Question about Winco 200-Amp Automatic Transfer Switch - 4WATS200-31R
Generator keeps running when power returns, can turn off at transfer or with sw in generator, but continues to run on automatic
  • cr8dog Apr 29, 2010
    winco pss8
  • 5,807 Answers
Hi
cr8dog,
Actually the manual and specs only says :
It doesn't have to do in turning off, you may need to do it Manually.
or have additional Circuits ( Magnetic Contactors and circuits ) to
do the things ( cutting and turning off the generator ).
Specify also what make and model the genset you are having
to give you more additional info, should you wish to have it
activated or test it manually.
Although some says it just like a thermostat inside the fridge.
but i don't, till i know the model and circuits involve.
Posted on Apr 29, 2010
  • Rommel Cana
    Rommel Cana Apr 29, 2010
    ATS PANEL WILL NOT CLOSE WITH
    NORMAL POWER APPLIED.
    1.Proper normal line power not available at line
    terminals in ATS panel.
    2.Defective holding coil in line side contactor.
    3.Broken or defective mechanical/electrical inter
    locks.
    4.Defective Start Stop Relay.
    5 Defective Phase Failure Monitor. (Three Phase
    Units only)
    6.Phase Rotation wrong to the Phase Failure
    Monitor.
  • Rommel Cana
    When the incoming (power company) voltage resumes,
    it energizes a timer until the power is stabilized, usually about 5 minutes.
    The timer contacts drop the generator contactor out, dropping the load for about
    a 1/4 of a second and re-energizing the incoming voltage contactor.
    The generator usually stays running up to 10 minutes to cool down and it then
    shuts its self off. The transfer switch is then ready for the next power failure.
    check also if the generator can manually be started and manually be stopped.
Generac generator won't turn off in automatic
It is possibly a transfer switch issue, not the generator control board. Have an electrican kill utility power, let it start and run, then disconnect the sensing wires in the ATS. If it stops problem is ATS
Mar 01, 2015 | Generac Electrical Supplies
Automatic transfer switch not transfering power to home
YOU MAY WANT TO CHECK THE RELAYS THAT ARE IN THE TRANSFER BOX
Dec 15, 2013 | Generac Guardian 200-Amp Automatic...
Generator will not stay running
The toggle switch automatically resets all faults when it is turned to the off position. I would turn the toggle switch off, turn off the breaker on the generator and then turn off all the loads in the house except a few lights. Turn the generator breaker back on, then turn the toggle switch back to automatic. If it starts and stays running, you were overloading the generator. Turn on other loads slowly and keep track of what is on so you don't overload it again. If it still does not stay on, you may have a problem with the panel. Let me know what happens.
Nov 20, 2013 | Briggs & Stratton 15,000 Watt Home Standby...
My gen starts and runs for 1 min or so then dies restarts then dies again and again. if i start it under load ( turn on air con) it will run for 10 min then die allen
Is there a fault?? All UL listed generators including Kohler are required to lockout on a fault on shut down. This really sounds like a problem with your 2-wire auto start connection between your automatic transfer switch and genset. RDT model automatic transfer switch it is the 2 middle wires on the green connector and terminals 3&4 in the generator. close to run and open to shut down. Any open at any time will cause the unit to shut down. The 12 will shut down instantly upon an open because your 5 minute cool down is built into the transfer switch.
Jun 27, 2011 | Kohler 12 kW Emergency Power System -...
What are some the problem if transfer switch dose not transfer when genarator cut in?
If the transfer switch is wired correctly, but for some reason it fails to switch over, even though the generator starts, this will not cause a problem or a safety issue. It will simply mean that no power from the generator goes to the house, and your house will still be connected to the utility company line. The generator will continue to run, but only with enough power to keep itself running at the proper speed. It will have no load on it, which is the same thing that would happen if everything in your house was turned off.
May 20, 2010 | Zenith GE ZTX Series 200A Automatic...
Onan generator emerald III genset. I push the start button and the generator comes on as if it has started, as soon as I let the button go, it shuts down.
Here are the most common reasons for your condition.
CHECK IF ENGINE KEEPS RUNNING The most common complaint is that the engine starts but will not keep running when the START switch is released. This happens because the control board will not allow the engine to continue running if the generator is not producing voltage or if the oil pressure signal is not present. See CONDITIONS REQUIRED TO KEEP RUNNING on the Troubleshooting Chart for your model. If the engine will not keep running, do the following:
A1. Generator AC Output Check the generator AC output voltage as soon as the engine starts. Models showing "B1-B2 Volts" or "L1 AC Volts" under CONDITIONS REQUIRED TO KEEP RUNNING need this AC voltage to keep running. Read between the points shown on the Troubleshooting Chart. If the AC voltage readings are good, proceed to "B" below.
A2. Field Flash If there is no AC, check for 10-12 VDC at the FIELD FLASH pin of the control board during cranking. If the field flash voltage is not present, the control board is defective. If the field flash voltage is present, the wiring or regulator may be defective. To eliminate the wiring, check continuity between the FIELD FLASH pin of the control board and pin 7 of the regulator. If the continuity is good, either the regulator or the field circuit (rotor and brushes) may be the problem.
A3 Field Circuit Check the field circuit by unplugging the regulator and measuring the resistance between pins 9 and 10 of the regulator’s mating plug. This reading should be 22 to 28 ohms. If this reading is too high, check the brushes and/or clean the slip rings (use the Slick Stick, or a similar tool). If this reading is too low, there may be a short in the rotor. Also, check the resistance from pins 9 and 10 to ground. This reading should be very high or infinity. If not, there is likely a ground in the rotor. If these readings are all good, the regulator is likely defective.
A4 External Excitation To confirm that the regulator is defective, turn off the generator’s AC circuit breaker(s), reconnect the regulator and apply 12 volts through a diode to pin 9 of the regulator plug (see illustration) while attempting to start the engine. CAUTION: DO NOT attempt this without the diode. If you do, there will be fireworks! Remove the 12 volts within 1-2 seconds after the engine starts. If the genset now continues to run and produces normal AC voltage, the generator is OK and the regulator is defective. If the genset does not continue to run but produces about 40% of normal AC voltage, again the generator is OK and the regulator is defective. If no AC voltage is produced, the generator may have a problem that is beyond the scope of this guide. Re-check all wiring for security and signs of damage. It may be necessary to take the unit to a qualified repair shop.
B. Check the oil pressure switch as soon as the engine starts. Models showing "LOP to GND" under CONDITIONS REQUIRED TO KEEP RUNNING need the oil pressure switch to be closed to ground when running. If the voltage on the LOL/LOP SW pin of the control does not go to near zero, the switch is not closing. These switches sometimes stick open if the generator has not been used or exercised often enough. Multiple start/stop cycles and/or tapping on the oil pressure switch will sometimes fix it. It may be necessary to temporarily jumper the switch to ground to keep the engine running. This can be done at the switch or at the OIL LOL/LOP SW pin on the control board. Models showing "LOP Open" under CONDITIONS REQUIRED TO KEEP RUNNING have electronic governors and require the low oil pressure switch to be closed at starting but open during running. When the switch opens, the governor module places a ground on the oil pressure input of the control board (P1-5). It is OK to temporarily ground P1-5 on this model to keep the engine running. NOTE: See chart for oil pressure and oil level switch locations.
C. If there is AC voltage present on B1-B2 or L1 AC, as applicable, and the correct oil pressure/level signal is present at the OIL LOL/LOP SW input of the control board, and the engine will not keep running, the control board is defective.
This should help you get it going.
Kelly
Mar 08, 2010 | Watts Onan Portable Generator - 5000 ,...
Series165 Automatic Transfer Switch with faulty controller
You have a faulty component in the controls somewhere. Sometimes you can find it by unhooking things, then try powering up until it stays on. Then you isolate it down by gradually hooking things back up until your problem comes back.
Jun 20, 2009 | RTO ASCO 165 Series 200A Automatic...