My Dayton Gas Unit heater will not stay on. The
My Dayton Gas Unit heater will not stay on. The Blocked Vent (spill)shut off switch keeps triping. I have replaced the motor to make sure that I have adequate air flow through the manifold. The first one hummed quite loud like it was under a load. There is no blackage external to the unit. I have also swapped this switch with the exact same unit and the issue stays with this heater. Voltage to the unit is 123 Volts AC. So no voltage drop going on with the fan motor.
  • 407 Answers
Have you tried the flue vent? If not, an easy way to check this would be to take the vent pipe off of the unit and see if it continues to have the problem. In most cases, this happens when you have blocked return air or dirty filters, flue blocked, or induction is blocked from switch or housing. One other possibility would be a dirty/clogged a coil which isn't allowing sufficient air to push out causing the limit to trip. I hope this helps somewhat.
Posted on Feb 07, 2010
30000BTU wall heater keeps shutting off LP gas supply.Pilot stays on,when I turn up the thermostat gas comes on, after a short time, gas supply & pilot shut off with a sharp loud noise
It sounds like either the high limit or the spill switch is bad. These are snap disc thermo safety devices. Locate and jump out, one at a time. If unit works when you jump out the limit, replace it. The same goes for the spill switch.
Feb 18, 2017 | Water Heaters
Preasure switch cycle lockout
Hello, If the pressure switch is open it must checked for a restriction in the flue pipe or blockage in the vent, the tubing going from the inducer motor to pressure could be loose, blocked or have water in it, or the switch it self is going bad.
Feb 26, 2011 | Dayton Gas Furnace Heater
Installed new heater it ran for 15 minutes and the gas cut off. The combustion fan and the fan keeps running, the only way to stop them from running is to throw the breaker. LED light blinks 4 times, book...
the high limit is an over heat switch that could mean the unit is over fired. you would need to time input or check manifold pressure. the roll out switch is a switch that shuts the unit off if combustion is spilling at the divitor on the unit where the vent connects. with this you need to check your venting
Jan 05, 2011 | Mr. Heater MHU75NG
My dayton NG heater fan will not shut off properly
Sounds like a bad fan switch. The switch is located on the heat exchanger and is 110 volt bi-metal switch. Follow the wires from the blower going back to the heatexchanger. Graingers can get you a new switch if you give them your model number. www.grainger.com.
Dec 12, 2009 | Dayton Heating & Cooling
Wall furnace shuts off after about 10-20 mins
sounds like its not venting properly...it likely is shutting off on a "Spill switch" or "Vent safety switch"....check the vent/chimney first off.....also the pilot could be dirty..,..a lazy pilot tends to blow out easily....pilot should be blue and sharp,,,big enough to fully envelope the thermocouple
Oct 30, 2009 | Heating & Cooling
Cozy wall heater working intemittently
Sounds like a limit switch is tripping.
This appliance is equipped with a manual reset blocked
flue switch designed to protect against a blocked flue condition,
which would cause combustion products to spill back into the
living quarters. NOTE: A partially blocked, inadequate, or
disconnected vent system may not activate the switch.
Discoloration of the grille is an indication of a bad vent. If this
occurs, the vent can be checked by a qualified serviceman using
a draft gauge. After 15 minutes the gauge should read between
-.02 up to -.04 inches w.c. Vent must be checked at the
beginning of each heating season.
Jan 28, 2009 | Heating & Cooling
Dayton 3E372B Fuel Trimmer
sounds like the thermal couple could also be the ignition module.Is it spark ignition or hot surface
May 05, 2008 | Dayton (3E379) Heater
Spill switch for warehouse heater
yeah...it may be needing some colling device...
Mar 18, 2008 | Dayton (3E379) Heater
Dayton gas heater mod 3E404
This is an easily fixed problem. There are two thermistor switches on Dayton furnaces. One controls the fan motor run function and the heater valve on/off function. The other called a blocked vent switch (located in the top front of the heater) stops the gas valve from opening in the event the
vent is plugged. However, if the furnace was totally shut down for the summer and is now being fired up for winter, the block vent switch has to be reset. The switch has a reset button on it, push it and it should solve your problem. Also, check to make sure the fan run thermistor is clean and does not have debris around it as that acts a insulator for heat to keep the fan run function on.
Dec 30, 2007 | Heating & Cooling
Dayton Gas Furnace Heater Logo
488 people viewed this question
Top Dayton Heating & Cooling Experts
Paul Carew
Mack Baxter
Dan Webster
Dan Webster
Are you a Dayton Heating and Cooling Expert? Answer questions, earn points and help others