Question about Goodman GMS90703BXA Heater
GMS90904CXA IR Blower continues to run after it
GMS90904CXA IR Blower continues to run after it should have turned off. One pressure SW has 24 volts and one has 0 volts. Both SW are closed. Trouble light blinks twice. Cycle power
everything works for a limited time however it
may be a week or an hour.
  • Goodman Master
  • 2,517 Answers
It sounds like the fan control switch is not shuutting off when it cools down look at the fan diff settingson the fan control you may be able to adjust this
Posted on Feb 03, 2010
I have a LX250N heater. When I attempted to start the heater this year to no avail. When I turn the heater on and raise the thermostat to demand heat I hear once click but the blower never comes on. Can...
safety circuit will not let blower turn on check to see if 24 volts ac on both sides of pressure switch if ok see if 24 volts at gas valve brown and yellow wires if not safety circuit open check copper tube to pressure switch to see if clogged
Jun 26, 2014 | Jandy LX 250N Lo-NOx, 250,000 BTU Heater,...
I have a model 560 Aprilaire humidifier thay doesn't work. I replaced the solonoid valve and it still doesn't work. What's my next move?
The system is 24 volt AC so start by checking the voltage from the transformer to make sure it is approximately 24 volts AC. The current will flow through the humidistat when continuity is made at the control as the humidistat senses that your house needs moisture. Disconnect the wires from the himidistat and set it to a high level, you should hear a click on the way up. With the 24 volt wires disconnected, check for continuity with a volt meter. If you don't have continuity replace it. Current also flows through an inductive sensor switch that hang on a wire from the blower. When the blower wire has current flowing through it, the switch senses that an closes makin the connection. With both wires disconnected from the 24 volts you can test for continuity when the blower is running. Overall, this is a continuous circle of wiring and is not directional like DC so think of the wiring a a big loop. The correct current has to flow through the transformer, through the humidistat, through the blower switch, through the solenoid completing the the circle before the solenoid will activate. Hope this helps.
Dec 07, 2010 | Aprilaire 550 Humidifier
Fan turns on, pilot on left side turns on red light at bottom stays solid during entire time then pilot goes out and blower stops no heat please help
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remaing solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Oct 05, 2010 | Goodman GMS90703BXA Heater
No blinks normal running igniter glows gas comes on wont run
Check for 24 volts across the gas valve when Ignitor is glowing. If no, bad board. If yes, bad gas valve or blockage.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
Mar 05, 2010 | Goodman GMS90703BXA Heater
80% ducane furnace makes several attempts to ignite then shuts down. glow stick lights but no ignition to main burners. any ideas?
Check for 24 volts across the gas valve terminals!
Mar 04, 2010 | Heating & Cooling
Goodman unit. when i turn it on the blower fan and the exhaust fan comes on butit does not lite no flames at all. i don't even hear the gas click in.
Feb 15, 2010 | Intertherm P3RA-048K Air Conditioner
Red light blinking continuosly meanig gas valve relay short how can I fix myself - furnance only blows cold air
You will need to check for 24 volts AC to the gas valve after the igniter starts sparking or glowing. If you have it but it does not open, bad gas valve and you will need to replace it. If you are not getting 24 volts after it starts glowing or sparking, you have a bad board.
Jan 16, 2010 | Heating & Cooling
I have an americanaire ultra sx 80 furnace that if it does start up the 1st time, the induction motor continue to run and it will not start
Jan 04, 2010 | Heating & Cooling
Unit runs normal but when thermostat satisfy draft motor does not stop.unless you turn off the power. and restart to run at normal again
Bad blower relay on circuit board. You can live with it or replace the board. Blower relay is not available as a separate part.
Dec 20, 2009 | Ingram GMS90904CXA Heater
Carrier furnace, pilot does not light, fans run for a couple minutes and then flashes code 31
Nov 28, 2009 | Carrier 38CKC042 Air Conditioner
Goodman GMS90703BXA Heater Logo
149 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others