My heater fired up ran like normal then the burner shut off and the fans stayed running it is flashing code #4 hi temp over limit swith how do i reset ???
  • 456 Answers
If the unit is like the one pictured then you have to switches that may have to be reset. One is located
near the burners and the other probably in same
compartment.
These switches are a bimetal disc held in by two screws and usually will have to wires going to it. in
between where the two wires clip on is a button usually red, Make sure you push it in.
If the furnace is different than the on pictured give more detail
Posted on Feb 06, 2010
Gas furnace short cycles 2 minutes or less. Multiple troubleshoot steps and replaced components - no help. Any advice?
I did not see that your indoor fan motor started. Near your indoor fan motor there is a temperature switch that is called the fan delay relay. On a temperature rise the relay shuts a contact that turns on the indoor fan motor. If the contact does not close the high temperature limit will shut the gas controls off like your getting. A fan delay relay also allows the fan to run a minute or so to carry away the remaining heat in the furnace and help cool the furnace down. The fan delay relay is normally mounted in a recessed area in the fire wall of the furnace plate. I have also seen them on the top of the furnace heat exchanger. Anyway, the fan delay relay will probably not be available on a sunday, so temporarily until parts are available, try turning the thermostat fan from auto to on and try the furnace again. By turning on the fan to on the high temp limit will not shut you down again.
I have had high temp limit change there trip points, but you said you bypassed it and did the same thing.
Another cause could be using the wrong type of air filter. The new pleated filters sold block to much air flow. If air mass flow rate drops the difference in temperatur go up and when the difference in temperature go up, it gets nearer the high limit and causes it to trip. All pleated filters drop normal air flow through ducts by at least 35%. To make your air duct system work properly use the what is called throw away filters which cost about 1/3 the cost of the pleated filter. Remember to either clean or change the throw away filter monthly to reduce dirt being drawn into your duct system.
Hope this helps.
Feb 13, 2015 | Heating & Cooling
Have a gmp125-4 furance blower runs all the time checked themostat wires error code 1 blink then 2 then 3 then 5 furance works if you turn power off turn back on when heat kickes off blower comes on gives...
Sounds like limit switch issue. Furnace heats up, high temp limit switch opens, fan will stay on. GMP model is older and do not have the codes.
May be over fired, have airflow problem, to cause the limit to open.
Next time before shutting off power, try to find the limit, it has two wires that connect to a 1.5 x 2 inch card mount to the furnace fire wall. tap on it and see if the blower stops. If so replace the limit.
Sep 06, 2011 | Goodman Heating & Cooling
My goodman furnacs says my limit switch is bad blower works but does not ignite .....? its modle gmt070-3 and where is it located
There are several limit switches in the unit there in various places in burner compartment. One on blower housing . One thing that I would try is replaceing your filter and turn the power off to the furnace and try starting the system after power is D/C for 5 minutes.
May 02, 2011 | Goodman GMS90703BXA Heater
My Ruud furnace used to regulate 1 deg +\- the set temp. Now it regulates right at the set temp and the fan cuts off while the burner continues to fire for a minute or so then the fan kicks back on for...
It appears to be the fan limiter switch. It comes on at a certain temp when heating up and shuts off on the high end of its setting. Once the burners are shut down, the fan continues for a few minutes to cool down the burners. The limiter switch is adjustable but it sounds to me to be defective and should be replaced. Good luck and stay warm, :-)
Mar 15, 2011 | Ruud Heating & Cooling
Furnace fires up and heats to desired heat setting and burner shuts down , but the main blower continues to run on.
its the fan control AFC not shutting off , it comes on at temp rise say 150f drops back to 130f with fan on , burner shuts off fan runs untill temp falls to 100f the fan shuts off in this case it keeps running
Nov 13, 2010 | Dayton Gas Furnace Heater
My coleman 7900 furnace blower cycles on and off while burner continues to operate
I would look at fan limit switch. They are normally located in electrical cotrol compartment. If your are lucky you will have one thats adjustable. It would helpful if I knew is your home a mobile or modular home as they usually use a button type limit on fan and hi limit. It sounds to me like you may be having problems with fan limit which controls temp. that fan comes on . Often what happens is that switch scenses temp to turn on and then draws cold enough air on return air to shut back down until temp.rises again.If this occurs when unit first comes on or continues after burner shuts off you can get a limit switch with a higher temperature rating or one that has adjustable temperature range. Hope this helps you.Thanks.
Nov 06, 2010 | Coleman Heating & Cooling
Goodman GS9 propane furnace inducer motor runs continuously
it sounds like the low temp limit switch, the one that cools the furnace down with the burner off and the thermostat open, when it cools to a point the fan stops, the other switch in burner area turns burner off/on, hope this helps
Jan 31, 2010 | Goodman GMS90703BXA Heater
Burner lights but limit switch will not turn fan on automatically. the burner will shut down if i don't run fan manually. is it the limit switch?
Hi, Yes, you have the answer to you're problem. Now, I don't no if you have just a high limit, or a combination Limit control? I will go with the combination fan control as when they go bad, they stick in the closed position and they have normally open contacts. When the heat exchanger starts to heat on a call for heat, there is a dial on the fan control with temp. settings on it , and it will start to rotate as the heat gets higher. When it reaches its set fan on temp, it with start the fan.We no the fan works so the blower is good, so it shuts the burners down on you're high limit temp. which is factory set to about 250*F. When you turn The t-stat from auto to on in the fan side, that solves the problem temp, only. You will need to R & R the Fan control. If you need some direction on doing this please let me know and if it is a Honeywell auto/on type that is rectangular in looks, and if you remove the cover you will see the temp. dial with arrows on it. Thank you.
Best of Luck, and Sincerely,
Shastalaker7
Nov 21, 2009 | Dayton Electric Heater
I have a H1001D pool heater that will not continue to stay hot. with heater turned on hi, fan comes on 20 sec.later temp. at vent is hot from the burning gas ,10 sec.later temp. is cool. fan continues...
One of the internal safeties are opening causing the main burner to shut down. Ensure you have proper water flow through the unit. It may be a high limit tripping and can be caused by several things, one being the limit is weak, second the heat exchanger may be partially plugged from scale. You may be able to determine the cause if your mechanically inclined, but I would recommend professional service.
Aug 03, 2009 | Hayward H Series
A 1979 Colman RV furnace. Blower shuts off shortly after burner shuts off leaving a hot heat exchanger. After 15 seconds blower comes on again blows for 10 seconds shuts off comes on in 15 seconds blows...
The fan limiting switch is acting up. It should stay running until lower temp is reached. It will cycle until the temp stays below or at the low setting. Limit switches are adjustable.
Jun 09, 2009 | Coleman Propane Forced Air Heater...
Open Questions:
See all Mr. Heater Natural Gas Garage Heater - 45,000 BTU Questions
Mr. Heater Natural Gas Garage Heater - 45,000 BTU Logo
231 people viewed this question
Top Mr. Heater Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Mack Baxter
Are you a Mr. Heater Heating and Cooling Expert? Answer questions, earn points and help others