Bryant gaspac 4 ton
Has led code of 8 flashes ( error in softwear or program) have already checked and cleaned the flame sensor. I can turn off the power and it resets the board but after a change in the weather colder it will happen again
    Scholar:
  • 54 Answers
Let me do some checking I'll get back to you on this ASAP.
Posted on Mar 04, 2008
Furnace Bryant plus 80 keeps failing intermittently to restart. Light indicator flashing code 3 which states pressure switch stuck open. Where is that so I can replace it.
You could also clean the flame sensor .Look for a black sort of box or it may be round should be near the combustion fan.
Dec 14, 2016 | Heating & Cooling
Error code= two red flashes, lockout/ no flame
Trane XV80 hard lockout, 2 flashes, Can't be reset - DoItYourself ...
www.doityourself.com > ... > Gas and Oil Home Heating Furnaces
Jan 10, 2013 - The only way I can get diagnostic Red LED light to reset is to switch ... a2 flash with absolutely no operation from the furnace does seem to ..... inducer gets a demand you should get a pressure switch error code 3. ... the flame sensor wire and giving the furnace a heating demand after resetting power twice. Luxaire Furnace Blowing Cold - 8 Red LED Flashes
Mar 1, 2010
Winchester furnace diagnostics
Feb 14, 2010
American Standard Freedom 80 - Cold Air - Getting Error Code 9 ...
Nov 20, 2009
York ignition lockout due to retries
Dec 29, 2008
More results from www.doityourself.com
7 Tips and Tricks to repair your Furnace DIY - YouTube
? 13:25
https://www.youtube.com/watch?v=rAtcvPqUsBA
Dec 18, 2012 - Uploaded by JRESHOW .
cause this fault. 2 RED FLASHES: This indicates that thenormally open pressure ... The furnace will lock out for one hour and then restart. 7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light ... problem. Bothheating and cooling operations will be affected. Check
Jan 23, 2016 | Heating & Cooling
Amana Air Command 90 furnace LED light blinks 3 times pause 3 times
TRI-COLOR (DSI LED) DIAGNOSTIC TABLE
No. of Red BLINKS
1 Flame sensed when no flame should be present
Verify the gas valve is operating and shutting down properly. Flame in burner assemble should extinguish promptly at the end of the cycle. Check orifices and gas pressure.
2 BLINKS Pressure switch stuck closed/ inducer error
Pressure switch stuck closed. Check switch function, verify inducer is turning off.
3 BLINKS 1st-stage pressure switch stuck open/inducer error
Check pressure switch function and tubing. Verify inducer is turning on the pulling sufficient vacuum to engage switch.
4 BLINKS Open limit switch Verify continuity through rollout switch circuit.
5 BLINKS Open rollout/open fuse detect Verify continuity through rollout switch circuit, check fuse.
6 BLINKS 1st-stage pressure switch cycle lockout If the first stage pressure switch cycles 5 times (open, closed) during one call for heat from the thermostat the control will lockout.Check pressure switch for fluttering, inconsistent closure or poor vacuum pressure.
7 BLINKS External lockout (retries exceeded) Failure to sense flame is often caused by carbon deposits on the
flame sensor, a disconnected or shorted flame sensor lead or a
poorly grounded furnace. Carbon deposits can be cleaned with
emery cloth. Verify sensor is not contacting the burner and is locatedin a good position to sense flame. Check sensor lead for shortingand verify furnace is grounded properly.
8 BLINKS External lockout (ignition recycles
exceeded where flame is established and then lost)Check items for exceeded retries listed above and verify valve is not dropping out allowing flame to be established and then lost.
9 BLINKS Grounding or Reversed polarity Verify the control and furnace are properly grounded. Check and reverse polarity (primary) if incorrect.
10 BLINKS Module gas valve contacts energized
with no call for heat Verify valve is not receiving voltage from a short. If a valve wiring is correct and condition persists, replace module.
11 BLINKS Limit switch open - possible blower
failure overheating limit Possible blower failure, restricted air flow through appliance or duct work. Verify continuity through limit switch circuit and correct overheating cause.
12 BLINKS Module Ignitor contact failure Fault code indicates the module ignitor contacts are not functioning
properly. Replace module.Solid Module - internal fault condition Module contacts for gas valve not operating or processor fault.
Reset control. if condition persists replace module.
3 double 2nd-stage Pressure Switch Stuck Open/Inducer Error
Check pressure switch function and tubing. Verify inducer.
Nov 11, 2013 | Patton Electric Patton PUH680-U Electric...
I have a Bryant furnace that is firing up then shutting right off.. The led is blinking green twice then yellow 4 times? What does this mean?
Hello, Make sure the flame sensor is clean near the burners, The flame sensor is a metal rod that is on the opposite side of the ignitor. To clean the flame sensor you will need some steel wool, turn off power to the furnace and remove the flame sensor and clean it with the steel wool. After cleaning reinstall it and turn power back on to furnace.
Feb 19, 2011 | Heating & Cooling
I have a newer tappan heater and get 4 blinks on led for error code the unit starts up fine and has flame but flame goes off when blower kicks on
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Heating & Cooling
What are the carrier 8000ts led error codes?
They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST
DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS
11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiating
status code recall. After one status code recall is completed component test will occur.
Thanks for Choosing FixYa.
Kelly
Oct 05, 2010 | Heating & Cooling
Meaning of rudd furnace trouble codes
Error Codes
A green LED indicates system faults
Steady On: System OK
Steady OFF: Board control fault or no power applied
1 Flash: Ignition failure (control in one-hour lockout)
2 Flashes: Pressure switch fault, fails open (switch is
stuck open)
3 Flashes: Limit switch open (main or auxiliary)
4 Flashes: Pressure switch fault, fails closed (switch is
stuck closed)
A yellow LED indicates flame status
Steady on: Normal flame is sensed
Flashes: As flame weakens, frequency of LED flashes
increases
Dec 12, 2009 | Heating & Cooling
I get a 5 flash on the led code light
I forget what that code is...theres a sticker in the blower compartment or in your manual will tell you what 5 blinks means....typically its a flame signal error code....The flame sensor should be cleaned annually anyway to eliminate this problem...4 inches long and resembles a straight coathanger....clean/shine it up with emery cloth
Oct 24, 2009 | Goodman GDS80904BNA Open Flame Heater
Why Wont My Bryant Furnace Stay Running
Look on the blower door panel in the wiring diagram there should be a flash code but it sounds like the flame sensor is not picking up the flame and you may be able to clean it
Oct 28, 2008 | Heating & Cooling
Heating & Cooling Logo
66 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen