Carrier model 58sxa080-gg series 100

Blower comes on, pilot lights, burners ignite, big blower comes on but the burners and pilot go out then the blower goes off before the house gets warm,
thermostat is set for 74 goes off at 64 will not come on again until i turn the thermostat off then back on but keeps going off before it reaches the correct temp

Posted by on

1 Answer

  • Level 1:

    An expert who has achieved level 1.

    Hot-Shot:

    An expert who has answered 20 questions.

    Corporal:

    An expert that hasĀ over 10 points.

    Mayor:

    An expert whose answer gotĀ voted for 2 times.

  • Contributor
  • 21 Answers

The flame detector rod is dirty? try cleaning with sand paper and scraping also. there should be a small amp. reading threw wire coming from flame detector rod. in milli amp range. increases when running. some times i use a jumper to hold gas valve on once started to allow time to test amps.

Posted on Feb 21, 2008

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Burners not burning, pilot light is off. How do I start the pilot light?


There is no pilot on this unit. It is electronic ignition.

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Mar 29, 2010 | Carrier XHB123D X/Y Series Heat/Cool Air...

1 Answer

I have a carrier 58sx040. Sometimes after the pilot comes on the main flame will start then stop about every 3 seconds. This problem intermittent. There is always a noise coming from the gas inlet when...


Dirty flame rod, polish it with a scrub pad.

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Mar 13, 2010 | Carrier Air Conditioners

1 Answer

Trying to determine whether I have a bad Ign/Lockout or inducer relay board on Mod 58SXA080-GG. If I shut off heat at t-stat or unplug ign mod. for 10 min. It will usually intiate a heat cycle but I only...


The inducer blower will put a vacuum on your pressure switch which in turn will tell the board to apply power to the ignitor. If you have a vent blockage, dirty air filter, plugged condensate line or any blockage of either vent or air intake, the furnace will lock-out and flash an error code on the circuit board. If after inspecting all the above for debris and found nothing, you can quickly jump the pressure switch after the inducer starts to see if the ignitor glows. You could also have a bad ignitor. Yes the lock-out is normal. Looks like you discovered the cause on your own, order a new switch.

Feb 15, 2010 | Carrier XHB123D X/Y Series Heat/Cool Air...

1 Answer

Carrier furnace ,burner not staying on after 4th try shuts down completely.cleaned the flame sensor but noticed the 3rd and 4th burner has a delay in lighting by the time the 4th burner lights and hits the...


Remove them and scrub them with a wire brush.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Jan 10, 2010 | Carrier XHB123D X/Y Series Heat/Cool Air...

1 Answer

I have a technical question regarding implementation of my Carrier furnace within my residence. Specifically, the furnance has been installed for 17 years and I have not had any problems with it. I have...


Thats a safety.

The unit senses a failure to ignite, so it goes into safety mode keeping the blower running to prevent overheating and fires. And keeping the inducer motor running to prevent the same, as well as raw gas build up inside the unit.

The newer systems are "smarter" and can detect more specific problems and failures. The older ones simply know that the thing didn't light, so they bring on the fans for safety.


Jan 01, 2010 | Carrier XHB123D X/Y Series Heat/Cool Air...

2 Answers

Having problems with Carrier 58RAV furnace. Goes through the motions, but gas never turns on. I think it is a problem with the LPGS. Please advise. Thanks


On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Dec 24, 2009 | Carrier Air Conditioners

1 Answer

Carrier furnace, pilot does not light, fans run for a couple minutes and then flashes code 31


On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Nov 28, 2009 | Carrier 38CKC042 Air Conditioner

2 Answers

Gas heater won't ignite


I agree. Either the pilot flame is dirty and is not making good contact to heat up the bi metal strip on the pilot assembly, or the pilot assembly is defective. 90% of the time if you clean the pilot orfice and the pilot burner it will take care of the problem

Nov 16, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...

1 Answer

Carrier Weathermaker SX model 58SX060-CC Blower runs all the time


Remove all power from the furnace, it is likely the brain in the furnace is need of being reset, from the battery replacement, why did you change the battery, was there an indicator telling you to change it?

Many times just removing all the power to the furnace will do the trick with a reset, if not let me know and we will go from there, but it sounds like the main brain is confused or bad, more likely confused, so try the power removed first.

Than let me know wbwill@sbcglobal.net

Oct 22, 2008 | Carrier XHB123D X/Y Series Heat/Cool Air...

Not finding what you are looking for?
Carrier XHB123D X/Y Series Heat/Cool Air Conditioner Logo

790 people viewed this question

Ask a Question

Usually answered in minutes!

Top Carrier Air Conditioners Experts

Cindy Wells

Level 3 Expert

4758 Answers

yadayada
yadayada

Level 3 Expert

61037 Answers

Lawrence Oravetz

Level 3 Expert

7686 Answers

Are you a Carrier Air Conditioner Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...