Intertherm heat pump,just cliks the contactor points @ times
I have replaced the contactor points & capacitor. The unit works well for heat & a/c. But at times the unit just sits & cliks the contactor. I do not know what the issue may be.
The ubit is a : Intertherm for my doublewide home, model #1832036/A...any help is appreciated........JW
    Guru:
  • 415 Answers
Visually inspect all of the line voltage wires and connectors feeding line voltage to your unit. It is possible a disconnect box or a connection in your circuit breaker electrical panel box is overheated/overheating; thereby preventing proper amount of power necessary for your motors to run. Be sure to turn the power off to your main breaker before attempting to open panels for electrical inspection.
I hope this is very helpful to you moving forward. :-)
Posted on Apr 23, 2010
Air conditioner outside fan does not turn off
Is the compressor shutting down and fan is not??? How about the blower, is the coil freezing? Need to check the contactor on the outdoor unit, 240 volts hurts, please use caution. If not confident as to what you are doing call a professional. If need be turn off breaker, you do not want the coil freezing inside!
Aug 19, 2017 | Heating & Cooling
Intertherm MGHA-070ABFC-05 will not run/cool
Multiple problems. Eliminate thermostat first. Remove face from wall and turn on breaker. If fan still runs you have a bad board or bad relay. If fan outside is running compressor should be too. These operate on same contactor. Verify you are getting 24 volts to coil side of contactor. If odf stops working and contactor remains pulled in you have a bad motor. If odf motor stops working the compressor will shut off due to overheating.
Jun 07, 2016 | Intertherm Heating & Cooling
I have a E2EH- 023HB Intertherm electric furnace. The contactors are sparking after furnace is turned on for a few minutes
replace contacters, probably old and pitted (remember points in the distributer on older cars?)
Feb 18, 2015 | Intertherm Heating & Cooling
My york heat and air unit with emergency heat is blowing 30 amp fuses and sparking at the fuses and contactor when turn main breaker back on. I have replaced contactor, transformer and the compacitor on...
You either have something wired wrong or you have a direct short in the system. Are you starting the A/C or the furnace? If it's the A/C, it could be a shorted compressor, capacitor, fan motor or it's wired wrong.
Oct 30, 2013 | Heating & Cooling
Outside AC unit not coming on but indoor fan is working, replaced the start/run 5/50 capacitor but still didnt fix it, let it set allday while came home tried it and it came on and worked great, but the...
Sounds like you are on the right track. The symptom of the contactor not pulling is your clue to the solution. When you turn the thermostat down lower than the room temperature and the thermostat calls for cooling, the outside unit should start immediately. There are a few exceptions to this but generally this is correct. So if you turn the system to cool and the thermostat is calling for cool then the contactor should pull in immediately. If it does not then check for 24 volts to the contactor. If you have 24 volts to the contactor then the contactor is the problem. If you do not have 24 volt power to the contactor coil then you will have to find where the break in voltage to the contactor is happening.
There are many reasons why you may not be getting 24 volts to the contactor, so check what i stated above before you go any further. Repost if this is the solution or you need further assistance.
Important tip....the yellow wire from the thermostat carries the 24 volt power from the thermostat to the contactor.
Sep 08, 2011 | Intertherm P3RA-036K Air Conditioner
MY GOODMAN HEAT PUMP GPH1336H21AE EVAP FAN MOTOR DOES NOT WORK. THE MOTOR HAS BEEN REPLACED AND THE FUSE IS GOOD. I SUSPECT THE CIRCUIT BOARD BUT DON'T KNOW HOW TO TEST IT HELP.
Have you checked the capacitor on the unit. You will need a capacitor meter in or to check it. nI would check it first then the board. You check the board by running the one lead to the fan terminal and the other lead to the common and see if you have voltage. If you do not have voltage then the board is bad.
Mar 06, 2011 | Amana Heating & Cooling
I have an Intertherm S3BA-048KA Split AC system which has stopped blowing cold air. Indoor blower is working fine. Outdoor fan is not working. I have reset breakers (indoor/outdoor) without success. I...
First thing I would look at is to make sure you have power at the disconnect 110 coming
in on each leg to unit. Second, I would look at the capacitor for obvious bulging or leaking
Third I would check to see if the contactor has burnt points or bugs in it. Your disconnect
may have fuses in it which may have failed as well .
(All checks of the unit with power off to all breakers as there will be more than one
double breaker supplying power to the unit).
The hum you hear indicates that the contactor is pulled in on the outside unit but still may
be burnt or have ants or earwigs especially in between the contacts
. The capacitor can hold a charge even after equipment is off so discharge it to the chassis
before removal. Replace only with same Microfarad rating and equal voltage or higher
Remember to mark the wires as to which came off the HERM / C/ FAN terminals or take a
cell phone picture.
I have just replaced my intertherm condensing unit after it had it's 3rd compressor failure.
It was more cost effective than buying a compressor and hoping all the other components
were going to last.
Feb 26, 2011 | Heating & Cooling
I have a evcon eb12b heat pump, it works intermitantly on heat, ihave replaced the contactor, and have 24v at the contactor, come times the heat pump will come on sometimes it wont, The hvac repair guy...
does this unit have a capacitor that is hooked up to the motor, as it may be the capacitor or motor, of course this is just a guess as I am not there to see it. I guess you can push in the contactor a few times and make sure all is coming on like it should, might be the control board. Just a matter of pluck and chuck. Good Luck Tim
Oct 24, 2010 | Heating & Cooling
Heating & Cooling Logo
56 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen