Have a split unit a/c, outside unit starts, runs for about 5 mins then shuts off, electrician looked at it and said compressor drawing high amps and it's shutting it down due to overheating? could it be air in system or dirty condenser or evaporator?
    Guru:
  • 415 Answers
It could be. It could also be a problem with the capacitor or a restriction in the refrigerant lines or a low charge due to a leak in the system.
Posted on Apr 28, 2010
The outside unit leds have a 29 code, before it goes into shutdown. Outside is a LAU180HSV Invertor V Split System. Installed in 2012.
That code means that the compressor is drawing too much current when it is trying to start. It is highly unlikely that the main board is bad.
May 04, 2016 | LG Art Cool LA180HSV 18,200 BTU SingZone...
Samsung 2.0TR split ac compressor getting heated up and tripped after running for 10 mins
High limit switch set to high, obstruction in the system, or your compressor may be wearing out.
Apr 12, 2013 | Heating & Cooling
Hi i have a roof top LG LS- k1830 HL 18000/19000btu heat & cool mini split air conditioner. my ? is the condenser fan wont run and the after the unit is on for a while the high pressure line does...
the condenser fan will start as soon as the compressor turns on( that is the outside unit)
the inside fan will run regardless if the compressor is running or not
Jul 15, 2017 | LG LS-K1830HL Heat Cool Mini Split Air...
For the past two days I have had to reset the main circuit breaker for the outside unit. It appears to be running fine now. I'm just wondering is this an indication of the compressor about to go bad,...
Bill, first thing, make sure the outdoor coil isn't stopped up with dirt. This will cause the compressor to overheat and possibly trip the breaker. If you you can check the amp draw that would be good. Look on the data tag on the outside unit and look for RLA or "running load amps". Running amp draw should never exceed this number, it should actually normally run 10% under RLA. If its real hot where you are like it is here (109) it will be running close to RLA.
If you coil is stopped up with dirt, etc., turn off the breakers, use you water hose and sprayer and carefully wash out the coil.
If all this fails, and your amp draw is good, change your breakers. Hope this helps , stay cool.. Mark
Jul 10, 2011 | GE Heating & Cooling
My unit was working fine until 3 days ago when the breaker tripped, I reset the breaker and worked fine for a day then tripped again when it tripped both the ac breaker andthe main in the trailer as well...
High amp draw can be caused by a few different things, so first check that incoming voltage to trailer is sufficient. (115 volts) Not unusual for some parks to install more hydro hook-ups on a feed line, and when all are up and running, your incoming voltage could be decreased. If your o.k. that way, then I'd start looking at the compressor circuit of your ac, in particular, the compressor start-up capacitor. The capacitor basically stores electricity and boosts it to higher voltage for compressor and fan start-ups to reduce current draw that will trip the breaker. Please have a knowledgeable electrician, or RV tech check this for you, as a capacitor can give a real good high voltage (possible fatal) shock, even when power is off to unit. I also suspect that the start relay has shorted (welded) itself due to high amp draw situation, and that is reason it comes on by itself.
Jun 21, 2010 | Dometic Rooftop RV Air Conditioner
It blows cold air for 5 min. and the it blows cool air for 15 min. the room warms up . Why does it stops blowing cold air continuasly???? The thermostat was disconectet on purpose so it coul clow cold air...
See if you can reposition the thermister on the facing of the evaporator coils. That could be it or the thermister might be bad. They don't use copper/mercury sensing bulbs these days. They use these cheap thermisters.
May 22, 2010 | LG Heat cool Window Air Conditioner
Kenmore AC compressor on and off while outside unit fan running
If the out door fan keeps running and the compressor cycles off that would be the overload in the compressor.
What keeps the windings cool is the refrigerant back to the compressor.
For the overload to cycle it would have to be either not enough cooling back to the compressor or high amp draw, which could be the metering device (txv or orifice) or low on charge, or other things would be a bad capacitor, sometimes a bad start relay not staying open, when compressor gets up to speed or anything causing the compressor to draw high amps.
To check the refrigerant, he needs to check the superheat at the compressor it should be appoximately 12° to15°, and next time the compressor goes off if you shut the power off and feel the top of the compressor and if it's hot 130° or higher it's probably refrigerant.
Aug 14, 2009 | Heating & Cooling
I turn on the unit and in about 1 .5 min it trips the cb ,, I put a amp probe on the circuit and found out that after 1.5 the unit jumps up to 40 amps on a 15 amp breacker which the unit is rated for . the...
You are going to have to install a disconnect box next to the unit, with the proper sized fused disconnect inside, and have a new breaker installed at the panel, when the unit comes on, its the compressor that takes the most energy to run, the compressor at start up draws alot of amps, You will need to talk to an Electrician to do your breaker and disconnect work,
Jan 20, 2009 | Fujitsu 18C1 Air Conditioner
Heating & Cooling Logo
227 people viewed this question
Top Mitsubishi Heating & Cooling Experts
vince
D. E. Hev
Stuart Slabber
Level 1 Expert
Are you a Mitsubishi Heating and Cooling Expert? Answer questions, earn points and help others