Replacing Totaline 5 wire programable stat on my std htg/cooling system and can not get the cooling to turn off on new stat. White wire was on old Totalline terminal W1/O/B; what is the new terminal connector label?
  • Honeywell Master
  • 43,501 Answers
Here is a tip that will help you with that...
http://www.fixya.com/support/r3623083-thermostat_wiring_terminal_designations
heatman101
Posted on May 03, 2010
I am replacing a Totaline p274-0200 with a Focus Pro TH6110d. We have a 1H/1C Electric Heat pump with an emergency heat option. Not sure how to wire the Focus Pro.
R=red g=green o/b= orange blue=common y=yellow w=white do you have heat strips? Is u do u have 2 heat 1 cool no u have a 2 get one cool can u send me a picture of the wiring on the old stat
Sep 24, 2015 | Heating & Cooling
I am wanting to wire a Baxi 105E boiler to a Danfoss 102 mechanical timer. The boiler has 5 wires = red, blue, earth, black and yellow. The Timer has six terminals = 1 DHW, 2 HTG, 3 COM, I (earth), 5...
1) Contact baxi:
http://www.baxi.co.uk/contact.htm
2) Which boiler wires? I don't know. Page 24 manual.
Manual says to disconnect link between terminals 1 and 2, and instert timer in-line.
http://www.acwilgar.co.uk/Boiler-Manual-PDF/Baxi/Combi%20instant%2080E%20&%20105E.pdf
2) I can tell you about the timer wiring.
Timer is 230Volts
Not sure if you have British Hot-Neutral 230Volt, or Hot-Hot 230Volt.
Wiring is same 2 wires, but words to describe are different.
Let's say you have Hot-Neutral 230V
Connect Hot to L6
Connect Neutral to N5
This will power the timer so it runs and keeps time.
You can get Hot-Neutral wires from Hot-Neutral that arrive to power the boiler.
Now the timer terminals are separate.
E terminal is Earth or ground.
The Common is Hot wire.
The timer then turns on-off and switches back and forth between DHW and HTG.
HTG is heating
DHW is defrost.
Timer has 2 sets contacts.
When timer activates first set of contacts, then DHW defrost terminal receives power from Hot wire on Com terminal. At this time, all power is cut to HTG heating terminal.
When the defrost cycle ends, then the heating circuit receives power, and then the timer has programming that opens and closes a second set of contacts going to HTG heating terminal.
Which wires from boiler connect to each terminal, I am not sure.
Feb 03, 2013 | Hardware & Accessories
Control fuse keeps blowing on a htg/cooling call
There is a short somwhere in the low voltage circuit. Test the continuity of the remaindimg wires to ground, you should have no resistance, if you do have resistane the wire will have to be replaced. Also, the thermostat can have an internal short which can cause the fuse to blow.
Jan 08, 2013 | Rheem 13PJL30A01-RHLLHM3617JA 2.5 Ton 14...
I am a service technician trying to install a Totaline p474-1050 stat to work for one stage heat gas one stage cool.. I do not have the operating manual just installation... In the installation manual I...
Dear friend, don't worry! I encourage you.
You can download freely from:
www.totaline.com/.../P374-0431ThermostatRemoteControlandReceiverOwner'sManual.pdf -
Plz reply, if you satisfied.
Dec 29, 2010 | Heating & Cooling
Heat comes on when the temperature setting calls for cool.
getting heat in the cooling mode leans toward the reversing valve in the outside unit. it changes the flow of refergerint so that the hot air you get outside in the summer is blown inside in the winter. another possibility is that the reversing valve isn't getting 24v check to see if you have 24v at O and C either at the t-stat, furnace, or the outside unit. if you check at the furnace rember the safty switch for the lower door if that switch is open you will have no power. i would look at the t stat first if you have 24v there go to the outside . 24v present outside will mean a bad valve or board, no 24v means a bad or broken conection in the control wire between the stat and the outside unit(usally the orange wire)
Jul 10, 2010 | Carrier Heating & Cooling
Six wire hook up and new thermostat has only 5
Some thermostats have an extra terminal for an outdoor sensor which tries to anticipate the need for heating or cooling. If this option is not present, you will have an unused terminal which may have a shorting link to a neighboring terminal. Your installation instructions should mention this if the option is or is not included with your model. Also, heat pump systems vary in the system control voltage and not all thermostats and systems are compatible with the more common split system thermostat.
Oct 01, 2009 | Honeywell Electronic Programmable...
No heat new thermostat
you have a short in the wireing.disconnect at air handler and hook-up short t-stat wire to t-stat,ifok chk wire to condenser
Jan 10, 2009 | Heating & Cooling
I have a Ruud thermostat want to change to totaline p274-0200-c
what are the choices on the new t-stat need to know that first
Nov 23, 2008 | Ruud UBHC Air Conditioner
Wiring a Honeywell VisionPRO TH8320U1008 Thermostat
the thermostat will to any temperature but will not shut off
Nov 25, 2007 | Honeywell CT3600 7 Day Electronic...
Heating & Cooling Logo
229 people viewed this question
Top Honeywell Heating & Cooling Experts
Bill Long
paulcarew
Brandon Berry
Brandon Berry
Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others