton. your model number has an 18 in it. tells you 18000 btu's
Apr 13, 2017 | Goodman Heating & Cooling
What is the compressor part number for a Goodman heat pump model PHKJ036
ZR32K5EPFV800 is the OEM part number. I have to ask why you believe the compressor is bad.
Feb 24, 2017 | Goodman Heating & Cooling
Airhandler- the themostat is on auto/I understand cool,heat.emerg heat,The (G) terminal-then why heat mode or,emer heat fan blows?Only when i switch to cool mode the handler still want start up blowing...
the fan fill come on with the sequencer (stack switch you call it) it will also come on with the fan relay. on some goodmans the fan relay is the black box on the circuit board. use a jumper to jump red to green, this should bring the fan on sounds like you could have a broken green wire, try using a different wire instead of green
Sep 12, 2013 | Goodman Heating & Cooling
Where can I find the specs for an earlier Goodman heat pump?
You say 2 to 3 years... I'm assuming the unit is older than that. Especially being r22. What about the first 10 years??? Normally you will get 400 to 500 sqft per ton of cooling, but, that depends on heat load calculations. If the unit wasn't big enough you would have had this issue 10 years ago, not when the system kept running low on refrigerant. At first guess I would say a 2 ton unit is not big enough but if it worked fine for 10 years...wuth all that in mind, if it were me, (a seasoned professional) I would spend 1800 to fix my 15 year old r22 unit before I spent $4000 on a new r410a piece of junk. Best Wishes!!
Jun 29, 2017 | Goodman GMS90703BXA Heater
Goodman heat pump model gph1442h41aa will not turn on
first confirm that the condensing unit outside is getting power or even a command to come on .check function of thermostat your t-stat may command heat in the cooling mode.instead of the heat mode, being a heating system generated by a cooling condensor. also check bateries in t-stat. make sure breker in the panel box is on ,it is a double breaker usualy marked with an amp rating of 20 ,or a 30 on it . also check disconnect switch located next to your outdoor condensor usualy a gray box on wall of building. make sure its on or diconnect tab is pluged in . hope this was helpful. good luck.
Feb 11, 2013 | Goodman GPH1524M41 2 Ton 15 SEER...
Have a goodman 3 ton heat pump - ac worked excellent this summer - however when in the heat pump mode we hear sounds like gravel or rocks inside the big copper line - heat works but what causes the sounds/
Feb 14, 2010 | Heating & Cooling
Do you know how I can get a Goodman Ht pmp Manual
this manual willl not help your system perform better , have a qualified tech check your sub-cooling. temp diff, and match your piston with your coil. many goodman systems may say they are 3 or 4 ton but are half a ton smaller than advertised at the compressor. a three ton system will have a two and a half ton compressor
Oct 01, 2009 | Goodman Heating & Cooling
I would like to know the specifications of my Goodman model CPKE42-18 AC/Heat pump system. BTUs heating and cooling? Thank You,
Many HVAC people talk in tonnage. One ton is equal to 12,000 Btus. Therefore your model specifies your cooling tonnage at 3 and 1\2 tons. Your heating would be determined by how many if any supllimentary heat strips are added. If you live in Anahiem or Miami that's not really important. But if you live anywhere that gets down into the 40's at night you'll want strips. Cooling wise depending on where you live and what your insulation is like, I'd say your unit is good for 1100-1300 Sq feet of living space.
Jul 15, 2009 | Goodman Heating & Cooling
Will not go into defrost
Did you change the thermostat in heat pump? or did you change it when you replaced the board?
Dec 06, 2008 | Goodman CLQ36AR49 Air Conditioner
Goodman CLQ36AR49 Air Conditioner Logo
414 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others