About to weeks ago my outside compessor and fan were not kicking on and the indoon furnace fan was running constantly i figured out were the voltage stoped and i reset the high pressure switch. the copressor kicked on right away. for about four or five days now the inside fan in the furnace runs consantly and the copressor keeps kicking on randomly as well as the copressor fan but it only stays on for 2 to 3 minutes then kicks off my thermostat never kicks off and the temp. inside my home never drops below 75. with some research i have a elimated some things. it's not the defrost cycle there is no heat from vents when it stops. theres one refrigerant line that does frost up quickly but it could be nothing. please help!!
  • 4 more comments
  • gturner5 May 03, 2010
    i just went outside and and trigered the contactor and it is a 1/4 in. or little smaller copper line that runs between the expansion valve and the expansion valve sensing bulb. its warmer today than yesterday outside so it did'nt frost imediatly but got very cold and after i released the contactor it continued to frost up the entire length or the copper line.
    no and no to your questions.
    it frosted right away starting at the expansion vavle extending about 4 inches.
    if you dont mind what is flashing.
    just to be completely clear all i need to have done is to recharge the freon by a qualifyed service tech.
    is this correct or is ther anything that could happen when it is charged that would identify the low freon as a secondary problem and not the primary and only problem
    is there any chance that the refrigerant is leaking inside my house.
    i have recently ben in my basement alot trying to fix my dryer and i figured i would have smelled something.
    this oil your talking about when it leaks is the oil noticable and does it leave a residue that does'nt go away after the oil dry's up?
    THIS WAS VERY HELPFUL FOR A RESONABLE PRICE
    THE INFORMATION WAS DIRECT AND EASY TO UNDERSTAND
    I AM HAPPY WITH MY DIAGNOSIS AND WILL BE A REPEAT COSTUMER
    President:
  • 949 Answers
Sorry you are having trouble, with summer coming on we will need the cooling.
Thank you for the details it helps a lot. I think we can safely eliminate the thermostat, the fuses, the controls from the furnace (air handler) and power to the condenser.
It sounds like we may have a problem with either high pressure or low pressure that is causing the entire condenser to turn off. Since you only had to reset the high pressure the one time I am suspecting our problem is on the low side. That is usually an indication that we are low on refrigerant. Can you tell me which line is the one that freezes up?
Posted on May 03, 2010
  • 3 more comments
  • Philip May 03, 2010
    If we are frosting that close to the thermal expansion valve it would most likely indicate a low charge. Without enough refrigerant in the system we are flashing too soon.
    Do you have refrigerant gauges and are you EPA certified?
    Flashing is where liquid refrigerant (freon) turns to a gas. During this evaporation the maximum cooling takes place, the valve opening should be letting liquid flow down that small tube, but from what you are describing the liquid is 'flashing' or turning into a gas way too soon, meaning there is not enough liquid in the system.
    I hope that makes sense.
    The reason I am asking about gauges and certification is to cover myself. In the US you have to be certified to use refrigerant (freon).
    To check the amount of charge in the system you will need a set of gauges.
    Not sure how much further we can go here without them.
    The signs point to a low charge, this can be easily verified with gauges on the unit.
    If it is low (which I am pretty confident it is), it may not be as simple as recharging or filling it up. To have a low system means the refrigerant has gone somewhere (leaked out).
    If the amount that is gone is small then they will most likely just recharge it and you are good to go without other repairs.
    If the amount that is gone is large they will have to find where it is leaking from and repair that leak then recharge it. If this is the case, it all depends on where the leaks is.
    Yes, it could be leaking anywhere in the system. Refrigerant typically does not have a noticeable odor. The oil that accompanies the refrigerant usually has an odor that you will notice.
    If you have small leak that has leaked while the unit was off it would most likely not be detected by smell. If it were a larger leak that comes out when running you would be more likely to have oil with it.
    Depending on the size of the leak it could leave a small amount of oil. If you find a joint in the tubing and it feels oily that could be an indication that the leak is there.
Trouble shoot Dayton gas furnace model GG9S100C16MP11A fan is left on constant but in cold weather 10 or colder fan will go off and furnace will go thru a restart mode and run fine for awhile then will do...
Do not run contentiously during heat mode. the fan runs at a slower speed with heat and heat fires first then the fan cycles on during heat cycle then when heat satisfies the thermostat the heat will cycle off and fan will run for a couple more minutes and then cycle off. So set stat on fan cycle to auto.
Feb 03, 2015 | Dayton Gas Furnace Heater
Where is the low voltage 24 vac transformer located?
The transformer is located in the furnace. You might want to check to make sure the furnace door is on correctly brcause theres a swich that will open for safety . Also some have a fuse on the solid state board.
May 26, 2014 | Rheem RASL024JEC-RHPNHM2421JC 2 Ton 18.50...
Why does my fan runs continus. and the condenser won't run out side.
The fan runs continously because your condensor is not kicking on and removing the heat. The thermostat needs to come under the set temp. to kick off the fan. If your compressor doesn't run and the fan on the outside unit does run, your compressor has an issue. If nothing runs outside, then your transformer on the inside unit(air handler) has an issue. This could also be a control relay on the condenser or the air handler.
Jan 15, 2010 | Omega Trane Furnace Draft Inducer Blower...
It's cold out, and my Central Air kicks on every time my furnace kicks in. I get heat, but don't think my outside unit (fan) should be kicking in each time my furnace kicks on. Suggestions
Hi, If you have what is called a heat pump, the outdoor unit is supposed to run. It has a reversing valve which reverses the flow of refrigerant and the indoor unit becomes the condenser and the outdoor becomes the evaporator coil. Now, if you don't have a heat pump and the furnace is gas fired, then the control wiring or thermostat is calling for both to come on. Control wiring has to be touching together somewhere and bringing on both. Look over the exposed stat wire outside if you have a dog that may have chewed the wires, I have seen this happen. If all wiring looks good, then the stat is faulty and must be replaced. Make sure you don't have a heat pump first, as the fan, compressor, and all will run on heat and cooling. I hope this will solve you're problem, please let me know, I would like to hear back. Sincerely,
Shastalaker7
Nov 20, 2009 | Heating & Cooling
Outside unit runs continuously, even when system is off.
On A/C units, there is a low voltage line that leads to a contactor, which engages to close the high voltage circuit to the condensor unit. Over time, the accual contacts in the contactor can weld themselves together. Try shutting off your furnace breaker but leaving on the one for the outside condensor unit. If it still runs, your contactor probably needs replaced. Contact a licensed electrician or HVAC contractor and tell them you think your contactor is in need of replacement. Is a fairly simple and quick replace, but the contactor itself is not cheap.
Oct 10, 2009 | Ruud Central System Air Conditioner
Blower will not turn on when a/c compressor comes on - tstat ok fuses ok
You should have a fan relay on your furnace that would control your fan in air conditioning and that sounds like you are needing
May 24, 2009 | Honeywell L4064B2236 Fan/Limit Control...
Fan running constantly in the house
Check t-stat and make sure fan is set to "Auto", that might be why fan is running all the time, or it could be a fan relay that is stuck closed. It sounds like you A/C is over charged or you have a bad high pressure switch, this was a common problem with this manufacture especially in the heat mode.
Apr 24, 2009 | Ruud Central System Air Conditioner
Fan is still running in house constantly
Check your wall thermostat to make sure the "fan" switch is in the "auto" position. If it is set at the "on" position, the indoor fan WILL run continuously. Not really enough info as to what type of split system you have. Gas? Electric? Heat pump? Oil? Wood? Newspapers? See what I mean? Is it variable speed? Do you have a "special" thermostat for certain operations? Does your system incorperate inverter technology?
Goodman Furnace m/n GKS90453BKAC
A constant red light (not blinking) indicates that the thermostat is not calling for heat. Of course you know it is but just to be safe, jump out R and W on the board. If it continues to do the same as you indicated, replace the board.
Dec 05, 2007 | Goodman GMS90703BXA Heater