Carrier Crusader Furnace Won't Light No Gas flow Gas is available Inducer fan starts when heat is demanded Igniter DOES NOT glow Igniter DOES glow during self test All other self test functions work correctly Air Conditioning side works correctly
    Guru:
  • 415 Answers
Check all of the plastic tubing that connects to the pressure switches for any moisture build-up, crimps, or cracks and correct as necessary. :-)
Posted on Apr 26, 2010
  • wamedina Dec 04, 2010
    What was (is) the solution? I have identical unit with exactly the same problem. wamedina@yahoo.com
My York furnace sometimes doesn't completely ignite
A noisy inducer probably is headed for replacement.
The igniter can produce a healthy glow and still be defective. Mine had to be replaced with a new, improved one.
The thermocouple could be defective even though it seems to open the gas valve when it should.
The heat sensor in the bonnet could be defective. That controls main blower operation.
The heat exchanger could be cracked.
Jan 10, 2014 | Heating & Cooling
Carrier Furnace won't start up
Sequence of events: call for heat at T-stat, inducer motor turns on, negative pressure created in heat exchanger closes pressure switch, pressure switch control wire runs through all safety's (these must all be in closed/safe position) if ok then glow plug lights. Time delay then gas valve opens, flame verified by "flame rod" t-stat = :)
Apr 22, 2013 | Heating & Cooling
Carrier 48sx gas pack. Won't turn on. No smell. No igniting sound. Blower fan works. How do I troubleshoot this?
Remove the panel from the heater section, you will need to watch what happends as there is a call for heat. There may be a light on the control board that lights up or blinks to indicate a call for heat. The inducer blower (exhaust blower) will start. INn a few seconds after the blower starts, the igniter will glow orange. After a few more seconds the gas valve should open and the burner will ignite. If the inducer does not run, you may have a bad motor or control board. If the igniter does not glow, you could have a bad pressure switch, bad pressure switch hose or a broken igniter. If the gas valve does not open, you may have a bad control board or bad gas valve. If you get no light on control board, bad fuse, bad thermostat or bad control board.
Jan 03, 2011 | Heating & Cooling
Burners not burning, pilot light is off. How do I start the pilot light?
There is no pilot on this unit. It is electronic ignition.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 29, 2010 | Carrier XHB123D X/Y Series Heat/Cool Air...
I have a carrier 58sx040. Sometimes after the pilot comes on the main flame will start then stop about every 3 seconds. This problem intermittent. There is always a noise coming from the gas inlet when...
Dirty flame rod, polish it with a scrub pad.
Mar 13, 2010 | Carrier Heating & Cooling
No blinks normal running igniter glows gas comes on wont run
Check for 24 volts across the gas valve when Ignitor is glowing. If no, bad board. If yes, bad gas valve or blockage.
Mar 05, 2010 | Goodman GMS90703BXA Heater
Carrier furnace ,burner not staying on after 4th try shuts down completely.cleaned the flame sensor but noticed the 3rd and 4th burner has a delay in lighting by the time the 4th burner lights and hits the...
Remove them and scrub them with a wire brush.
Jan 10, 2010 | Carrier XHB123D X/Y Series Heat/Cool Air...
Having problems with Carrier 58RAV furnace. Goes through the motions, but gas never turns on. I think it is a problem with the LPGS. Please advise. Thanks
Dec 24, 2009 | Carrier Heating & Cooling
Carrier furnace, pilot does not light, fans run for a couple minutes and then flashes code 31
Nov 28, 2009 | Carrier 38CKC042 Air Conditioner
My furnace turns on but does not heat. There are two distinctly different fans that turn on, but then they shut off. After a few minutes it does it again. I think this is because it is not igniting? Can I...
Read this first:
Nov 06, 2009 | Heating & Cooling
Heating & Cooling Logo
381 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen