Gas valve clicks but does not light
When i turn up thermostat small blower comes on and a few seconds
later i here a click from where the gas valve is.furnace will not light
  • Ken Bledsoe May 11, 2010
    Do you have a hot surface ignitor? Can u look inside the unit and look it looks like a flat thin piece of ceramic get back with me. ken
    Genius:
  • 1,400 Answers
Hello
The click is either the gas valve opening or the ignitor trying to ignite.
From what you decribe,im going to say you have a bad ignitor.
If the gas valve is indeed opening,then you need igniton to light the gas,
which leads me to say bad ignitor.
Hope this helps.
Posted on Feb 02, 2010
Goodman gms80903bna light blinks once fan runs all the time,
I believe this code is ignition failure.
Turn power off and after 20 seconds turn power on with thermostat calling for heat. Vent blower should come on first. After a bit igniter should lite up. You should hear click noise of gas valve open up. If igniter does lite and you hear click noise, flame should come on for a few seconds minimum. If igniter doesn't lite and you hear click noise from gas valve, igniter is bad. If flame lites and then goes out, flame sensor probably needs cleaned. Both igniter and flame sensor are in metal plate under burners. Igniter has 2 wire going to it and flame sensor has one wire. If you think it is flame sensor you can remove with taking it out with 1 1/4" hex screw. Flame sensor will have white film on it if it needs cleaned, clean with steel wool or a dollar bill. If it isn't weither of these it is gas valve or circuit board.
Jan 27, 2011 | Goodman Heating & Cooling
Goodman unit. when i turn it on the blower fan and the exhaust fan comes on butit does not lite no flames at all. i don't even hear the gas click in.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Feb 15, 2010 | Intertherm P3RA-048K Air Conditioner
I have an intertherm gas furnace and it will turn on but it takse almost an hour from the time i turn the heat up until it kicks on. I can hear the click and it sounds like the motor is humming. I have...
Jan 23, 2010 | Heating & Cooling
Burners ignite but turn off after a few seconds
Jan 08, 2010 | Ruud Heating & Cooling
WILL NOT LIGHT ALL 5 BURNNERS WILL ONLY LIGHT 2 THEN SHUTS OFF GOES TO LOCKDOWN
Nov 23, 2009 | Coffee Makers & Espresso Machines
When I turn my furnace on, the purge blower starts as normal, then after 15 seconds the ignitor starts to glow but when the gas valve should turn on it only turns on for a split second and then you can...
Nov 19, 2009 | Goodman GMS90703BXA Heater
Hello I have a goodman gas furnace
On a call for heat, the 24 volt thermostat2.gif sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Oct 18, 2009 | Goodman Heating & Cooling
Blower works but no heat
If in fact you have the above listed furnace, you do not have a pilot but electronic ignition. You will need to remove the front cover on the furnace, tape down the door safety switch and then have someone help you by turning up your thermostat to a very high setting. Watch and listen inside the furnace. There should be some blinking going on at the control board followed by a small blower fan starting up. Then after 10-15 seconds there should be a click followed by an orange glow viewed thru the viewing window to the burner section. In a few seconds the gas valve should click and the burners will ignite. There is a safety switch that will sense flame and then keep the gas going to the burners. If it does not sense it, it will shut it off within 10 seconds. If all is well so far, your blower will turn on in about 90 seconds after flame. There is a diagnostic code chart on the back side of the access door if you get an error code (blinking) on the control board.
Always check little things like air filter, condensate drain and broken or loose wires.
Nov 05, 2008 | Goodman GMS90703BXA Heater
Duct fan comes in, igniter lights, but no flame
Remove the front panel. Tape the door switch to the closed position. If the thermostat is calling for heat the furnace should do the following: a light on the circuit board will flash and then the exhaust blower will start. A few seconds later (10-15) you should hear clicking at at the circuit board and an orange glow should be seen thru the small viewing port. A few seconds later the gas valve should open and the orange light will turn blue. If the blue flame only lasts a few seconds and then goes out, their may either be a blockage not allowing the flame to travel to all the burners and not allowing a flame sensor to sence flame, shutting down the unit. After a few cycles of not starting, the circuit board will flash a series of codes that you can read if you look on the back of the front cover. It will give you a starting point where we can research and come up witha more difinitive answer. Let us know what you find for codes.
Oct 26, 2007 | Goodman GMS90703BXA Heater