Question about Goodman GMS90703BXA Heater
Hi, I have a weatherking gas furnace (model # wgdj-10eamec)that the blower wont come on. It lites and fires but no fan blower. I took the blower out and put power to it and it worked (nice and smooth), so i put it back and still no blower.
  • Goodman Master
  • 2,461 Answers
Hi check out the fan control afc could be dusty or not coming on at temp rise you can adjust the temp rise and fall see if this helps
Posted on Feb 08, 2010
04 goodman furnace model GMS8 ciculator blower wont stay on gas fires and runs but high limit trip because of no air from blower any ideas bad motor or control module
You need to check the motor amp draw against the spec tag on the motor. If the motor has power to the motor wires it's either the motor or the run capacitor.
Nov 17, 2014 | Heating & Cooling
Furnace blower won't turn on
You may need to replace the sail switch. It senses the fan speed and when it connects the gas valve should open and furnace should fire up.
Dec 09, 2013 | SUBURBAN MANUFACTURING Rv Motorhome...
Weatherking GAS furnace
Check the run capacitor.
Dec 07, 2013 | Heating & Cooling
I have a weatherking gas furnace that will not blow
Sounds like a bad blower relay. Check the voltage from the board or relay going to the blower for 110 volts. Replace the relay or board if no voltage.
Feb 07, 2010 | Heating & Cooling
Heil 75kbtu gas furnace 80% efficiency installed winter 2004-2005 timeframe. the exhaust fan comes on and the green lite on the valve flashes green but the unit wont fire. a service tech asked if the pilot...
if it has a pilot, you can follow the pilot tube from the gas valve back to the burner assembly and find it. It may not have one and if this is the case, the air flow switch is supposed to close when the inducer fan comes on . If the flue is clogged, condensation in the bottom of inducer fan(would hear cracking). then after the draft safety switch is closed,the gas vavle will get 24 volts and allow the gas valve to open
Oct 27, 2009 | Cross Furnace Draft Inducer Blower 115...
WeatherKing Acclaim II
  1. The sensor that tells the furnace whether the gas is lit has got build-up on it and is giving the furnace bad information.
  2. The flame sensor is often a single wire or rod that sticks up in the center of the flame.
  3. You can shut off the furnace and the gas and clean the sensor with some sandpaper.
If that still doesn't work, the sensor may need to be replaced.
Please rate this solution.
Jan 16, 2009 | Heating & Cooling
Finding the cooling contactor on weatherking acclaim II gas furna
the "y" terminal sends the hot leg of the 24 volts and the "c" terminal sends the common leg to the condenser..
Nov 15, 2008 | Weather King Heating & Cooling
Weatherking control board
the fan comes on only after the burner fires. so no stat voltage is expected. it is not powering the blower, the elec board is. only after burner lights will fan be energized due to heat build up. usually on older weatherking there is a heat sensor on the bulhead above the burners. it is stuck sounds like to me. try a sharp rap on the right side about four feet up the side and a foot back . if fan stops you know the switch was stuck . probably needs a new fan switch.
Oct 20, 2008 | Heating & Cooling
Goodman GMS90703BXA Heater Logo
141 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others