Hi - Where exactly is the IRF630fet - I am also going to try to replace the 2 Capacitors - if I can find them! - You mentioned the 100uf/63v and 2200uf/16v capacitors - Cheers - Terry

Posted by on

  • martinc996 Sep 04, 2013

    Hi, is this the same solution for "DC Bus Fault" on all 9120 units as i have the same fault on a 5000i model. Thanks

  • Vassilis Chamaidis Sep 05, 2013

    Hi martinc996. This solution is for the 700VA model.

×

1 Answer

  • Level 1:

    An expert who has achieved level 1.

    MVP:

    An expert that gotĀ 5 achievements.

    Governor:

    An expert whose answer gotĀ voted for 20 times.

    New Friend:

    An expert that has 1 follower.

  • Contributor
  • 21 Answers

Normally DC BUS FAULT is fixed by replacing C14 and C10. C14 is the 100uf/63V and C10 is 2200uf/16V. They are located between the heat dissipator and the logic board near transformer TX1.

Posted on Mar 12, 2008

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

What cause dc bus fault on 9120 power ware ups?


why don't you check the DC bank capacitors, you may need to replace them

Apr 04, 2015 | Powerware 9120 UPS System

2 Answers

APC SURTD3000XLI UPS error light, 2 battery lights no output


check the fan in the back .... try to replace if damaged

Nov 13, 2013 | APC Smart-UPS RT 3000VA UPS System

1 Answer

APC SURT3000XL UPS


The fault indicator means that there is a fault in the circuitry of the UPS. It could be the control board or another part of the system. (If the batteries were bad, you would see the Replace Battery light illuminate.) If the SURT3000XL is under warranty, contact APC. The standard warranty period is 2 years for repair/replacement. Note: you'll probably have to pay for the shipping of the unit. If the unit is out of warranty, replace it with a new UPS.

I hope this helps.

Cindy Wells

Nov 13, 2013 | APC UPS Battery Backup Systems

3 Answers

Replaced old 12 V, 33 AH batteries for Ferrups 3.1 UPS. Within a min from starting the UPS, those two huge capacitors (situated on the Top Rear, when you remove the Cover, furthest when you see from the...


Mike Decamp is clueless. That is not a answer. The UPS has large DC capacitors. These do go bad over time. The capacitors are required to maintain a good DC Buss and helps in assisting when putting the UPS in bypass and back online. You can not turn on the inverter with out precharging the capacitors. Get the part numbers of the caps and replace. Make sure UPS and batteries are off or you will get shocked.

Jan 27, 2011 | Powerware Ferrups 3.1kVA L5-30P (3) 5-15...

1 Answer

I have a Symmetra LX 16000 , and ups sen me the message ...Critical - UPS A main intelligence module fault exists.. code 0x0203.


Hi Scabcmx,

Without knowing the full model number of your UPS I cannot go into specific details fully for you.. but a good test with any 'intelligence module fault' is to re-seat the module and run a self test. If the fault remains then your intelligence module is bad and you will need to acquire a new one to replace the faulty one. This can all be done 'on-line' and you should not have any downtime... assuming there is a redundant intelligence module in the unit which is normally the case. This will clear the fault.

If you would like more information give me a call: 407.380.9200.

Oct 12, 2010 | APC - UPS - Matix/Symmetra Enterprise UPS...

2 Answers

I had problem with my MGE Galaxy 30KVA. The problem is batt temperature fault and now the UPS status is not protected. I have tried to restart the UPS but the error still shown and cannot be deleted....


I have a temperature fault in my galaxy 3000. Try to clean the radiator behind the cabinet with the air compresor and clean all the fan inside so air circulation is good. Don't know about batt temperature fault. Hope this help.

Sep 15, 2010 | MGE Galaxy 3000 UPS System

1 Answer

Symmetra LX16000,5.93kva; Problem;Alarm indicating power module fault.


Hi Akortic,



Without knowing the full model number of your UPS I cannot go into specific details fully for you.. but a good test with any 'power module fault' is to re-seat the module and run a self test. This only applies if you have an extra/redundant power module to support the load. If the fault remains then you have a bad power module and you will need to replace it as soon as possible. This can all be done 'on-line' and you should not have any downtime... assuming there is a redundant power module in the UPS. This will clear the fault.

If you would like more information give me a call: 407.380.9200.

Nov 13, 2009 | APC - UPS - Matix/Symmetra Enterprise UPS...

1 Answer

DC FEEDBACK FAULT ON CHLORIDE EDP70 30KVA UPS



Sir,

I have edp70 30kva 3:3 out problom is that ups is just given me the 20 to 30 sec backup. and output 2 phase 220v last phase is given just 15v ac. plz send me the tecnicaly solution.And plz reply as soon as my email, henchman11@hotmail.com

Mar 16, 2009 | Exide Chloride Power Station (EXP2000) UPS...

1 Answer

9120 Capacitor & transistor problems


Well all of the above mentioned parts are available in any electronics spare parts store. The capacitors are common which you can easily buy in any electronic store. Good luck!!

Apr 13, 2008 | Powerware 9120 UPS System

10 Answers

Powerware 9120 DC Bus Fault Problem.


there is a 100uf/63v capacitor near the IRF630 fet. You need to replace this in order to fix this error. Along there is also a 2200uf/16v capacitor. It is a good idea to change the both at the same time.

Feb 13, 2007 | Powerware 9120 UPS System

Not finding what you are looking for?
Powerware 9120 UPS System Logo

Related Topics:

506 people viewed this question

Ask a Question

Usually answered in minutes!

Top Powerware UPS Battery Backup Systems Experts

yadayada
yadayada

Level 3 Expert

60683 Answers

Jax Planet
Jax Planet

Level 2 Expert

921 Answers

Clive Gray

Level 3 Expert

1479 Answers

Are you a Powerware UPS Battery Backup System Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...