Question about Haier Energy Star ESA3183 Air Conditioner
Heat pump breaker tripped now no power to the unit at all
    Novelist:
    Champion:
  • 246 Answers
When AC unit trips the breaker it usually means one of four possiblities.
1) the AC unit is causing the breaker to trip, i.e. a shorted fan motor, compressor, or some other electrical component - in which case you will probably need to have a repairman look at it.
2) you've plugged the unit into a outlet that is connected to a breaker which is too small to handle the load the AC unit is putting on it.
3) a defective breaker (not likely but possible)
4) just a 'random' trip and if you reset the breaker it might work fine.
good luck!
Posted on May 04, 2010
Unit runs for hours then power goes away, breaker not tripped
Possibly a backed up drain, possibly loose/melted high voltage wires just not tripping breaker, possibly wrong size breaker
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
May 29, 2017 | Heating & Cooling
Unit trips the beaker as soon as you turn power on
When the breaker trips immediately, you usually have a direct short in the unit. It's best to have a qualified technician check it out.
Mar 23, 2016 | Fujitsu AOU48RLXFZ HFI Multi Zone Ductless...
Any ideas as to why the panel breaker for my Goodman CPE24-1AB heat pump would immediately trip when the air conditioner is turned on?
Without looking up the specifications for this heat pump, I cannot be certain, but I expect the operation to provide cooling may require more power than when heating. You probably can find the specifications online for this unit. As you probably know, power is measured in watts and is calculated by voltage times current. This also is likely to be 240 volts operation. If you take the specified power on cooling and divide by voltage (240), that will indicate the current in amperage that will be required to start it. Your circuit breaker is set for current and needs to be a higher current than is required. If that is the problem, you can buy circuit breakers at Home Depot or Lowes. You have to remove the front panel of your breaker box and snap out the circuit breaker. To be safe it would be good to turn off the main breaker switch before you open the front panel and remove the circuit breaker for the heat pump. Should your calculation of current required be less than the rating of the circuit breaker, that implies a malfunction of the heat pump in the cooling mode and would require a service call to the local representative of the heat pump manufacturer.
May 16, 2014 | Goodman CLQ36AR49 Air Conditioner
Circuit breaker trips when emergency/auxiliary heat shuts off
That is an enigma and it just makes no sense!!!!!!!!Could the switch involved be the culprit? I would check that out just to make sure. Try also checking the breaker by replacing it. Sometimes those things are guilty of crazy operation.
Sep 10, 2017 | GE Heating & Cooling
My kenmore heat pump unit trip the 30 amp breaker when I reset make noise and trip the breaker
Sounds like the compressor has a dead short. Heres how to verify take the cover off the electrical panel on the heat pump. Locate the wires that go to the compressor disconnect them tape the ends and flip the breaker back on if it doesnt trip you know that the compressor is shorted and it needs to be replaced. let me know ok.
Jul 23, 2011 | Kenmore Heating & Cooling
No power to tstat
If you have no power to the cooler control, your breaker has tripped. Check it. Turn it off hard, and back on hard. If it trips again, you have a problem up top, with a motor, pump, that is pulling enough amps to trip breaker. This is all it can be on these units, no power from main breaker to unit control.
Shastalaker7
A/C, & Heating Contractor
Mar 29, 2011 | Mastercool 67471 Evaporative Cooler Air...
Largest circut breaker allowed on a residential heat pump
Sounds like the breaker is doing it's job. Stopping an over amping condition. You need to find out what the breaker is feeding power to. If it is the outdoor unit or the indoor unit. Also, the wire used has to be sized to the breaker otherwise, it will burn inside the walls and start a fire! Both the indoor and outdoor units should have tags or lables stating what the required amount of power is required. Better not let them do anything else untill you get more info. Sounds very dangerous to me but, I'm not there seeing what's going on.
Hope this helps!
Feb 06, 2010 | Ruud UAKA060 Air Conditioner
Breaker trips on condenser unit on heat pump after several hours of operation
Hi, check amps on unit, and make sure breaker matches, check unit voltage tag, it will tell you what size breaker you need, or may be breaker is loosing resistance, replace breaker, if problem continues, a/c maybe over working because of high temp, temp. affect amperages, and that would be normal, if it trips after few hrs. also check a/c for lack of freon, sometimes, they need a tap up of refrigerant, not enough freon and they would run longer, get hotter and eventual trips. breaker doing his job. good luck
Aug 03, 2009 | Amana PTH123B25AJ Heat Pump Air...
My Amana heat pump model PHD60C02F1 Keeps tripping the circuit breaker
Is this kicking the ground fault on the cord or the breaker. If it trips breaker could be bad breaker. If it trips quickly it is a short in the unit. Russ
Aug 01, 2009 | Amana PTH123B25AJ Heat Pump Air...
Heat pump trips circuit breaker
I seem to have the same problem. But when I reset the breakers, they won't stay in the on position. They go back to the off position. What gives? It is 95F inside the house.
Jan 18, 2006 | Haier Energy Star ESA3183 Air Conditioner
Haier Energy Star ESA3183 Air Conditioner Logo
268 people viewed this question
Top Haier Heating & Cooling Experts
Tom Chichester
Matt
Matt
Level 1 Expert
Vincent Schnittert
Vincent Schnittert
Level 1 Expert
Are you a Haier Heating and Cooling Expert? Answer questions, earn points and help others