What is the surge protection in modems. whether
What is the surge protection in modems. whethe (a) between phase and neutral only/ Or (b) bet. ph-neu, ph.-earth and earth- neutral. Pl e-mail model No and type of surge protection.(a) / (b)
  • 429 Answers
3 wire 120 all three are protected
Phone cord only uses two wire, both are protected.
Surge is only high voltage/amp
Posted on Feb 07, 2010
When i turn on the drive it display it display code for ground fault. my wiring are correct. And i cannot use keypad of drive. how can i resolve the fault .
why cant you use the keypad/'display of drive, is it not lit up ? if so you most likely have a grounded phase on the load side (motor) I suggest disconnecting motor completely and measuring to ground with a high voltage tester (megger) if you have a phase to ground then all the power that drive puts on that wire will shunt to ground , causing infinite current , this will affect the power supply of drive and not allow drive to even power up correctly
also you failed to mention if motor was 3 phase if so , some drives require installer to remove shunt jumpers (see install directions) this will "Lift" the surge suppresors off earth ground and over to "virtual" ground that occurs at center of three phase power , this might be seen as a ground fault if this is not done correctly
Jun 12, 2015 | Delta Vfd750b43a Ac Drive Vfd B Inverter...
What's the difference between a surge and a spike in voltage?
A spike is an increase in voltage for 1-2 nanoseconds.
A surge is the increase lasts 3+ nanoseconds.
Feb 05, 2014 | Electronics - Others
Tripping off of the Input protection
Need more info. What are the measurements on the input to the UPS. What is the total load you have? What other alarms are displaying? Check the input power to UPS. Also make sure the UPS is and will work for the correct voltage (Input of UPS) some UPS's are selectable voltages.
Jan 20, 2014 | Eaton Powerware Pulsar M 3000 3000VA...
Surge protection
Yes, the surge protection works on both the switched and unswitched outlets
May 20, 2013 | Computers & Internet
No power
something is loose or power not correct. ck polarity at outlet. narrow pin is hot wide is neutral and round center is gnd. 120v hot to neu and gnd 0v neu to gnd
Sep 17, 2012 | Whirlpool Washing Machines
QO115GFI breaker trips when I switch on the breaker next to it.
I happen to have one of these in the box, so I've reviewed the installation & on-line literature for this model. Let's address installation notes:
Don't connect more than 250 ft of load conductor for the total one-way run, to prevent nuisance tripping.
The breaker is to be used on grounded power supply circuits only. We're talking a properly-grounded breaker box, not just the protected circuit.
Look at the side of the breaker. You will notice that the curly white wire is meant to be connected to the (properly grounded) neutral bar in your panel.
The circuit neutral that you're protecting should be landed on the terminal just above that curly wire. Make sure you have the right neutral!
The circuit's hot wire would of course be landed on the topmost screw.
You did not state what you mean by "the breaker next to it": just above, just below, or directly across from the GFI breaker?
I suspect that you meant just above or below the GFI breaker. And I assume you've swapped out other breakers to rule out a defective breaker.
Now, it is possible that you have a "shared neutral" situation. It's a common wiring practice to use one neutral wire for two "hots", where one circuit is fed from the phase A side and the other is fed from the phase B side, (which you'll have in a two-pole, 220V breaker), picking up a 110 volts from each phase. The two 110v "Hots" share a single neutral wire between them to carry return current. The phase shift between the two phases allows this.
However, to avoid nuisance tripping of your GFI, your protected circuit cannot share neutrals with another circuit, as the "other" circuit's operation will cause the 6 milliamp differential between current out (hot) and current return (neutral) which the GFI by design senses and trips.
Your GFI-protected circuit probably needs its own dedicated neutral!
I'd like to hear what you find. Good luck!
Feb 24, 2012 | Square D QO115GFI QO Circuit Breaker
This thing doesn't work. When moving the remote unit downstairs, it doesn't connect to the network.
The powerline modems are affected by the other connected equipment in your house and the wiring phases.
For BOTH modems try the following first:
-Connect the modems directly to the wall socket, don't use an extension lead.
-If you have a surge protecting extension block plugged in in the next/adjacent socket, try plugging it in on a different mains socket.
If this does not work, you may want to think again about routing an Ethernet cable between floors.
Higher performance and lower cost.
Feb 13, 2011 | Zyxel PLA407 HomePlug AV 200 Mbps...
I installed a 3 ph 208v Square D starter with 2- 120v relays wired from the incomming power, in series, for phase loss protection. I took a neutral to the mag coil and and a wire from the relay contact to...
1. Why not buy a phase loss monitor that monitors all 3 legs. 208v 3ph is 115-120V to neutral. If you're using two 120V relays you'd only be monitoring 2 legs of the 3 phase. Using relays can be risky, as sometimes when you loose one phase you'll still pick up voltage through your load. If your set on using relays use 2-208V relays. Connect one to phase A+B and the other to B+A and then wire two of the normally open contacts in series and put that in your circuit with your pressure switch. I'f you're using 208V for control voltage, then you need to take L2 to the oveloads and then to the coil. L1 would go to your pressure switch, and the return from the pressure switch would go to the other side of your coil. You could add your phase loss protection here.
Apr 10, 2010 | Square D Ehb24020pl 20 A Ehb4 Ehb Circuit...
Electrical connection of hobart h600
it requires 3 phase with ground it is a four wire system
Jul 24, 2009 | Hobart H600 Stand Mixer
Understanding Outlet Circuit Test Results
open ground=ground wire (green) is not connected to the circuit box ground or to the earth ground.
(there should have steel rod place in the ground by the local electric company, and gtound wire is connected to that rod).
Open Neutral= same as open ground. unless you are testing 240V, which have 2 hot (110v) and a neutral (0V).
Open Hot= open 110v line (black)
hot/ground reversed= if you understand the above, then this sould be self explaintory.
same a hot/neu. reverse.
if you don't understand how electric wiring works, My suggestion is to stay out.
Dec 27, 2008 | IDEAL MCM TESTER GFI CIRCUIT